Additionally:<br>
First, in DOE2.x, if I'm not mistaken, the BOILER "MIN-RATIO," or cycling
threshold, holds the efficiency (PLR modified EIR) constant below the specified
PLR, contrary to reality and intuition. I think this input defaults to a
PLR of 20%, just a bit above where boiler efficiency starts to really go
down the tubes. So this needs to be dropped to a very low value(where your
EIR-fPLR curve goes wacko) if you roll your own curves.<br>
<br>
Aquastat temp (under BOILER), and HW reset scheds(HW-LOOP) can also have 
major effects. Actually you need to create another custom curve(HIR-FT),
and reduce the aquastat minimum, if you want the HW temp to interact with
the boiler, which it most certainly does. See the DOE2.2 BOILER docs.<br>
<br>
Also, if you set up your model with optimistic assumptions (most defaults),
you may miss many hours at very low (<5%) heating loads.<br>
<br>
In any case, most modulating boilers go down to 20 or 25%, and so may not
show great savings compared to a 33% low fire.<br>
<br>
A method of calculating part load efficiency for boilers is outlined in the
spreadsheets that can be downloaded from:<br>
<a class="moz-txt-link-freetext" href="http://www.keh-ee.com/cycling.htm">http://www.keh-ee.com/cycling.htm</a><br>
<br>
These require some modification and care in use for purpose of developing
DOE2 curves. Steady-state efficiency may vary somewhat with load, producing
the manufacturer's cited increase in efficiency at 50% load. This cited efficiency
improvment may also take into account some assumed HW reset, much as ARI
NPLV chiller points include condenser "relief," at the lower loads.<br>
<br>
GOOD LUCK! In consideration of the other thread: Even with 3D IFC/DXF interfaces,
architects (are any still reading) should not attempt this.<br>
<br>
Fred<br>
<br>
Wade McLaughlin wrote:<br>
<blockquote type="cite" cite="mid:MDAEMON-F200302121304.AA0428750pd80000347763@gard.com">
  <meta content="MSHTML 6.00.2800.1106" name="GENERATOR">
  <style></style>
  <div><font face="Arial" size="2">Hello All,</font></div>
  <div> </div>
  <div><font face="Arial" size="2">As part of a comprehensive energy study
for a new  elementary school, we are analyzing fuel savings opportunities
for a  proposed boiler with fully modulating burners as compared to a  base-case
sectional lo-hi-lo boiler.  So far, we have found that, all  things being
equal, there are no significant savings associated with such a  measure (at
least not for the boiler size and models we've been  considering).</font></div>
  <div> </div>
  <div><font face="Arial" size="2">We use PowerDOE for most of our energy
 simulations.  In the course of this study, we have come to question the
 default boiler part-load heat-input-ratio curve (</font><font face="Arial" size="2">
HW-Blr-HIR-fPLR) found in Bdllib.dat.  Until now, we have applied  this curve
to most base-case boiler calculations (perhaps mistakenly?).   Does anyone
know of the origins of this curve or what it would have been based  upon? 
Most manufacturers we have spoken with state that peak boiler  efficiency
occurs between 25% and 50% load.  Using the default  curve, peak performance
occurs at full load and efficiency  decreases by nearly 10% at half load.</font></div>
  <div> </div>
  <div><font face="Arial" size="2">Also, if this curve is in error, can anyone
suggest  a method for developing a more reasonable curve estimate?</font></div>
  <div> </div>
  <div><font face="Arial" size="2">Thanks,</font></div>
  <div><font face="Arial" size="2">Wade</font></div>
  <div> </div>
  <div><font face="Arial" size="2">Wade McLaughlin<br>
DMI<br>
450 Lexington  St.<br>
Newton, MA  02466<br>
p 617-527-1525 x103<br>
f   617-527-6606</font></div>
  <pre><br>======================================================<br>You received this e-mail because you are subscribed <br>to the <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</a> mailing list.  To unsubscribe <br>from this mailing list send a blank message to <br><a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</a><br></pre>
  </blockquote>
  <br>
  <pre class="moz-signature" cols="$mailwrapcol">

</pre>
  <br>
  </body>
  </html>
<PRE>

======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE>