[Bldg-sim] emissivity of air
Horowitz, Scott
Scott.Horowitz at nrel.gov
Fri Jul 14 07:52:10 PDT 2023
Note that EnergyPlus v9.3 (May 2020) introduced the Carroll MRT model as an alternate interior radiant heat exchange algorithm.
* Input: https://bigladdersoftware.com/epx/docs/22-2/input-output-reference/group-simulation-parameters.html#zone-radiant-exchange-algorithm
* Engineering description: https://bigladdersoftware.com/epx/docs/22-2/engineering-reference/inside-heat-balance.html#carrollmrt
That said, I can’t speak to whether the model captures all effects we’re talking about here.
Scott
From: Bldg-sim <bldg-sim-bounces at lists.onebuilding.org> On Behalf Of Chris Yates via Bldg-sim
Sent: Friday, July 14, 2023 8:10 AM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] emissivity of air
CAUTION: This email originated from outside of NREL. Do not click links or open attachments unless you recognize the sender and know the content is safe.
In this episode of throwback Friday, we’ll revisit the subject of water vapor’s damping effect on radiant temperatures!
To my knowledge, only IES, the CSE as described by Chip, and possibly ESP-r model this effect within the zone model. E+ version 9 certainly doesn’t.
I recently revisited some IES simulations with the Riyad weather file with and without the effect enabled. It had up to 1.5 Celsius effect on MRT for a large space with direct adiabatic spray cooling in the AHU.
Comfort was still pretty bad (that’s why the contractor went for chillers and fan coils instead 😊). However, it might not be such an insignificant effect that it can be ignored especially in locations such as atria and warehousing.
Also, interestingly, this is essentially a greenhouse effect – water vapor being a greenhouse gas.
For those wishing to know more, the write-up in IES apache methods succinctly describes the effect. https://help.iesve.com/ve2021/long_wave_radiation_heat_transfer.htm
Chris
From: Chris Yates <chris.malcolm.yates at gmail.com<mailto:chris.malcolm.yates at gmail.com>>
Sent: Tuesday, April 4, 2017 12:05 PM
Cc: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] emissivity of air
Thanks Chip
Isn't the sky in essence modelled as a 'superdome' in most models? I guess there may be similar algorithms in climate processors.
This is a longstanding concern of mine. MRT models are very popular, especially when considering 'less traditional' modes of cooling such as chilled beams or night cooling thermally massive buildings. However, there are issues the models. For example, my understanding is that the further a zone departs from simple convex geometry, the less valid they become. Modelling exact (i.e. non convex) geometries has become quite popular in the UK, but engineers don't realise they could be invalidating MRT calcs.
I'm fairly certain that I experienced a marked difference in results between IES with internal air emissivity on and off for a building that wasn't a 'superdome'. It was in actual fact 'a dome' - three storey's within a glazed barrel vault! I presented the more onerous set of results ultimately!
Don't be surprised if I revive this post in the months to come after I've had the opportunity to do some digging!
Many thanks
Chris
On Mon, Apr 3, 2017 at 4:58 PM, Chip Barnaby via Bldg-sim <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>> wrote:
Chris / all --
IES is not alone -- CSE (California Simulation Engine) accounts for this effect. CSE performs the simulations for CBECC-Res, the Title 24 residential compliance tool.
The CSE zone model is based on (underappreciated) work by Joe Carroll from the 1980s. See http://www.ibpsa.org/proceedings/BS2013/p_2487.pdf and papers referenced therein. In particular,
Carroll, J. A., 1980. An ‘MRT Method’ of Computing Radiant Energy Exchange in Rooms, Proc. Second Systems Simulation and Economic Analysis Conference, San Diego, CA.
At thermal wavelengths, air (especially humid air) is hazy. Depending on space size, some/most of the thermal radiant will be absorbed before it reaches other surfaces. But it takes a big space (read "SuperDome") for the effect to be very significant.
CSE creates a virtual surface that participates in the long-wave radiant network. For an example 2850 ft2 zone with 24528 ft2 surface area (including partitions) exposed to the room air, the air "surface" area is 1784 ft2 or about 7%. So the effect is modest but not entirely negligible.
Common comfort assessment methods (PMV / PPD) use MRT that is generally calculated directly from surface temperatures (in other words, ignoring the shielding effect of intervening air). That method introduces an error for large spaces but is generally a reasonable approximation.
I don't think there would be much effect on small scales that would be seen within cooling equipment.
AFAIK, EnergyPlus does not represent this effect, although I may be wrong. It certainly could, given that it uses a first-principles heat balance zone model.
Chip Barnaby
--
Charles S. "Chip" Barnaby, FIBPSA / FASHRAE
chipbarnaby at gmail.com<mailto:chipbarnaby at gmail.com>
879 Bean Rd, Moultonborough, NH 03254 USA
(o) +1 603 253 4593<tel:(603)%20253-4593> or +1 603 253 4400<tel:(603)%20253-4400> (m) +1 781 883 4593<tel:(781)%20883-4593>
----- Original message -----
From: "Chris Yates via Bldg-sim" <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>>
To: "bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>" <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>>
Subject: [Bldg-sim] emissivity of air
Date: Mon, 3 Apr 2017 13:34:31 +0100
Dear all,
In IES apache 'simulation options' there is a setting called 'Internal air emissivity model'. This model has the effect of moist air dampening higher radiant temperatures. Apparently, this effect is more pronounced in large spaces - though I haven't tested this.
IES seems to be quite unique in implementing the 'emissivity of air'.
The concept seems a little unusual to me. So, I was wondering what experiences the simulation community has of this phenomenon? Where else it may be implemented in simulation tools? And, how does it feature for common comfort temperature assessments involving some combination of radiant temperatures (e.g. operative)?
Also, might it also demonstate enhanced comfort for systems with direct adiabatic cooling in dry climates (e.g. spray bar in supply side of AHU)?
Best regards
Chris
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20230714/a7913667/attachment.htm>
More information about the Bldg-sim
mailing list