[Bldg-sim] Ground heat transfer in EnergyPlus
Joel Neymark
neymarkj at msn.com
Thu Feb 11 08:21:05 PST 2021
Hi Christoph,
We published a Ground-coupled slab BESTEST in 2009 ([full report]
https://www.nrel.gov/docs/fy09osti/45742.pdf;[BS2019 paper]
http://www.ibpsa.org/proceedings/BS2009/BS09_1099_1106.pdf). A number of
programs are compared there; this was adapted to become Section 5.2.4 of
ASHRAE Standard 140, /Method of Test for Evaluating Building Performance
Simulation Software/.
More specific to EnergyPlus (and more recently), Neal Kruis of Big
Ladder Software developed the Kiva ground heat transfer calculation
tool, which is integrated with EnergyPlus and has been "BESTESTed".
(https://bigladdersoftware.com/projects/kiva/)
There's a blurb with section header "Below-Grade Opaque Surfaces" in the
/2017 ASHRAE Handbook of Fundamentals/, p. 19.12; it gives additional
discussion. That's been updated for the soon-to-be published /2021/ /HoF/.
Cheers.
joel
Joel Neymark, P.E.
J. Neymark & Associates
Golden, CO 80401
On 2/10/2021 2:11 PM, Christoph Reinhart via Bldg-sim wrote:
>
> Dear colleagues,
>
> I am teaching a new seminar this spring where we will be digging into
> more advanced modeling features such as Trombe walls, solar chimneys
> and ground heat transfer. I cannot wait J.
>
> Regarding ground heat transfer, I know that there are a variety of
> models available within EnergyPlus from Slab to FC. I wonder if some
> of you could point me to good best practice guidelines and papers that
> compare these models. I am particular keen on modeling spaces that are
> half buried (think Frank Lloyd Wright’s Solar Hemicycle).
>
> Thank you for your help,
>
> Christoph
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message toBLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20210211/ade14024/attachment-0002.html>
More information about the Bldg-sim
mailing list