<DIV><SPAN class=963345512-28082002><FONT face=Arial color=#0000ff size=2>Thanks 
for your helpful response..  </FONT></SPAN></DIV>
<DIV><SPAN class=963345512-28082002><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=963345512-28082002><FONT face=Arial color=#0000ff size=2>At the 
moment we analyze buildings during the schematic phase of the project to compare 
envelope, systems & plant alternatives.  So we don't go into the 
details that you describe but we might have to in the future to show compliance 
with energy conservation codes before submitting construction documents.  
We model hotels the way architects design it during the schematic phase with 
modifications to eliminate the details but keeping the design intent 
intact.  This means the different space types (meeting rooms, gymnasiums, 
indoor swimming pools, laudry, restaurants, lobbies, etc.) and area 
configurations requiring different design criteria and systems requirements 
are maintained.  There is no problem using DOE2.1E for hotels since the 
rooms are served by FCUs  or induction units with heating and cooling 
coils.  In the case of FCUs the outdoor air is supplied to the corridor and 
transferred to the room.  There is only one exhaust system <SPAN 
class=931472413-28082002>in a hotel </SPAN>for the bathroom which can be 
modelled in DOE2.1E.  So DOE2.1E can handle hotels.  In the case 
of high rise apartment buildings there can be 3 exhaust systems (bathroom, 
kitchen & dryer) with different air quantities and operating 
schedules.  At the moment we have to treat the exhaust systems as 
one system and use the weighted average values of the operating profile 
fractions.  </FONT></SPAN></DIV>
<DIV><SPAN class=963345512-28082002><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=963345512-28082002><SPAN class=931472413-28082002><FONT 
face=Arial color=#0000ff size=2>We also have a solution for dealing with the 
other issues that I raised.  They were (1) varying the outdoor air based on 
occupancy (using CO2 sensors) independently of the supply air in a VAV system 
and (2) under-floor air distribution versus ceiling air distribution.  I 
was interested in finding out how others handled these situations.  DOE2.1E 
also does not allow duplicate systems using the LIKE/EXCEPT keywords.  This 
is awkward when dealing with floor by floor airhanding units in a high-rise 
buildings with two or more units per floor and served by one or 
more separate outdoor air handling units</FONT></SPAN></SPAN></DIV>
<DIV><SPAN class=963345512-28082002><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=963345512-28082002><FONT face=Arial color=#0000ff size=2>Thanks 
again for your response.</FONT></SPAN></DIV>
<DIV><SPAN class=963345512-28082002><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=963345512-28082002><FONT face=Arial color=#0000ff 
size=2>Varkie</FONT></SPAN></DIV>
<DIV><SPAN class=963345512-28082002></SPAN><FONT 
face=Tahoma><BR></FONT></DIV></DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma 
  size=2>-----Original Message-----<BR><B>From:</B> Aulbach, John 
  [mailto:JAulbach@semprasolutions.com]<BR><B>Sent:</B> Tuesday, August 27, 2002 
  3:15 PM<BR><B>To:</B> Bldg-sim@gard.com<BR><B>Subject:</B> [Bldg-sim] 
  Apartment/hotel DOE-2.1E systems.<BR><BR></FONT></DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff 
  size=2>Always glad to help a fellow Chicagoan. Even though I now live in 
  California.</FONT></SPAN></DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff size=2>Back 
  in the days I did energy modeling for Hilton Hotels, I would always divide the 
  hotel Guest Tower up into several levels of occupancy. Since only one side of 
  a typical hotel room faces the external (solar/transmission) and hotels rooms 
  usually have drapes closed, I didn't worry too much about outdoor fenestration 
  or transmission conditions versus the effect of internal load and, of course, 
  outside air on the room.</FONT></SPAN></DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff size=2>I 
  then divided the hotel guest rooms up into three or four (as many as six) 
  occupied levels, as hotel occupancies are roller coasters of conventions, 
  holiday periods, and every else in between. I made a group of guest rooms 
  fully occupied, and a group partially occupied, and a third group lightly 
  occupied (assuming a three way division).</FONT></SPAN></DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff size=2>I 
  then chose the FOUR PIPE INDUCTION system for my HVAC. This system allows for 
  Primary AND Secondary heating and cooling coils. The Primary coils would 
  temper the outside airflow, and the secondary would attack the combination of 
  the primary tempered and the induced room air. The Induction ratio became the 
  ratio of all fan coil airflow (say 500 guest room x 200 CFM/fan coil) to the 
  total outside air.</FONT></SPAN></DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff size=2>This 
  is direct ventilation of the guest rooms and/or the corridor are pulled into 
  the guest room and further treated by the fan coils. And exhaust air is 
  permitted in this SYSTEM-TYPE.</FONT></SPAN></DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff size=2>High 
  rise apartment living areas can be handled in the same way. 
  </FONT></SPAN></DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff size=2>I 
  thank Bruce Birdsall, one of the original DOE-2 developers at Lawrence 
  Berkeley Labs  for teaching me this trick.</FONT></SPAN></DIV>
  <DIV><SPAN class=225101720-27082002><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV>
  <DIV><SPAN class=225101720-27082002>
  <DIV><FONT color=#0000ff size=4><STRONG>John R. Aulbach, PE, 
  CEM</STRONG></FONT></DIV>
  <DIV><FONT size=2><STRONG>Project Engineer</STRONG></FONT></DIV>
  <DIV><FONT size=2><STRONG>Sempra Energy Solutions</STRONG></FONT></DIV>
  <DIV><FONT size=2><STRONG>555 West Fifth Street</STRONG></FONT></DIV>
  <DIV><FONT size=2><STRONG>Mail Location 27F3</STRONG></FONT></DIV>
  <DIV><FONT size=2><STRONG>Los Angeles, CA 90013</STRONG></FONT></DIV>
  <DIV><FONT size=2><STRONG>Tel: (213) 244-8551 Beeper (888) 
  520-1051</STRONG></FONT></DIV>
  <DIV><STRONG><FONT size=2></FONT></STRONG> </DIV>
  <P align=left><B><FONT face="Courier New" size=1>"Sempra Energy Solutions is 
  not the same company as SDG&E/ SoCalGas, the Utilities.  Sempra 
  Energy Solutions is not regulated by the California Publi</FONT><FONT 
  face="Courier New" size=1>c Utilities Commission, and you do not have to buy 
  Sempra Energy Solutions products or services to continue to receive quality 
  regulated service from the Utilities."  </FONT></B></P></SPAN></DIV><PRE>
======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>