<DIV><FONT face=Arial size=2>John,</FONT></DIV>
<DIV><FONT face=Arial size=2>As far as I know, the nominal capacity and EIR 
numbers are as you say - 100% load, 44/85.  </FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>The default curves for modifying the capacity and 
EIR as functions of CHW and CW temperature will return a value of 1.00 at 44 and 
85.  What DOE does is use the hourly values for CHW and CW temp and then 
multiplies the nominal EIR and capacity by the results of the other 
formulae.  For example, if you are modeling CW reset, and your CW temp goes 
down in the spring or fall, then the vaule of the EIR f(CHW, CW) formula will 
return less than 1 in these conditions, and the value of capacity f (CHW, CW) 
will be greater than 1.  </FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>If you are modeling a system where CHW temp is 
always 44 and CW temp is always 85, then you don't need to mess around with the 
formulae that are based on CHW and CW temp.  However, I would use actual 
mfgr data for the chiller performance as a function of PLR, especially if you 
are modeling a rotary screw chiller or a chiller with a VFD.  
</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>If you are modeling CHW and CW temps other than 
44/85, I would also get mfgr data on the chiller performance at other points and 
use the data to create new coefficients for the curves.  I recently did a 
job where we were modeling a rotary chiller as the base case and a VFD-driven 
centrifugal with CW reset and 48 F CHW along with free cooling in the winter as 
the proposed case.  So I created and debugged all kinds of curves and 
coefficients for that job.  </FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>If you would like any more info on creating new 
curves, I can give you some tips on that - let me know.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>I would also be interested in hearing what others 
in the group have to say on this topic - if you can forward me any other 
responses you have gotten, I would appreciate it.</FONT></DIV>
<DIV><FONT face=Arial size=2><BR>Sincerely,</DIV>
<DIV> </DIV>
<DIV>Alec Stevens<BR>DMI<BR>p: 617-527-1525x105<BR>f: 617-527-6606<BR>e: <A 
href="mailto:astevens@dmiinc.com">astevens@dmiinc.com</A><BR></FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV> ----- Original Message ----- </DIV>
<BLOCKQUOTE dir=ltr 
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
  <DIV 
  style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
  <A title=JAulbach@semprasolutions.com 
  href="mailto:JAulbach@semprasolutions.com">Aulbach, John</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A title=BLDG-SIM@gard.com 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Friday, June 15, 2001 5:02 PM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [BLDG-SIM] Defining a chiller 
  size and E-I-R in DOE-2.1E</DIV>
  <DIV><BR></DIV>
  <P><FONT face=Arial size=2>I don't currently have a DOE-2 Engineering 
  Document, so this question is posed to the DOE "gods and gurus":</FONT> </P>
  <P><FONT face=Arial size=2>There are three curves that modify the 
  (capacity)/(part load ratio)/(electric input ratio) in DOE-2 (or PowerDOE or 
  eQuest) of a chiller (let's use a hermetic centrifugal chiller for this 
  example).  Within PLANT, there is a place to insert a "nominal capacity" 
  and an "electric input ratio".</FONT></P>
  <P><FONT face=Arial size=2>The question is, whatever I put into these input 
  slots represent what? ARI conditions? 100% design?</FONT> </P>
  <P><FONT face=Arial size=2>And then the three curves modify these vs. load, 
  entering condenser water, and exiting chilled water. So the 100% point is what 
  (full load, 44 DegF CHW leaving, and 85 DegF Condens.water 
entering?</FONT></P>
  <P><B><FONT face=Arial size=2>John R. Aulbach, PE, CEM</FONT></B> <BR><FONT 
  face=Arial size=2>Project Engineer</FONT> <BR><FONT face=Arial size=2>Sempra 
  Energy Solutions</FONT> <BR><FONT face=Arial size=2>555 West Fifth 
  Street</FONT> <BR><FONT face=Arial size=2>Mail Location 27F3</FONT> <BR><FONT 
  face=Arial size=2>Los Angeles, CA 90071</FONT> <BR><FONT face=Arial size=2>Tel 
  :(213) 244-8551 Beeper (888) 520-1051</FONT> </P>
  <P><FONT face="Times New Roman" size=2>"Sempra Energy Solutions is not the 
  same company as SDG&E/ SoCalGas, the Utilities.  Sempra Energy 
  Solutions is not regulated by the California Public Utilities Commission, and 
  you do not have to buy Sempra Energy Solutions products or services to 
  continue to receive quality regulated service from the Utilities."  
  </FONT></P><BR><BR><PRE>
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>