<DIV><FONT face=Arial size=2>This module has never worked ideally in any version 
of DOE-2.  It is quite common in Australia to have 2-pipe cooling only 
induction units (active or passive chilled beams) in the zone with ventilation, 
dehumidification, and heating provided from the primary air system.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>In 2.1E you could manually zero out the zone 
heating capacities and use an outdoor-reset schedule to control SAT for heating 
and rely on the zone units for space cooling.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>I have fiddled around with the IU system all day in 
EQuest v3.24 and I am no closer to a solution.  It will not allow 
HEAT-CONTROL = RESET and COOL-CONTROL=RESET does not produce the desired 
effect.  Furthermore it is allowing zone heating when both my MAX-HEAT-RATE 
and HEATING-CAPACITY are set to a very small value (-1BTU/hr) ...</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Has anyone else had similar difficulties or 
successes with this system?  I could use 4-pipe fan coils and set up a 
dummy system passing outdoor air using OA-FROM-SYSTEM, but getting the 
dehumidifcation load is tricky.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Regards,</FONT></DIV>
<DIV><FONT face=Arial size=2>Graham</FONT></DIV></FONT></DIV><PRE>

===========================