<DIV><FONT face=Arial color=#0000ff size=2><SPAN
class=784223614-24032004>Konstantin,</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN
class=784223614-24032004></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=784223614-24032004>What
front end are you using to insulate you from having to deal with text at the BDL
level? Our office has been using Visual DOE for about 7 years now and the
central plant editor allows you to specify a closed cooling tower. Anyway,
I did a quick sample run specifying a low efficiency (as noted by the high
approach) closed tower and the BDL text the program wrote looks something like
what I have below. If your GUI front end doesn't allow a closed tower, you
might have to roll up your sleeves and insert similar text into the input
file. Make sure to change parameters as appropriate.</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN
class=784223614-24032004></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=784223614-24032004>Good
luck.</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN
class=784223614-24032004></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=784223614-24032004>Mike
Busman</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN
class=784223614-24032004>NORESCO, LLC</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN
class=784223614-24032004></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=784223614-24032004>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
face="Courier New"><FONT color=#000000><SPAN
class=784223614-24032004> </SPAN>*3143 * $Cooling
Tower<?xml:namespace prefix = o ns = "urn:schemas-microsoft-com:office:office"
/><o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3144 * TOWER0 =
PLANT-EQUIPMENT<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3145 *<SPAN
style="mso-spacerun: yes"> </SPAN>TYPE =
CLOSED-TWR<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3146 *<SPAN
style="mso-spacerun: yes"> </SPAN>SIZE =
-999<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3147 *<SPAN
style="mso-spacerun: yes"> </SPAN>INSTALLED-NUMBER =
1<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3148 *<SPAN
style="mso-spacerun: yes"> </SPAN>MAX-NUMBER-AVAILABLE =
1<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3149 *
..<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3150 *<SPAN
style="mso-spacerun: yes"> </SPAN><o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3151 *
PART-LOAD-RATIO<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3152 *<SPAN
style="mso-spacerun: yes"> </SPAN>TYPE =
CLOSED-TWR<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3153 *<SPAN
style="mso-spacerun: yes"> </SPAN>ELEC-INPUT-RATIO =
0.0081<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3154 *
..<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3155 *<SPAN
style="mso-spacerun: yes"> </SPAN><o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3156 *
PLANT-PARAMETERS<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3157 *<SPAN
style="mso-spacerun: yes"> </SPAN><o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3158 *<SPAN
style="mso-spacerun: yes"> </SPAN>$Electric Compression
Chiller<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3159 *<SPAN
style="mso-spacerun: yes"> </SPAN>OPEN-CENT-COND-TYPE =
TOWER<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3160 *<SPAN
style="mso-spacerun: yes"> </SPAN>OPEN-CENT-UNL-RAT =
.1<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3161 *<SPAN
style="mso-spacerun: yes"> </SPAN><o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3162 * $Compression
chiller('s) condenser and evaporator water
flow<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3163 * $ includes
evaporator flow for two-loop systems.<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3164 *<SPAN
style="mso-spacerun: yes"> </SPAN>COMP-TO-TWR-WTR =
6<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3165 *<SPAN
style="mso-spacerun: yes"> </SPAN>CHILL-WTR-T =
44<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3166 *<SPAN
style="mso-spacerun: yes"> </SPAN><o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3167 * $Fuel Hot
Water Plant Boiler.<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3168 *<SPAN
style="mso-spacerun: yes"> </SPAN>HW-BOILER-HIR<SPAN
style="mso-spacerun: yes"> </SPAN>=
1.666667<o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3169 *<SPAN
style="mso-spacerun: yes"> </SPAN><o:p></o:p></FONT></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><FONT face="Courier New"><SPAN
style="mso-spacerun: yes"> </SPAN>*3170 *
$Tower</FONT></FONT></SPAN></P><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT><FONT
face="Courier New"><o:p>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN class=784223614-24032004>
</SPAN>*3171 *<SPAN style="mso-spacerun: yes">
</SPAN>TWR-DESIGN-APPROACH = 20<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN style="mso-spacerun: yes">
</SPAN>*3172 *<SPAN style="mso-spacerun: yes">
</SPAN>TWR-DESIGN-RANGE = 10<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN style="mso-spacerun: yes">
</SPAN>*3173 *<SPAN style="mso-spacerun: yes">
</SPAN>TWR-DESIGN-WETBULB = 78<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN style="mso-spacerun: yes">
</SPAN>*3174 *<SPAN style="mso-spacerun: yes"> </SPAN>TWR-SETPT-CTRL
= FIXED<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN style="mso-spacerun: yes">
</SPAN>*3175 *<SPAN style="mso-spacerun: yes"> </SPAN>TWR-SETPT-T =
85<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN style="mso-spacerun: yes">
</SPAN>*3176 *<SPAN style="mso-spacerun: yes"> </SPAN>TWR-THROTTLE =
10<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN style="mso-spacerun: yes">
</SPAN>*3177 *<SPAN style="mso-spacerun: yes"> </SPAN>MIN-TWR-WTR-T
= 66<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN style="mso-spacerun: yes">
</SPAN>*3178 *<SPAN style="mso-spacerun: yes"> </SPAN>TWR-CAP-CTRL =
ONE-SPEED-FAN<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN style="mso-spacerun: yes">
</SPAN>*3179 *<SPAN style="mso-spacerun: yes">
</SPAN>DIRECT-COOL-MODE = NOT-AVAILABLE<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN style="mso-spacerun: yes">
</SPAN>*3180 *<SPAN style="mso-spacerun: yes"> </SPAN>$ Condenser
pump includes a weighted average including all<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN style="mso-spacerun: yes">
</SPAN>*3181 *<SPAN style="mso-spacerun: yes"> </SPAN>$ the
evaporator and condenser pumps for water cooled
chillers<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN style="mso-spacerun: yes">
</SPAN>*3182 *<SPAN style="mso-spacerun: yes"> </SPAN>TWR-PUMP-HEAD
= 10.0<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN style="mso-spacerun: yes">
</SPAN>*3183 *<SPAN style="mso-spacerun: yes">
</SPAN>TWR-IMPELLER-EFF = 0.77<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'"><FONT
color=#000000><SPAN style="mso-spacerun: yes">
</SPAN>*3184 *<SPAN style="mso-spacerun: yes"> </SPAN>TWR-MOTOR-EFF
= 0.9<o:p></o:p></FONT></SPAN></P>
<P class=MsoPlainText style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 8pt; FONT-FAMILY: Arial; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'MS Mincho'; mso-bidi-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA"><FONT
color=#000000><SPAN style="mso-spacerun: yes"> <SPAN
class=784223614-24032004> </SPAN>
</SPAN>*3185 *<SPAN style="mso-spacerun: yes">
</SPAN></FONT></SPAN></o:p></FONT></FONT></SPAN></P></SPAN></FONT></DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
<DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma
size=2>-----Original Message-----<BR><B>From:</B> Konstantin Babets
[mailto:babetsk@jbb.com]<BR><B>Sent:</B> Wednesday, March 24, 2004 6:13
AM<BR><B>To:</B> mbusman@noresco.com; BLDG-SIM@gard.com<BR><B>Subject:</B> Re:
[BLDG-SIM] Closed circuit cooling tower in DOE2.1E<BR><BR></FONT></DIV>
<DIV><FONT face=Arial size=2>Thanks to everybody for helping with my river
water cooling problem. I found that using hourly output and programming excell
spreadsheet was the way to go.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Here is another problem. How can I approach
modeling a closed circuit cooling tower in DOE2.1E?</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Konstantin Babets</FONT></DIV>
<DIV><FONT face=Arial size=2>Jaros Baum and Bolles</FONT></DIV>
<DIV><FONT face=Arial size=2>Consulting Engineers</FONT></DIV>
<DIV><FONT face=Arial size=2>212 530 9455</FONT></DIV>
<BLOCKQUOTE dir=ltr
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
<DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
<DIV
style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B>
<A title=mbusman@noresco.com
href="mailto:mbusman@noresco.com">mbusman@noresco.com</A> </DIV>
<DIV style="FONT: 10pt arial"><B>To:</B> <A title=babetsk@jbb.com
href="mailto:babetsk@jbb.com">babetsk@jbb.com</A> ; <A
title=BLDG-SIM@gard.com
href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> </DIV>
<DIV style="FONT: 10pt arial"><B>Sent:</B> Thursday, March 18, 2004 12:20
PM</DIV>
<DIV style="FONT: 10pt arial"><B>Subject:</B> RE: [BLDG-SIM] River water
cooling</DIV>
<DIV><BR></DIV>
<DIV><SPAN class=151510117-18032004><FONT face=Arial color=#0000ff
size=2>Konstantin,</FONT></SPAN></DIV>
<DIV><SPAN class=151510117-18032004><FONT face=Arial color=#0000ff
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=151510117-18032004><FONT face=Arial color=#0000ff size=2>I
have become a big fan of the hourly output report capabilities of DOE-2 for
presentation purposes, troubleshooting, and to handle situations such as
yours where I'm not aware of how to approach the solution within
DOE-2.</FONT></SPAN></DIV>
<DIV><SPAN class=151510117-18032004><FONT face=Arial color=#0000ff
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=151510117-18032004><FONT face=Arial color=#0000ff
size=2>You could probably run an hourly report to export systems tons
load, CHW supply temperature, and any other variables you might need (CHW
pump kW, condenser pump kW, lighting kW, etc.) and dump the 8760 hours of
data into an Excel file. Based on your CHW pump kW, you might want to
add a column to account for pump heat to give you total cooling load seen by
the chiller.</FONT></SPAN></DIV>
<DIV><SPAN class=151510117-18032004><FONT face=Arial color=#0000ff
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=151510117-18032004><FONT face=Arial color=#0000ff
size=2>Then you need to add 3 columns to calculate from the DOE chiller
curve coefficients the multiplier for capacity based on CHW and CW temp. (I
assume you have a good idea of the variation in river water temp. by
season), multiplier for EIR based on the water temperatures, and
EIR-FPLR. The product of these three values should give you the hourly
EIR. Add another column so that based on the total tons cooling load,
you can then calculate chiller kW from the hourly EIR.</FONT></SPAN></DIV>
<DIV><SPAN class=151510117-18032004><FONT face=Arial color=#0000ff
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=151510117-18032004><FONT face=Arial color=#0000ff size=2>It
might end up being a big spreadsheet, but it's really simple in concept to
set up and should give you the results you desire. If you'd like to
discuss further, feel free to call me.</FONT></SPAN></DIV>
<DIV><SPAN class=151510117-18032004><FONT face=Arial color=#0000ff
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=151510117-18032004><FONT face=Arial color=#0000ff
size=2>Mike Busman</FONT></SPAN></DIV>
<DIV><SPAN class=151510117-18032004><FONT face=Arial color=#0000ff
size=2>NORESCO, LLC</FONT></SPAN></DIV>
<DIV><SPAN class=151510117-18032004><FONT face=Arial color=#0000ff
size=2>949-253-3533, ext. 303</FONT></SPAN></DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
<DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma
size=2>-----Original Message-----<BR><B>From:</B> Konstantin Babets
[mailto:babetsk@jbb.com]<BR><B>Sent:</B> Thursday, March 18, 2004 7:52
AM<BR><B>To:</B> BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] River
water cooling<BR><BR></FONT></DIV>
<DIV><FONT face=Arial size=2>Alec, thank you.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Unfortunately I am using Doe2.1E, where I
cannot schedule loop temperatures. BTW, is it possible to write a
custom function to access the PLANT? It does look like I can
only use custom functions to modify computations in Loads and Systems.
</FONT></DIV>
<DIV><FONT face=Arial size=2>Any ideas?</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>
<DIV><FONT face=Arial size=2>Konstantin Babets</FONT></DIV>
<DIV><FONT face=Arial size=2>Jaros Baum and Bolles</FONT></DIV>
<DIV><FONT face=Arial size=2>Consulting Engineers</FONT></DIV>
<DIV><FONT face=Arial size=2>212 530 9455</FONT></DIV></FONT></DIV>
<BLOCKQUOTE dir=ltr
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
<DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
<DIV
style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B>
<A title=astevens@dmiinc.com href="mailto:astevens@dmiinc.com">Alec
Stevens</A> </DIV>
<DIV style="FONT: 10pt arial"><B>To:</B> <A title=babetsk@jbb.com
href="mailto:babetsk@jbb.com">babetsk@jbb.com</A> </DIV>
<DIV style="FONT: 10pt arial"><B>Sent:</B> Wednesday, March 17, 2004
6:02 PM</DIV>
<DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [BLDG-SIM] River water
cooling</DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT><BR></DIV>
<DIV><FONT face=Arial size=2>Konstantin,</FONT></DIV>
<DIV><FONT face=Arial size=2>Not 100% sure, but I think you should be
able to schedule the loop temperature. Create day/week/year
schedules and input the appropriate variation in river water temp, use
that for loop temp.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>I know you can do this for ground source
loop temperature for a WLHP system, so it should be applicable to CW
loop.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>just for fun:</FONT></DIV>
<DIV><FONT face=Arial size=2><A
href="http://www.utilities.cornell.edu/LSC/default.htm">http://www.utilities.cornell.edu/LSC/default.htm</A></FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>good luck</FONT></DIV>
<DIV><FONT face=Arial size=2>Alec</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<BLOCKQUOTE dir=ltr
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
<DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
<DIV
style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B>
<A title=babetsk@jbb.com href="mailto:babetsk@jbb.com">Konstantin
Babets</A> </DIV>
<DIV style="FONT: 10pt arial"><B>To:</B> <A title=BLDG-SIM@gard.com
href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> </DIV>
<DIV style="FONT: 10pt arial"><B>Sent:</B> Wednesday, March 17, 2004
4:53 PM</DIV>
<DIV style="FONT: 10pt arial"><B>Subject:</B> [BLDG-SIM] River water
cooling</DIV>
<DIV><BR></DIV>
<DIV><FONT face=Arial size=2>Hello,</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>I am working on a project that considers
utilizing river water instead of a conventional cooling tower
condenser water. Does anyone have an idea how could this be
simulated in DOE2.1? (Basically, somehow I need to reset entering
condenser water temperature to that of a river
water).</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Thank you,</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Konstantin Babets</FONT></DIV>
<DIV><FONT face=Arial size=2>Jaros Baum and Bolles</FONT></DIV>
<DIV><FONT face=Arial size=2>Consulting Engineers</FONT></DIV>
<DIV><FONT face=Arial size=2>212 530 9455</FONT></DIV><PRE>==================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE></BLOCKQUOTE><PRE>=====================================================You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE></BLOCKQUOTE></BLOCKQUOTE><PRE>
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>