[Bldg-sim] ASHRAE 90.1 zoning for System 7 - variable temp and humidity requirements

Madhav Munshi mmunshi at kohlerronan.com
Thu Feb 13 09:37:22 PST 2025


Thanks Bill - I should have added that the space setpoints for humidity and temperature will be consistent for Proposed and Baseline in all options.

But if different space temp and humidity configs are in the same system, there is still some creep/loss/gain of humidity across spaces. Will have to test this all ways to see what works best and within the language of ASHRAE 90.1.



MADHAV MUNSHI BEMP

Senior Associate

mmunshi at kohlerronan.com<mailto:mmunshi at kohlerronan.com>



KOHLER RONAN | Consulting Engineers

171 Madison Avenue, New York, NY 10016

212.695.2422



________________________________
From: Bill Bishop <William.J.Bishop at imegcorp.com>
Sent: Thursday, February 13, 2025 12:07 PM
To: Madhav Munshi <mmunshi at kohlerronan.com>; bldg sim <bldg-sim at lists.onebuilding.org>
Subject: RE: ASHRAE 90.1 zoning for System 7 - variable temp and humidity requirements


Hi Madhav,



I suggest you consider adding separate single-zone systems for select spaces based on interpreting G3.1.1.c (if you’re modeling per Appendix G).

If you go the simple route and model one System 7 per floor in the Baseline, it could be argued that you should model the Proposed design with the same humidification for the entire floor, the same as the Baseline is modeled. (See language in Table G3.1 No.4 that “Temperature and humidity control set points and schedules… shall be the same for proposed design and baseline building design.”

If your project allows for flexibility in modeling approach (i.e. you don’t have to follow a strict interpretation of Appendix G.) then your Option 2 of modeling multiple Systems 7 matching your Proposed zoning makes sense.



Regards,

~Bill



William Bishop, PE, CEM, LEED AP, ASHRAE (BEMP, BEAP, CDP)
Senior Associate / Sustainability & Energy Engineer of Distinction

[Pathfinder | now IMEG]<https://pathfinder-ea.com/>

Pathfinder | now IMEG                                                           (585) 698-1956 | phone

134 South Fitzhugh Street | Rochester, NY 14608                  (315) 879-1122 | mobile

William.J.Bishop at imegcorp.com<mailto:William.J.Bishop at imegcorp.com>  website<https://pathfinder-ea.com/> | vCard<https://dynasend.com/signatures/vcard/William.J.Bishop-at-imegcorp.com.vcf> | map<https://www.google.com/maps/place/Pathfinder+Engineers+%26+Architects+LLP/@43.1504815,-77.6145058,17z/data=!3m1!4b1!4m6!3m5!1s0x89d6b4fe9e48aab1:0x6991ae3d559d5aee!8m2!3d43.1504776!4d-77.6119309!16s%2Fg%2F1tcw955j?hl=en&entry=ttu> [Twitter] <https://merlin.allaboutbirds.org/>   [Facebook] <https://fossilfreefunds.org/>   [LinkedIn] <https://www.linkedin.com/company/imeg-corp>

Learn more<https://www.imegcorp.com/news_events/new-york-based-pathfinder-engineers-joins-imeg/> about our transition to IMEG.   Ride your bike!  [A person on a motorcycle  Description automatically generated]



From: Bldg-sim <bldg-sim-bounces at lists.onebuilding.org> On Behalf Of Madhav Munshi via Bldg-sim
Sent: Thursday, February 13, 2025 10:53 AM
To: bldg sim <bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] ASHRAE 90.1 zoning for System 7 - variable temp and humidity requirements



External Email: Treat links and attachments with caution.

Hello everyone,



We are working on a project - 5 floors and greater than 200,000sf. Each floor has spaces with different temperature and humidity requirements.



For example

Space type 1: 70F - 50% RH Strict control

Space type 2: 70-75F 40% min - 60% max RH,

Space type 3: 70-75F 50% max RH summer only



This happens on all floors.



Proposed zoning has spaces combined on the basis of different environmental requirements.



How would you approach the zoning for the ASHRAE Baseline?

  1.  One System 7 per floor: If we do floor by floor, we will be adding system level humidification for all spaces on that floor and allow whatever happens to each room. Definitely might end up humidifying spaces that don't need humidification
  2.  Multiple Systems per floor: Split up each floor zoning by temp and humidity and have multiple Sys 7's per floor.
  3.  Alternative Approach??

What do you all think? I am inclined to start with 1 system 7 per floor and stick with the ASHRAE requirements.



Thank you



Madhav



MADHAV MUNSHI | BEMP

Senior Associate

mmunshi at kohlerronan.com<mailto:mmunshi at kohlerronan.com>



[A blue and white letter k  Description automatically generated]<https://kohlerronan.com/>



KOHLER RONAN | Consulting Engineers

171 Madison Avenue, New York, NY 10016

212.695.2422 F 212.695.2423



93 Lake Avenue, Danbury, CT 06810

203.778.1017 F 203.778.1018


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250213/ef4d5ae3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 24130 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250213/ef4d5ae3/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 12799 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250213/ef4d5ae3/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 420 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250213/ef4d5ae3/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 342 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250213/ef4d5ae3/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 387 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250213/ef4d5ae3/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 2724 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250213/ef4d5ae3/attachment-0005.png>


More information about the Bldg-sim mailing list