<!doctype html public "-//w3c//dtd html 4.0 transitional//en">
<html>
<body bgcolor="#FFFFFF">
One caveat, I think. I don't think DOE2.1 will automatically adjust ARI
EIR for reduced design tower flow. The DOE2 correlations are based on the
water T from the tower. The standard ARI chiller conditions are for 3 gpm/ton.
If you input 2 gpm/ton tower water, you need to manually change the DOE2
chiller EIR to represent the off-ARI chiller EIR at 85F from the tower,
and 100F back at full load. The magnitude of that change is very chiller-dependent,
but adding .05-.10 kW/ton isn't a bad start.
<p>I think the same holds true for CHW flow/dT, but the magnitude of the
effect(usually of decreasing flow/increasing dT) is less because the chiller
lift isn't changed except a little bit by slightly decreased heat transfer
coefficients.
<p>I actually never ran the hourly reports on this; so ....
<p>Alec Stevens wrote:
<blockquote TYPE=CITE><font face="Arial"><font size=-1>John,</font></font><font face="Arial"><font size=-1>As
far as I know, the nominal capacity and EIR numbers are as you say - 100%
load, 44/85.</font></font> </blockquote>
--
<br>Fred W. Porter
<br>Senior Engineer
<br>Architectural Energy Corp.
<br>2540 Frontier Ave. Suite 201
<br>Boulder CO 80301
<br>email: fporter@archenergy.com
<br>
</body>
</html>
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM