<P><FONT SIZE=2>Mark, Bldg-Simmers,</FONT>
</P>
<P><FONT SIZE=2>The UK's Building Research Establishment's "Office of the Future" is one Euro building that deliberately uses voids formed into precast concrete floor/ceiling panels to distribute & extract natural ventilation air, consciously activating their thermal mass. These proprietary panels were invented & seem to be most widely used in Scandinavia; they create an undulating ceiling with ~10' period peak to peak, with 'waves' ~2.5' deep. A flat floor is cast above, and air is driven by wind pressure between this floor slab and the lower ceiling formed by the precast panels. Their curving shape lend themselves very well to direct/indirect lighting fixtures suspended below the high points of the ceiling; for both nat vent & daylighting purposes, sections are oriented perpendicular to the exterior walls. The shapes tend to elicit that 'WOW' factor from architects....</FONT></P>
<P><FONT SIZE=2>As I say, these are a proprietary precast system, but the manufacturer's name escapes me at the moment. For more information, speak to Feilden Clegg Architects (London, UK?) or the BRE; David Lloyd Jones' book "Architecture & the Environment - Bioclimatic Building Design" has both lovely pictures & (hail Mary!) monitored energy performance #s (83 kWhe/sq.m-yr *total*!)</FONT></P>
<BR>
<P><FONT SIZE=2>Hope this helps,</FONT>
<BR><FONT SIZE=2>Ian G. Theaker, P.Eng. </FONT>
<BR><FONT SIZE=2>Senior Energy Engineer</FONT>
<BR><FONT SIZE=2> </FONT>
<BR><FONT SIZE=2>503.382.2266 OFFICE</FONT>
<BR><FONT SIZE=2>503.382.2654 DIRECT</FONT>
<BR><FONT SIZE=2>503.382.2262 FAX</FONT>
</P>
<P><FONT SIZE=2>Consultants of Choice to the Built Environment</FONT>
<BR><FONT SIZE=2>www.interfaceengineering.com </FONT>
</P>
<BR>
<P><FONT SIZE=2>-----Original Message-----</FONT>
<BR><FONT SIZE=2>From: postman@gard.com [<A HREF="mailto:postman@gard.com">mailto:postman@gard.com</A>] </FONT>
<BR><FONT SIZE=2>Sent: Friday, September 12, 2003 12:02 AM</FONT>
<BR><FONT SIZE=2>To: bldg-sim@gard.com</FONT>
<BR><FONT SIZE=2>Subject: [bldg-sim] Digest (09/12/2003 03:01) (#2003-62)</FONT>
</P>
<BR>
<P><FONT SIZE=2>(#2003-62) - Topics this issue:</FONT>
</P>
<P><FONT SIZE=2> 1) Integrated air distribution system, <mcase@etcgrp.com></FONT>
</P>
<P><FONT SIZE=2>----------------------------------------------------------------------</FONT>
</P>
<BR>
<P><FONT SIZE=2>Date: Thu, 11 Sep 2003 10:33:55 -0600</FONT>
<BR><FONT SIZE=2>From: "Mark E. Case" <mcase@etcgrp.com></FONT>
<BR><FONT SIZE=2>Subject: Integrated air distribution system</FONT>
</P>
<P><FONT SIZE=2>This is a multi-part message in MIME format.</FONT>
</P>
<P><FONT SIZE=2>------=_NextPart_000_0026_01C37850.3AACDD30</FONT>
<BR><FONT SIZE=2>Content-Type: text/plain;</FONT>
<BR> <FONT SIZE=2>charset="iso-8859-1"</FONT>
<BR><FONT SIZE=2>Content-Transfer-Encoding: 7bit</FONT>
</P>
<P><FONT SIZE=2>I'm looking for information on structurally integrated air distribution systems (for want of a better term). I seem to remember reference to a building that had the air distribution integrated into the floor slab at one of JE Braun's presentations on building mass thermal storage. The idea was to more effectively couple the air system with the building's thermal mass. I know some related work has been done with raised floor systems over concrete slabs but that's not really what I'm thinking of. </FONT></P>
<P><FONT SIZE=2>I opened my big mouth at a design concept meeting for a local green project, the architect thought WOW!, and now the engineer wants some references. Imagine that. Any references would be appreciated. </FONT></P>
<BR>
<P><FONT SIZE=2>Mark E. Case, President</FONT>
<BR><FONT SIZE=2>etc Group, Inc.</FONT>
<BR><FONT SIZE=2>3481 South 2300 East</FONT>
<BR><FONT SIZE=2>Salt Lake City, UT 84109</FONT>
<BR><FONT SIZE=2>801-278-1927, 801-278-1942(F)</FONT>
<BR><FONT SIZE=2> </FONT>
<BR><FONT SIZE=2>---------------------------------------------------------------------- </FONT>
<BR><FONT SIZE=2>CONFIDENTIALITY NOTICE This e-mail transmission, and any documents, files or previous e-mail messages attached to it may contain confidential information that is legally privileged. If you are not the intended recipient or the person responsible for delivering it to the intended recipient, you are hereby notified that any disclosure, copying, distribution or use of any of the information contained in or attached to this transmission is strictly prohibited. If you have received this transmission in error, please immediately notify us by telephone at (801) 278-1927 and destroy the original transmission and its attachments without reading them. Thank you. </FONT></P>
<BR>
<P><FONT SIZE=2>------=_NextPart_000_0026_01C37850.3AACDD30</FONT>
<BR><FONT SIZE=2>Content-Type: text/html;</FONT>
<BR> <FONT SIZE=2>charset="iso-8859-1"</FONT>
<BR><FONT SIZE=2>Content-Transfer-Encoding: quoted-printable</FONT>
</P>
<P><FONT SIZE=2><!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 3.2//EN"></FONT>
<BR><FONT SIZE=2><HTML></FONT>
<BR><FONT SIZE=2><HEAD></FONT>
<BR><FONT SIZE=2><META HTTP-EQUIV=3D"Content-Type" CONTENT=3D"text/html; = charset=3Diso-8859-1"> <META NAME=3D"Generator" CONTENT=3D"MS Exchange Server version = 6.0.6396.0"> <TITLE>Integrated air distribution system</TITLE> </HEAD> <BODY></FONT></P>
<P><FONT SIZE=2><!-- Converted from text/rtf format --></FONT>
</P>
<P><FONT SIZE=2><P><FONT SIZE=3D2 FACE=3D"Arial">I'm looking for information on = structurally integrated air distribution systems (for want of a better = term). I seem to remember reference to a building that had the air = distribution integrated into the floor slab at one of JE Braun's = presentations on building mass thermal storage. The idea was to more = effectively couple the air system with the building's thermal mass. I = know some related work has been done with raised floor systems over = concrete slabs but that's not really what I'm thinking of. </FONT></P></FONT></P>
<P><FONT SIZE=2><P><FONT SIZE=3D2 FACE=3D"Arial">I opened my big mouth at a design = concept meeting for a local green project, the architect thought WOW!, = and now the engineer wants some references. Imagine = that.</FONT></P></FONT></P>
<P><FONT SIZE=2><P><FONT SIZE=3D2 FACE=3D"Arial">Any references would be appreciated. = </FONT> </P> <BR></FONT>
</P>
<P><FONT SIZE=2><P><FONT SIZE=3D2 FACE=3D"Arial">Mark E. Case, President</FONT></FONT>
</P>
<P><FONT SIZE=2><BR><FONT SIZE=3D2 FACE=3D"Arial">etc Group, Inc.</FONT></FONT>
</P>
<P><FONT SIZE=2><BR><FONT SIZE=3D2 FACE=3D"Arial">3481 South 2300 East</FONT></FONT>
</P>
<P><FONT SIZE=2><BR><FONT SIZE=3D2 FACE=3D"Arial">Salt Lake City, UT 84109</FONT></FONT>
</P>
<P><FONT SIZE=2><BR><FONT SIZE=3D2 FACE=3D"Arial">801-278-1927, 801-278-1942(F)</FONT></FONT>
</P>
<P><FONT SIZE=2><BR><FONT FACE=3D"Arial">=A0</FONT></FONT>
</P>
<P><FONT SIZE=2><BR><FONT = FACE=3D"Arial">----------------------------------------------------------=</FONT>
<BR><FONT SIZE=2>------------ </FONT></FONT>
</P>
<P><FONT SIZE=2><BR><FONT SIZE=3D1 FACE=3D"Arial">CONFIDENTIALITY NOTICE This e-mail = transmission, and any documents, files or previous e-mail messages = attached to it may contain confidential information that is legally = privileged.=A0 If you are not the intended recipient or the person = responsible for delivering it to the intended recipient, you are hereby = notified that any disclosure, copying, distribution or use of any of the = information contained in or attached to this transmission is strictly = prohibited.=A0 If you have received this transmission in error, please = immediately notify us by telephone at (801) 278-1927 and destroy the = original transmission and its attachments without reading them. Thank = you. </FONT></P></FONT></P>
<P><FONT SIZE=2></BODY></FONT>
<BR><FONT SIZE=2></HTML></FONT>
<BR><FONT SIZE=2>------=_NextPart_000_0026_01C37850.3AACDD30--</FONT>
</P>
<P><FONT SIZE=2>------------------------------</FONT>
</P>
<P><FONT SIZE=2>End bldg-sim@gard.com Digest [09/12/2003 03:01]</FONT>
<BR><FONT SIZE=2>-----------------------------------------------</FONT>
</P>
<P><FONT SIZE=2>======================================================</FONT>
<BR><FONT SIZE=2>You received this e-mail because you are subscribed </FONT>
<BR><FONT SIZE=2>to the BLDG-SIM@GARD.COM mailing list. To unsubscribe </FONT>
<BR><FONT SIZE=2>from this mailing list send a blank message to </FONT>
<BR><FONT SIZE=2>BLDG-SIM-UNSUBSCRIBE@GARD.COM</FONT>
</P>
<PRE>
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY>
</HTML>