[Bldg-sim] Lies, darn lies, and statistics
Marc Costa
mcosta at energycoalition.org
Tue Mar 14 15:17:17 PDT 2023
I've found res and nonres to have 2 very different calibration paths. Just
my 2 cents on residential - I've found it helpful to calibrate to indoor
air temp in addition to monthly energy bills. Especially in low-income
households that have a high tolerance for thermal discomfort and price
anxiety. This combined with one or two granular time series of t-stat or
HVAC loads seem to be the only way to get a sense of what actually happens
in homes. The use case is transactive energy and community level smart
local energy markets providing distribution circuit ancillary services -
pretty specific thing - but will become increasingly important in many
national and subnational initiatives.
Marc
On Tue, Mar 14, 2023 at 2:39 PM Jim Dirkes via Bldg-sim <
bldg-sim at lists.onebuilding.org> wrote:
> Thanks! Modelers will understand it readily. Clients need some explanation
> and level-setting.
>
> Jim Dirkes 1631 Acacia Drive NW Grand Rapids, MI 49504 - 616 450 8653
> *Coffee Conversation:*
>
> *The "individual" is an impossible concept, conceived by the Enlightenment
> philosophers. It makes no sense to the Christian. In marriages, and
> families, in associations and friendships and religious orders, we are not
> individuals, but a communion of persons.*
>
> ------- Original Message -------
> On Tuesday, March 14th, 2023 at 3:58 PM, Vikram Sami <
> vikram at olsonkundig.com> wrote:
>
> George Box coined that one I think
>
>
>
> *From:* Bldg-sim <bldg-sim-bounces at lists.onebuilding.org> *On Behalf Of *Jim
> Dirkes via Bldg-sim
> *Sent:* Tuesday, March 14, 2023 12:13 PM
> *To:* chris.malcolm.yates at gmail.com
> *Cc:* bldg-sim at onebuilding.org
> *Subject:* Re: [Bldg-sim] Lies, darn lies, and statistics
>
>
>
> I think Dru Crawley coined the phrase, "All models are wrong. Some are
> useful."
>
>
>
> Chris, you highlighted an assortment of variables which are omnipresent,
> inconsistent and uncontrollable - so what, exactly, does your client
> expect? Is it a realistic expectation? For example, are they going to nail
> you to the wall when, inevitably, you are "wrong" next year?
>
>
>
> I have not calibrated many models, but have been made more appreciative of
> all the uncontrollables by the ones I calibrated :(. All the statisticians
> know that there is always more than one solution which will result in a
> high R2 value or low CVRSME, so which is correct?
>
>
>
> Rather than a calibrated model, lately I've been encouraging clients to
> consider one of the FDD platforms on top of their Building Automation
> System. Spending time and money to evaluate whether things are working
> properly makes more sense to me - it's "real life" vs a prediction. (Can't
> forget to mention thoughtful and thorough commissioning here; that's
> essential.)
>
>
>
> ps, I love your thoughtful approach. You're setting a great example! One
> aspect of that is to reach out to the wider modeling community to gather
> input and feedback.
>
>
>
> Jim Dirkes 1631 Acacia Drive NW Grand Rapids, MI 49504 - 616 450 8653
>
> *Coffee Conversation:*
>
> The "individual" is an impossible concept, conceived by the Enlightenment
> philosophers. It makes no sense to the Christian. In marriages, and
> families, in associations and friendships and religious orders, we are not
> individuals, but a communion of persons.
>
>
>
> ------- Original Message -------
> On Tuesday, March 14th, 2023 at 2:10 PM, chris.malcolm.yates at gmail.com <
> chris.malcolm.yates at gmail.com> wrote:
>
>
> I think I need to qualify this: informed by G14, but definitely not
> compliant with it! There is some allowance for repairing or “healing” data,
> but when the data has a lot of holes or modes/ category variables then
> forget it. This is my case, but the client still wants some kind of
> representative simulation.
>
>
>
> Monthly models can be garbage. School holidays cut across months at
> different times, combined heat and power is popular which complicates gas
> usage especially when metering is limited… did the heat by-product of
> electricity generation go to the building, or was it rejected? They can
> work for heating in our temperate climate, but not for cooling.
>
>
>
> Nevertheless, we need some kind of representative simulation model. We
> can’t make any ECM qualifying claims but we can do something useful. This
> is where these methods can give you a lot of insight before you start
> modelling.
>
>
>
> I hadn’t tried the IMT previously. We tend to have limited our regression
> analysis to monthly “degree day” methods (your 2p model, I think). I
> plugged some project specific daily electricity data into the MVR example
> (multi variate regression) and it seemed to give decent CVRMSE (~2-3%) but
> low R2 (~0.7). However, it appeared to provide some insight on cooling
> usage (monthly 2p models are meaningless for this in the UK’s temperate
> climate).
>
>
>
> I also made some 2p monthly models of gas. I thought these were good until
> I compared successive years. *I guess this is were understanding a range
> of statistical indices is helpful.*
>
>
>
> Here’s the final rub, because the underlying data has so many
> inconsistencies that can only be made sense of with some regression models,
> it’s easier to “calibrate” the simulation model to the regression models
> than the original data. But I may use 2p monthly for gas, daily MVR for
> electric…
>
>
>
> So I need to ask if I have wondered completely off-piste with this!
>
>
>
> Chris
>
>
>
> *From:* David Eldridge <dancingdavide at hotmail.com>
> *Sent:* Tuesday, March 14, 2023 12:53 PM
> *To:* Jim Dirkes <jvdirkes2 at protonmail.com>
> *Cc:* chris.malcolm.yates at gmail.com; bldg-sim at onebuilding.org
> *Subject:* Re: [Bldg-sim] Lies, darn lies, and statistics
>
>
>
> Indirectly there probably isn’t a daily set of metrics in the Guideline
> since the simulation programs aren’t usually outputting daily results, but
> there’s no reason there couldn’t be one statistically.
>
>
>
> You could make one if you had only daily utility data and had to aggregate
> the simulation results to daily totals, there isn’t a published target
> metric but you could still show that you calculated one and why you think
> it was a good or bad result.
>
>
>
> DSE Mobile
>
>
>
> On Mar 14, 2023, at 6:10 AM, Jim Dirkes via Bldg-sim <
> bldg-sim at lists.onebuilding.org> wrote:
>
>
>
> Dear Chris,
>
> Kudos for appreciating a gap in your understanding. (I'm in your camp)
>
>
>
> On the other hand, there are SO many variables in building operation that,
> short of a highly instrumented (and carefully calibrated) building for
> everything from lights to people to plug loads to HVAC - calibration is a
> fiction (and I'm confident that no such building exists). Daily calibration
> is a complete fiction, perhaps even a deception. On top of that, a
> "calibrated" model is just a moment in time; everything going forward is
> guaranteed to be different than during the calibration time period.
>
>
>
> I think of "calibration" as more like a sensitivity analysis - determine
> which variables matter more and which matter less. GenOpt works nicely for
> that purpose https://github.com/lbl-srg/GenOpt
> <https://nam02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fgithub.com%2Flbl-srg%2FGenOpt&data=05%7C01%7Cvikram%40olsonkundig.com%7C23d28a6b405f47b5562808db24c09278%7Cd5b3df51a48046ba8f92ef77dd2c7d72%7C0%7C0%7C638144181738291281%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=dqFeAoOGreAjFSPjUPx7jYjnk6VDzoAgDtyGVo0z4DQ%3D&reserved=0>
>
>
>
> Jim Dirkes 1631 Acacia Drive NW Grand Rapids, MI 49504 - 616 450 8653
>
> *Coffee Conversation:*
>
> The "individual" is an impossible concept, conceived by the Enlightenment
> philosophers. It makes no sense to the Christian. In marriages, and
> families, in associations and friendships and religious orders, we are not
> individuals, but a communion of persons.
>
>
>
> ------- Original Message -------
> On Tuesday, March 14th, 2023 at 6:52 AM, Chris Yates via Bldg-sim <
> bldg-sim at lists.onebuilding.org> wrote:
>
> Hi All
>
>
>
> I do find ASHRAE Guideline 14 a little too hardcore for my basic
> understanding of statistics. I can plug any of the equations into Excel,
> but I’ve realised my statistics understanding is very limited! (I’m outed!)
>
>
>
> We don’t actually have to work to G14 in the UK (probably good because my
> copy is a bit old). I finally realised I didn’t know enough after I’d been
> (lazily) using R2 in Excel on some monthly data. I thought that R2 > 0.9
> was generally ok… yeah, it wasn’t.
>
>
>
> So, are there any easy to understand resources available?
>
>
>
> I’ve been messing around with the IMT as well. It’s been fun going back to
> DOS 😊. This got me into daily methods, which leads to my next question.
> Is there any reason why there isn’t a daily calibration option specified in
> G14?
>
>
>
> Many thanks!
>
>
>
> Chris Yates
>
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> <https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fbldg-sim-onebuilding.org&data=05%7C01%7Cvikram%40olsonkundig.com%7C23d28a6b405f47b5562808db24c09278%7Cd5b3df51a48046ba8f92ef77dd2c7d72%7C0%7C0%7C638144181738291281%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=3GlZl01UE3n9OolRQ9aaVR9PpXGKfw%2BUnhMR2WKvBsw%3D&reserved=0>
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
--
CONFIDENTIALITY NOTE: The information in this email is intended only for
the use of the individual or entity named above. If you may have received
this message in error, please email or call the sender. If you are not the
intended recipient, any dissemination, distribution or copying is strictly
prohibited.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20230314/8397a054/attachment.htm>
More information about the Bldg-sim
mailing list