<DIV><SPAN class=788551217-07042003><FONT face=Arial color=#0000ff size=2>As a 
long time DOE-2 user, I would go with the Constant Volume Reheat, make the 
chiller an air cooled DX, and kill the hot water and chilled water pumps. As you 
appear to be running Visual DOE, you do not have the "fancy" version of DOE-2.1E 
to actually put in kW/GPM for hot and chilled water pumps. You need to keep the 
pseudo-chilled water flow going to the the chiller (else the chiller will not 
operate). The fact you have electric heat negates any problems with the hot 
water pump.</FONT></SPAN></DIV>
<DIV><SPAN class=788551217-07042003><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=788551217-07042003><FONT face=Arial color=#0000ff size=2>Try 
something like 100% loss or 0% motor efficiency to remove any pump 
kW.</FONT></SPAN></DIV>
<DIV><SPAN class=788551217-07042003><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=788551217-07042003><FONT face=Arial color=#0000ff size=2>Hope 
it works. Have BLDG-SIMs other "wise" emissaries input at 
well.</FONT></SPAN></DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma 
  size=2>-----Original Message-----<BR><B>From:</B> John M. Topmiller 
  [mailto:jmt@abacus-engr.com]<BR><B>Sent:</B> Monday, April 07, 2003 5:42 
  AM<BR><B>To:</B> BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] Modeling DX 
  with reheat in VisualDOE/DOE-2<BR><BR></FONT></DIV><!-- Converted from text/rtf format -->
  <P><FONT face=Arial size=2>I have a fairly simple system in a building that I 
  am modeling but I'm not sure the best DOE-2 system to use.  The building 
  is served by one air handler in the middle of the building with DX cooling and 
  no heating at the unit level.  Each of the two sides of the building has 
  electric resistance reheats in the ducts; I'd figure I'd model the building 
  with two zones each with 50 kW reheat.  I considered modeling the system 
  as Packaged Single Zone AC with Heating and Subzone Reheating, however, with 
  this system the heating in the control zone comes from the air handler and 
  only the subzones have reheat capabilities.  With this system I'd have to 
  set up a dummy control zone to truly model the building.  The system also 
  is close to the Constant-Volume Reheat Fan System in the DOE-2 manual, but I 
  have DX cooling and not a chiller and cooling coil system.  With this 
  system I'd have to convert the cooling loads of the chiller to that of a DX 
  system.  </FONT></P>
  <P><FONT face=Arial size=2>Does anyone have any experience with this type of 
  system and know the best way to proceed?</FONT> </P>
  <P><FONT face=Arial size=2>Thanks,</FONT> </P>
  <P><FONT face=Arial size=2>John M. Topmiller, CEM</FONT> <BR><FONT face=Arial 
  size=2>Energy Engineer</FONT> <BR><FONT face=Arial size=2>Abacus Engineered 
  Systems</FONT> <BR><FONT face=Arial size=2>4431 North Front St., Suite 
  100<BR>Harrisburg, PA 17110-1709</FONT> <BR><FONT face=Arial size=2>p: (717) 
  232-8182 ext. 239</FONT> <BR><FONT face=Arial size=2>c: (717) 514-9767<BR>f: 
  (717) 232-8187</FONT> <BR><A href="mailto:jmt@abacus-engr.com"><U><FONT 
  face=Arial size=2>jmt@abacus-engr.com</FONT></U></A> </P>
  <P><A href="http://www.abacus-engr.com"><U><FONT face=Arial 
  size=2>www.abacus-engr.com</FONT></U></A> </P><PRE>
=====================================================You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE></BODY></HTML>