<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff size=2>John, 
I think the answer to your question has two parts:</FONT></SPAN></DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff size=2>1. DOE 
uses two curves for modifying the full load EIR (1/COP) of a 
<U>constant</U> speed chiller.  The first adjusts for part load and the 
second for temperature. </FONT></SPAN></DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff 
size=2>I use a curve with <U>fixed</U> CHWT and CWT at various part 
load conditions (at <U>design</U> conditions not ARI rated 
conditions) for the EIR f(PLR) curve (the one you're asking about) and 
create a second curve based on various combinations of CHWT, CWT at full 
load for the EIR f(LCHWT, ECWT) curve.  The assumption, I think, is 
that the PLR curve reamins relatively uniform as the water temperatures change 
so once you have the shape of the PLR curve you can account for 
temperature differences with a second curve.</FONT></SPAN></DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff size=2>2. The 
above methodology works fine for constant speed chillers but needs to be 
modified for variable speed chillers.  Rather than using EIR F(PLR) you 
need to use EIR f(PLR,dT).  This curve now accounts for the change 
in the difference of the water temperature across the chiller.  See 
Volume 6 of the DOE 2.2 v41 reference manual available at <A 
href="http://www.DOE2.com">www.DOE2.com</A>, there is a section on chiller 
performance that explains this much better than I could do.  DOE 
2.2 v41 incorporates this change and has default curves for 
both.</FONT></SPAN></DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff size=2>It 
sounds like you both may be correct depending on the type of chiller you want to 
model.</FONT></SPAN></DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff size=2>Mike 
Tillou, PE</FONT></SPAN></DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff size=2>etc 
Group, Inc</FONT></SPAN></DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff 
size=2>413-664-9070</FONT></SPAN></DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=976153420-15102003><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV></DIV>
<DIV><FONT face=Tahoma size=2>-----Original Message-----<BR><B>From:</B> 
postman@gard.com [mailto:postman@gard.com] <B>On Behalf Of </B>Aulbach, 
John<BR><B>Sent:</B> Wednesday, October 15, 2003 2:23 PM<BR><B>To:</B> 
BLDG-SIM@GARD.COM<BR><B>Subject:</B> [BLDG-SIM] Major disagreement on Chiller 
Performance Curves in DOE-2.1E and DOE-2.2<BR><BR></DIV></FONT>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <P><FONT size=2>I am having a "friendly" disagreement with a colleague on what 
  chiller curves to ask for from a manufacturer to input into DOE-2 (could be 
  either 2.1E or 2.2). We both agree that the infamous ARI point for a 100% load 
  should be input. But the curves are where we disagree.</FONT></P>
  <P><FONT size=2>Is the Default DOE-2 curve for % Power versus % Tons the ARI 
  curve with the allowable reduction in condenser water temperature, or is it 
  based on the FIXED 85°F entering condenser water and FIXED 44°F leaving 
  chilled water ALL the way down the curve?</FONT></P>
  <P><FONT size=2>Therefore, when I am given a chiller with a variable speed 
  drive installed, what parameters should I ask for in such a Power/Tons to be 
  FIXED ???</FONT></P><BR><BR><BR><BR>
  <P><FONT size=2>John R. Aulbach, PE, CEM</FONT> <BR><FONT size=2>Project 
  Engineer</FONT> <BR><FONT size=2>Sempra Energy Solutions</FONT> <BR><FONT 
  size=2>555 West Fifth Street</FONT> <BR><FONT size=2>Mail Location 27F3</FONT> 
  <BR><FONT size=2>Los Angeles, CA 90013</FONT> <BR><FONT size=2>Tel: (213) 
  244-8551 Cell (213) 219-4875</FONT> <BR><FONT size=2> </FONT> </P>
  <P><FONT size=2>"Sempra Energy Solutions is not the same company as SDG&E/ 
  SoCalGas, the Utilities.  Sempra Energy Solutions is not regulated by the 
  California Public Utilities Commission, and you do not have to buy Sempra 
  Energy Solutions products or services to continue to receive quality regulated 
  service from the Utilities."  </FONT></P><PRE>
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>