Chip:
<p>Determining appropriate heat gain from office desktop computers, printers,
etc. has always been a gray area for HVAC designers.  Coming up with
real world information such as equipment nameplate power rating vs. actual
wattage consumed and suitable diversity factors have been a challenge for
load calculations.
<p>However, an excellent article titled "Heat Gain from Office Equipment"
by Wilkins and Hosni published in the June 2000 ASHRAE Journal addressed
this issue. Bottom line: about .5 to 1.0 watts per square foot. Useful
information and tables comparing nameplate data vs. measured power vs.
overall office diversity.
<p>Article is available at ASHRAE site in .pdf form.  It is one of
the more useful publications to emerge from the ASHRAE research program,
in my opinion.
<br> 
<dl>
<dd>
<font size=-1>Thomas E. Anderson</font></dd>

<dd>
<font size=-1>President</font></dd>

<dd>
<font size=-1>Cx Associates, Ltd.</font></dd>

<dd>
<font size=-1>Building Commissioning Specialists</font></dd>

<dd>
<i><font size=-1><a href="http://www.cx-assoc.com">http://www.cx-assoc.com</a></font></i></dd>

<dd>
<i><font size=-1>933 Road 101</font></i></dd>

<dd>
<i><font size=-1>Jeffersonville, Vermont 05464 USA</font></i></dd>

<dd>
<i><font size=-1>hvac@cx-assoc.com</font></i></dd>

<dd>
<i><font size=-1>Tel: 802-644-5616 Fax: 802-644-6797</font></i></dd>
</dl>

<p>Chip Barnaby wrote:
<blockquote TYPE=CITE>Greetings --
<p>Does anyone have good source(s) for typical operating condition assumptions
<br>for various building occupancies?
<p>We're assembling a library that includes setpoints, lighting power density,
<br>occupant density, plug loads, etc plus associated schedules. 
The data will
<br>be used for load (sizing) calcs, so we're looking for representative
design
<br>values.  However, info for energy calcs would also be helpful.
<p>Thanks for any leads.
<br>---------------------------------------------------------
<br>Chip Barnaby                  
cbarnaby@wrightsoft.com
<br>Vice President of Research
<br>Wrightsoft Corp.              
781-862-8719 x118 voice
<br>394 Lowell St, Suite 12        781-861-2058
fax
<br>Lexington, MA 02420           
www.wrightsoft.com
<br>---------------------------------------------------------
<p>======================================================
<br>You received this e-mail because you are subscribed
<br>to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe
<br>from this mailing list send a blank message to
<br>BLDG-SIM-UNSUBSCRIBE@GARD.COM</blockquote>
</html>