class=750244719-05022003>I am not a definitive authority, but I do not believe
that ASHRAE 90.1 or LEED requires DOE-2.1e exclusively. Section 11.2.1 of
90.1-1999 & 2001 requires "a program such as, but not limited to, DOE-2 or
BLAST." It then outlines required capabilities of the simulation
program. </SPAN><SPAN class=750244719-05022003>eQUEST is DOE-2 based, so I
believe that it is acceptable for 90.1 compliance and LEED
scoring.</SPAN></FONT></FONT></FONT></DIV>
<DIV><SPAN class=750244719-05022003>
<P><FONT face=Arial color=#0000ff size=2>Eric Christensen<BR>Econergy
International Corporation<BR>3825 Iris Avenue, Suite 350<BR>Boulder, CO
80301<BR>Phone: (303) 473-9007<BR>Fax: (303) 473-9060<BR>E-mail:
christensen@econergy.net<BR>Website: www.econergy.net </FONT></P></SPAN></DIV>
<DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma
size=2>-----Original Message-----<BR><B>From:</B> postman@gard.com
[mailto:postman@gard.com]<B>On Behalf Of </B>Chris Jones<BR><B>Sent:</B>
Wednesday, February 05, 2003 12:22 PM<BR><B>To:</B>
BLDG-SIM@GARD.COM<BR><B>Subject:</B> [BLDG-SIM] eQuest/DOE-2.2 User's
Group<BR><BR></FONT></DIV>We use DOE2.1e in our shop. Primarily because of
the significant verification against measured data that has been done on DOE2.1e
over the years. The other reason is that ASHRAE 90.1 and in particular
LEED require simulation using DOE2.1e. <BR><BR>Here in Canada, the Model
National Energy Code, Performance Option required simulation using EE4 (a free
compliance tool http://www.ee4.com ) that used the DOE2.1e engine from Hirsh and
Associates. Similar to eQuest, you can use EE4 to quickly generate an
input file then edit it for you particular situation.<BR><BR><BR><BR><BR><BR>
<BLOCKQUOTE class=cite cite="" type="cite"><FONT face=arial color=#000080
size=2>We use eQuest extensively, sometimes using the wizard mode to get
started, sometimes not. We began using DOE2.1d when it was first available on
PC platforms and kept with it through PowerDOE and the `never officially
released DOE2.2. We often use eQuest to create BDL code which we then edit
with a text editor. I must admit I m sometimes surprised to hear of
modelers (often in Academic situations) still working with 2.1e when `2.2 is a
significant improvement and is absolutely free via eQuest.
<BR></FONT><BR><FONT face=arial color=#000080 size=2>I, like John, am holding
off on EnergyPlus until I can justify the tremendous expense of training my
people on a new product that is still not ready for prime time. Eventually, I
hope, but not yet. I m guessing five years before there is a product that is
enough better than eQuest to justify the investment. (And that s assuming
eQuest doesn t continue to improve). <BR></FONT><BR><FONT face=arial
color=#000080 size=2>I imagine that there are numerous eQuest users that are
not aware of the BLDG-SIM forum. Too bad it would be nice to see more
interaction around the eQuest program. Perhaps SCE/EDR could provide an
information blurb about this forum on their web site or to everyone who down
loads eQuest.<BR></FONT><BR><FONT face=arial color=#000080
size=2> <BR></FONT><BR><FONT face=arial color=#000080
size=2> <BR></FONT><BR><FONT face=arial color=#000080 size=2>Mark E.
Case, P.E.<BR></FONT><BR><FONT face=arial color=#000080 size=2>etc Group,
Inc.<BR></FONT><BR><FONT face=arial color=#000080 size=2>Salt Lake City,
Utah<BR></FONT><BR><FONT face=arial color=#000080
size=2> <BR></FONT><BR><FONT face=tahoma size=2>-----Original
Message-----<BR><B>From:</B> postman@gard.com [<A
href="mailto:postman@gard.com" eudora="autourl">mailto:postman@gard.com</A>]
<B>On Behalf Of </B>Mike Roberts<BR><B>Sent:</B> Tuesday, February 04, 2003
1:03 PM<BR><B>To:</B> BLDG-SIM@GARD.COM<BR><B>Subject:</B> [BLDG-SIM]
eQuest/DOE-2.2 User's Group<BR></FONT><BR><FONT
face="Times New Roman, Times"> <BR></FONT><BR><FONT
face="Times New Roman, Times">John,<BR></FONT><BR><FONT
face="Times New Roman, Times"> <BR></FONT><BR><FONT
face="Times New Roman, Times">There are at least a few of us out here using
eQUEST/DOE-2.2 on a regular basis. I started using DOE-2.1 back when it
was Cal-ERDA 1.3 (about 1979) and have followed the Hirsch upgrades through
PowerDOE and eQUEST. I have only seen a Beta version of eQUEST 3.0, but
it looks very interesting.<BR></FONT><BR><FONT
face="Times New Roman, Times"> <BR></FONT><BR><FONT
face="Times New Roman, Times">My specialty is energy simulation and I use
eQUEST and the "Detailed Data Edit" Mode on almost all of our energy
simulation jobs. JJ Hirsch and Associates are looking for ways to offer
more support, but probably at a price. I can offer some support, free if
it is trivial (to me) or at my regular rates if it is more involved. Our
web site is <A
href="http://www.roberts-engineering.com/">http://www.roberts-engineering.com/</A>.
Hopefully, you will find some useful information there.<BR></FONT><BR><FONT
face="Times New Roman, Times"> <BR></FONT><BR><FONT
face="Times New Roman, Times">I think the User Group is a good idea, though
you already have a discussion forum through <A
href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A>. Let me know how
much interest you get.<BR></FONT><BR><FONT
face="Times New Roman, Times"> <BR></FONT><BR><FONT
face="Times New Roman, Times">Mike</FONT>
<DL><FONT face=tahoma size=2>
<DD>-----Original Message-----
<DD>From:</B> postman@gard.com [<A href="mailto:postman@gard.com"
eudora="autourl">mailto:postman@gard.com</A>]On Behalf Of </B>Aulbach, John
<DD>Sent:</B> Tuesday, February 04, 2003 11:43 AM
<DD>To:</B> BLDG-SIM@gard.com
<DD>Subject:</B> [BLDG-SIM] eQuest/DOE-2.2 User's Group</FONT><FONT
face="Times New Roman, Times" size=2>
<DD>May I ask how many people are attempting to use eQuest/DOE-2.2? I would
like to form a User Group for exchanging questions and war stories, as the
creators of the program do not apparently have funding for very much support
(Sad).</FONT><FONT face="Times New Roman, Times" size=2>
<DD>I have taken Marlin Addison's a few times, with the last version I have
(3.0) FINALLY beginning to make sense. I have used DOE-2.1 since 1984 and
have some small familiarity with the intent, switches, and boundaries of the
program. Until a decent front end come along for EnergyPlus, this is the way
I am going.</FONT><FONT face="Times New Roman, Times" size=2>
<DD>There claims to be over 7,000 downloads of the program. Anyone getting
into the "world past the Wizards" yet?</FONT> <BR><BR><FONT
face="Times New Roman, Times">
<DD></FONT><FONT face="Times New Roman, Times" size=2>
<DD>John R. Aulbach, PE, CEM</FONT> <FONT size=2>
<DD>Project Engineer</FONT> <FONT size=2>
<DD>Sempra Energy Solutions</FONT> <FONT size=2>
<DD>555 West Fifth Street</FONT> <FONT size=2>
<DD>Mail Location 27F3</FONT> <FONT size=2>
<DD>Los Angeles, CA 90013</FONT> <FONT size=2>
<DD>Tel: (213) 244-8551 Cell (213) 219-4875</FONT> <FONT size=2>
<DD></FONT> <BR><BR><FONT face="Times New Roman, Times" size=2>
<DD>"Sempra Energy Solutions is not the same company as SDG&E/ SoCalGas,
the Utilities. Sempra Energy Solutions is not regulated by the
California Public Utilities Commission, and you do not have to buy Sempra
Energy Solutions products or services to continue to receive quality
regulated service from the Utilities." </FONT><FONT
face="Times New Roman, Times">
<DD></FONT> </DD></DL><BR><PRE><FONT face="Courier New, Courier" size=2> </FONT></PRE><FONT
face="Courier New, Courier"></FONT><BR><PRE><FONT face="Courier New, Courier" size=2> </FONT></PRE><FONT
face="Courier New, Courier"></FONT><BR><PRE><FONT face="Courier New, Courier" size=2>==================</FONT></PRE><FONT
face="Courier New, Courier"></FONT><BR><PRE><FONT face="Courier New, Courier" size=2>You received this e-mail
because you are subscribed
</FONT></PRE><FONT face="Courier New, Courier"></FONT><BR><PRE><FONT face="Courier New, Courier" size=2>to the BLDG-SIM@GARD.COM
mailing list. To unsubscribe
</FONT></PRE><FONT face="Courier New, Courier"></FONT><BR><PRE><FONT face="Courier New, Courier" size=2>from this mailing list send
a blank message to
</FONT></PRE><FONT face="Courier New, Courier"></FONT><BR><PRE><FONT face="Courier New, Courier" size=2>BLDG-SIM-UNSUBSCRIBE@GARD.COM</FONT></PRE><FONT
face="Courier New, Courier"></FONT><BR>
<DIV align=center><FONT size=1>etc Group, Inc. 3481 South
2300 East, Salt Lake City, Utah 84109 (801) 278-1927, FAX
(801) 278-1942<BR></FONT></DIV><BR><FONT size=1>Normal.dot
2/4/2003 2:33 PM<BR></FONT><BR>
<DIV align=center><FONT size=1>etc Group, Inc. 3481 South
2300 East, Salt Lake City, Utah 84109 (801) 278-1927, FAX
(801) 278-1942<BR></FONT></DIV><BR><FONT size=1>Normal.dot
2/4/2003 2:33 PM<BR></FONT><BR>
<DIV align=center><FONT size=1>etc Group, Inc. 3481 South
2300 East, Salt Lake City, Utah 84109 (801) 278-1927, FAX
(801) 278-1942<BR></FONT></DIV><BR><FONT size=1>Normal.dot
2/4/2003 2:33 PM<BR></FONT><BR>
<DIV align=center><FONT size=1>etc Group, Inc. 3481 South
2300 East, Salt Lake City, Utah 84109 (801) 278-1927, FAX
(801) 278-1942<BR></FONT></DIV><BR><FONT size=1>Normal.dot
2/4/2003 2:33 PM<BR></FONT><BR>
<DIV align=center><FONT size=1>etc Group, Inc. 3481 South
2300 East, Salt Lake City, Utah 84109 (801) 278-1927, FAX
(801) 278-1942<BR></FONT></DIV><BR><FONT size=1>Normal.dot
2/4/2003 2:33 PM<BR></FONT><BR>
<DIV align=center><FONT size=1>etc Group, Inc. 3481 South
2300 East, Salt Lake City, Utah 84109 (801) 278-1927, FAX
(801) 278-1942<BR></FONT></DIV><BR><FONT size=1>Normal.dot
2/4/2003 2:33 PM<BR></FONT><BR>
<DIV align=center><FONT size=1>etc Group, Inc. 3481 South
2300 East, Salt Lake City, Utah 84109 (801) 278-1927, FAX
(801) 278-1942<BR></FONT></DIV><BR><FONT size=1>Normal.dot
2/4/2003 2:33 PM</BLOCKQUOTE><X-SIGSEP>
<P></X-SIGSEP><BR>Chris Jones, P. Eng.<BR>14 Oneida Avenue<BR>Toronto, ON M5J
2E3<BR>Tel. 416 203-7465<BR>Fax. 416
203-8249<BR><BR><BR></FONT></P><PRE>
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>