[Bldg-sim] Mass Stretch Code: TEDI calcs
smartin at shaunmartinconsulting.com
smartin at shaunmartinconsulting.com
Thu Jul 27 15:58:27 PDT 2023
Hi Madhav,
TEDI is a metric for the building envelope and ventilation load performance.
You can sum heating (ONLY) coil loads to determine the output. This is a
clip from the guideline we use in Canada (BC) that explains it. M.F.Area is
building area excluding unconditioned indoor parking area, but including all
other partially and unconditioned areas. So yes, the answer is option B,
excluding the cooling. It is not the peak (A) and does not include heating
system efficiency (C).
Shaun
Shaun Martin, BEMP, LEED-BD&C
Principal
Shaun Martin Consulting
<mailto:smartin at shaunmartinconsulting.com>
smartin at shaunmartinconsulting.com
+1-604-789-1095
From: Bldg-sim <bldg-sim-bounces at lists.onebuilding.org> On Behalf Of Madhav
Munshi via Bldg-sim
Sent: Thursday, July 27, 2023 2:14 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Mass Stretch Code: TEDI calcs
Hi group,
Hope everyone is doing well. We are working on a school building in MA and
need to perform "TEDI" models. I've read through the documentation and am a
little confused if it's a load metric or an energy metric. The limits are
expressed in kBtu/sf/year in the code language, but some of the supporting
documentation about how to extract this from equest/IES/ energy plus makes
me feel like it's a load metric. It has to be one the three and it seems
like its option B
A. Peak Heating and Cooling load per SF
B. Sum of annual heating and cooling loads (annual) per SF - without
efficiency accounting
C. Sum of annual heating and cooling energy per SF - with efficiency
accounting
https://www.mass.gov/doc/updated-guidelines-for-tedi-and-ashrae-app-g-modeli
ng/download
Appreciate your responses!
Thank you
Madhav
<https://kohlerronan.com/>
MADHAV MUNSHI BEMP
Senior Associate
<mailto:mmunshi at kohlerronan.com> mmunshi at kohlerronan.com
KOHLER RONAN | Consulting Engineers
171 Madison Avenue, New York, NY 10016
212.695.2422
<http://kohlerronan.com/>
<https://www.facebook.com/Kohler-Ronan-LLC-Consulting-Engineers-146070618769
600/> <https://twitter.com/KohlerRonan>
<https://www.linkedin.com/company/1672806?trk=hp-feed-company-name>
<https://www.instagram.com/kohler_ronan/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20230727/03c8a845/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.jpg
Type: image/jpeg
Size: 883 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20230727/03c8a845/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image012.png
Type: image/png
Size: 944 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20230727/03c8a845/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.png
Type: image/png
Size: 1045 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20230727/03c8a845/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image014.png
Type: image/png
Size: 1011 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20230727/03c8a845/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image015.png
Type: image/png
Size: 2021 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20230727/03c8a845/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 209226 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20230727/03c8a845/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 13568 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20230727/03c8a845/attachment-0005.png>
More information about the Bldg-sim
mailing list