<DIV><FONT face=Arial size=2>The default boiler part-load performance curve is 
based on the ICES reports (Integrated Community Energy Systems) prepared by Oak 
Ridge National Laboratory in the 1970's.  This single curve is almost 
certainly not representative of all boilers.  In fact I would expect that 
the part-load performance of atmospheric boilers might be significantly 
different than from forced-draft boilers, where the percentage of excess air at 
part-load firing can be better controlled. </FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>The default MIN-RATIO is 0.25 for all fuel-fired 
boilers.  For versions 2.1e and earlier, Fred is correct in stating that 
the program holds the efficiency constant at part-load ratios below this 
value.  Version 2.2/eQUEST/PowerDOE address this issue by applying part of 
the START-UP-TIME to the portion of the hour the boiler is cycling.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV><FONT face=Arial size=2>
<DIV><FONT face=Arial size=2>If you have part-load data that includes the effect 
of cycling, then the best approach is to create a curve including the cycling 
portion of the range (use the CURVE-FIT command to generate the coefficients), 
and set the MIN-RATIO to zero or a very small fraction.  </FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Using a curve-generating routine other than the 
2.2's CURVE-FIT algorithm may not give the correct results; DOE-2 expects that 
the part-load curve to give a value of exactly 1.0 at a part-load ratio of 
1.0, and the CURVE-FIT algorithm ensures this (see the documentation for more 
information).  If you generate the curve using a different program, such as 
Excel, the best fit often does not yield the value of 1.0 at PLR = 1.0  
There is a version of the program in development that can use any best-fit 
curve; this release will be available later this year.</FONT></DIV>
<DIV> </DIV>
<DIV>The fuel-fired boilers do not have default curves correcting 
performance for supply and ambient ambient temperature (CAPACITY-FT, 
HIR-FT),  so the AQUASTAT-T setpoint should have no effect unless you also 
define the curves; these hooks were added in case someone had data and 
wanted to model this effect.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>DOE-2.2 allows you to create libraries of boilers, 
chillers, VAV systems, etc.; similar to the material, construction, and window 
libraries of 2.1e (store the components in USRLIB.DAT).  If you have 
performance data for components that you would like to share, why not post them 
to this site so that others can include them in their libraries?</FONT></DIV>
<BLOCKQUOTE dir=ltr 
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
  <A title=fporter@archenergy.com href="mailto:fporter@archenergy.com">Fred 
  Porter</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A title=BLDG-SIM@gard.com 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Wednesday, February 12, 2003 4:58 
  PM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [BLDG-SIM] Boiler Performance 
  Curves</DIV>
  <DIV><FONT face=Arial size=2></FONT><FONT face=Arial size=2></FONT><FONT 
  face=Arial size=2></FONT><FONT face=Arial size=2></FONT><FONT face=Arial 
  size=2></FONT><FONT face=Arial size=2></FONT><FONT face=Arial 
  size=2></FONT><BR></DIV>Additionally:<BR>First, in DOE2.x, if I'm not 
  mistaken, the BOILER "MIN-RATIO," or cycling threshold, holds the efficiency 
  (PLR modified EIR) constant below the specified PLR, contrary to reality and 
  intuition. I think this input defaults to a PLR of 20%, just a bit above where 
  boiler efficiency starts to really go down the tubes. So this needs to be 
  dropped to a very low value(where your EIR-fPLR curve goes wacko) if you roll 
  your own curves.<BR><BR>Aquastat temp (under BOILER), and HW reset 
  scheds(HW-LOOP) can also have  major effects. Actually you need to create 
  another custom curve(HIR-FT), and reduce the aquastat minimum, if you want the 
  HW temp to interact with the boiler, which it most certainly does. See the 
  DOE2.2 BOILER docs.<BR><BR>Also, if you set up your model with optimistic 
  assumptions (most defaults), you may miss many hours at very low (<5%) 
  heating loads.<BR><BR>In any case, most modulating boilers go down to 20 or 
  25%, and so may not show great savings compared to a 33% low 
  fire.<BR><BR>A method of calculating part load efficiency for boilers is 
  outlined in the spreadsheets that can be downloaded from:<BR><A 
  class=moz-txt-link-freetext 
  href="http://www.keh-ee.com/cycling.htm">http://www.keh-ee.com/cycling.htm</A><BR><BR>These 
  require some modification and care in use for purpose of developing DOE2 
  curves. Steady-state efficiency may vary somewhat with load, producing the 
  manufacturer's cited increase in efficiency at 50% load. This cited efficiency 
  improvment may also take into account some assumed HW reset, much as ARI NPLV 
  chiller points include condenser "relief," at the lower loads.<BR><BR>GOOD 
  LUCK! In consideration of the other thread: Even with 3D IFC/DXF interfaces, 
  architects (are any still reading) should not attempt 
  this.<BR><BR>Fred<BR><BR>Wade McLaughlin wrote:<BR>
  <BLOCKQUOTE cite=mid:MDAEMON-F200302121304.AA0428750pd80000347763@gard.com 
  type="cite">
    <META content="MSHTML 6.00.2800.1106" name=GENERATOR>
    <STYLE></STYLE>

    <DIV><FONT face=Arial size=2>Hello All,</FONT></DIV>
    <DIV><FONT face=Arial size=2></FONT> </DIV>
    <DIV><FONT face=Arial size=2>As part of a comprehensive energy study for a 
    new elementary school, we are analyzing fuel savings opportunities 
    for a proposed boiler with fully modulating burners as 
    compared to a base-case sectional lo-hi-lo boiler.  So far, we have 
    found that, all things being equal, there are no significant savings 
    associated with such a measure (at least not for the boiler size and models 
    we've been considering).</FONT></DIV>
    <DIV><FONT face=Arial size=2></FONT> </DIV>
    <DIV><FONT face=Arial size=2>We use PowerDOE for most of our energy 
    simulations.  In the course of this study, we have come to question the 
    default boiler part-load heat-input-ratio curve (</FONT><FONT 
    face=Arial size=2> HW-Blr-HIR-fPLR) found in Bdllib.dat.  Until now, we 
    have applied this curve to most base-case boiler calculations (perhaps 
    mistakenly?).  Does anyone know of the origins of this curve or what it 
    would have been based upon?  Most manufacturers we have spoken with 
    state that peak boiler efficiency occurs between 25% and 50% load.  
    Using the default curve, peak performance occurs at full 
    load and efficiency decreases by nearly 10% at half 
    load.</FONT></DIV>
    <DIV> </DIV>
    <DIV><FONT face=Arial size=2>Also, if this curve is in error, can anyone 
    suggest a method for developing a more reasonable curve 
    estimate?</FONT></DIV>
    <DIV> </DIV>
    <DIV><FONT face=Arial size=2>Thanks,</FONT></DIV>
    <DIV><FONT face=Arial size=2>Wade</FONT></DIV>
    <DIV> </DIV>
    <DIV><FONT face=Arial size=2>Wade McLaughlin<BR>DMI<BR>450 Lexington 
    St.<BR>Newton, MA  02466<BR>p 617-527-1525 x103<BR>f  
    617-527-6606</FONT></DIV><PRE><BR>======================================================<BR>You received this e-mail because you are subscribed <BR>to the <A class=moz-txt-link-abbreviated href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A> mailing list.  To unsubscribe <BR>from this mailing list send a blank message to <BR><A class=moz-txt-link-abbreviated href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</A><BR></PRE></BLOCKQUOTE><BR><PRE class=moz-signature cols="$mailwrapcol"></PRE><BR><PRE>======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>