<DIV><SPAN class=340042919-15102003>The easy way to settle that is to create a 
spreadsheet that uses the coefficients.  You can get them from the .bdl 
file if you enter DIAGNOSTIC COMMENTS .. right before your chiller 
instructions.  Interestingly enough, that's what I was doing this 
morning.  I have attached my spreadsheet.  Please excuse that it is 
not ready for distribution.  Just something I was playing 
with.</SPAN></DIV>
<DIV><SPAN class=340042919-15102003></SPAN> </DIV>
<DIV><SPAN class=340042919-15102003>The coefficients are for DOE-2.2 and do 
include upgrades since the mid '70s that DOE-2.1E uses.  The VFD 
coefficients are new.</SPAN></DIV>
<DIV><SPAN class=340042919-15102003></SPAN> </DIV>
<DIV><SPAN class=340042919-15102003>
<DIV><SPAN class=340042919-15102003>As you can see, kW/ton does change with 
temperatures.</SPAN></DIV>
<DIV><SPAN class=340042919-15102003></SPAN> </DIV>If you want FIXED 
condenser water temperature and chilled water temperature (the default), do not 
turn on the resets.  Condenser water (and maybe chilled water) will still 
drift with what the equipment can do.</SPAN></DIV>
<DIV><SPAN class=340042919-15102003></SPAN> </DIV>
<DIV><SPAN class=340042919-15102003>Mike</SPAN></DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma 
  size=2>-----Original Message-----<BR><B>From:</B> postman@gard.com 
  [mailto:postman@gard.com]<B>On Behalf Of </B>Aulbach, John<BR><B>Sent:</B> 
  Wednesday, October 15, 2003 1:23 PM<BR><B>To:</B> 
  BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] Major disagreement on Chiller 
  Performance Curves in DOE-2.1E and DOE-2.2<BR><BR></FONT></DIV>
  <P><FONT size=2>I am having a "friendly" disagreement with a colleague on what 
  chiller curves to ask for from a manufacturer to input into DOE-2 (could be 
  either 2.1E or 2.2). We both agree that the infamous ARI point for a 100% load 
  should be input. But the curves are where we disagree.</FONT></P>
  <P><FONT size=2>Is the Default DOE-2 curve for % Power versus % Tons the ARI 
  curve with the allowable reduction in condenser water temperature, or is it 
  based on the FIXED 85°F entering condenser water and FIXED 44°F leaving 
  chilled water ALL the way down the curve?</FONT></P>
  <P><FONT size=2>Therefore, when I am given a chiller with a variable speed 
  drive installed, what parameters should I ask for in such a Power/Tons to be 
  FIXED ???</FONT></P><BR><BR><BR><BR>
  <P><FONT size=2>John R. Aulbach, PE, CEM</FONT> <BR><FONT size=2>Project 
  Engineer</FONT> <BR><FONT size=2>Sempra Energy Solutions</FONT> <BR><FONT 
  size=2>555 West Fifth Street</FONT> <BR><FONT size=2>Mail Location 27F3</FONT> 
  <BR><FONT size=2>Los Angeles, CA 90013</FONT> <BR><FONT size=2>Tel: (213) 
  244-8551 Cell (213) 219-4875</FONT> <BR><FONT size=2> </FONT> </P>
  <P><FONT size=2>"Sempra Energy Solutions is not the same company as SDG&E/ 
  SoCalGas, the Utilities.  Sempra Energy Solutions is not regulated by the 
  California Public Utilities Commission, and you do not have to buy Sempra 
  Energy Solutions products or services to continue to receive quality regulated 
  service from the Utilities."  </FONT></P><PRE>
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE></BODY></HTML>