[Bldg-sim] Constant air volume systems

Rathna Shree rathnashreep at yahoo.in
Wed Sep 30 03:47:19 PDT 2020


 Dear Mr. Bob,
That helps. We have to explore for options here. 
Thank you.
Regards,Rathnashree
    On Thursday, 24 September, 2020, 01:59:12 am IST, Bob Towell <btowell at cxegroup.com> wrote:  
 
 #yiv4428069805 #yiv4428069805 -- _filtered {} _filtered {} _filtered {} _filtered {}#yiv4428069805 #yiv4428069805 p.yiv4428069805MsoNormal, #yiv4428069805 li.yiv4428069805MsoNormal, #yiv4428069805 div.yiv4428069805MsoNormal {margin:0in;font-size:11.0pt;font-family:sans-serif;}#yiv4428069805 a:link, #yiv4428069805 span.yiv4428069805MsoHyperlink {color:blue;text-decoration:underline;}#yiv4428069805 p.yiv4428069805msonormal, #yiv4428069805 li.yiv4428069805msonormal, #yiv4428069805 div.yiv4428069805msonormal {margin-right:0in;margin-left:0in;font-size:11.0pt;font-family:sans-serif;}#yiv4428069805 span.yiv4428069805EmailStyle26 {font-family:sans-serif;color:windowtext;}#yiv4428069805 .yiv4428069805MsoChpDefault {font-size:10.0pt;} _filtered {}#yiv4428069805 div.yiv4428069805WordSection1 {}#yiv4428069805 
Hello Rathna,
 
  
 
I would like to add a couple of thoughts.  First, we are finding moresingle zone VAV units that will vary the airflow when the load is reduced, as the fan energy savings can be significant.  As you probably know, for a given system, as you reduce the airflow by 25% you can reduce the power required by over 50%.
 
  
 
Second, the energy code is often requiring two speed control at a minimum for single zone systems, which also can greatly improve humidity control as well.  With the cost of variable frequency drives so low today, some are finding a VFD more cost effective than a 2-speed motor.  Another reason for a VFD on a system without VAV boxes.
 
  
 
As Bill noted, this application should be defined by the design engineer, etc.
 
  
 
Hope this is helpful.
 
  
 
Robert L. (Bob) Towell, P.E., LEED AP, CCP, FASHRAE
 

 
20A Edwardsville Professional Park
 
Edwardsville, Illinois 62025-3602
 
Phone:  618-307-5882
 
Cell:      314-591-6543
 
  
 
CxE Group is a women (and veteran) owned business.
 
  
 
From: Rathna Shree <rathnashreep at yahoo.in> 
Sent: Wednesday, September 23, 2020 8:19 AM
To: Bishop, Bill <bbishop at pathfinder-ea.com>
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Constant air volume systems
 
  
 
Thank you Mr. Bill for the clarification. This helps.
 
  
 
On Tuesday, 22 September, 2020, 06:07:15 pm IST, Bishop, Bill <bbishop at pathfinder-ea.com> wrote:
 
  
 
  
 
Hi Rathnashree,
 
You need to know more about the air handling unit and system (controls, ductwork and zone dampers, if any) to know how to simulate the minimum flow associated with a VFD. An AHU may be designed as a constant volume unit and still use a VFD to balance the system at a fixed flowrate. You don’t automatically get energy savings by using a VFD, and you actually incur a small energy penalty associated with drive losses. If the system does not have any adjustable zone dampers that are automatically controlled, it may be designed to operate at constant volume, and you would use a minimum flow ratio of 1. If the unit only handles a small number of zones, it may be designed to run at constant volume. I suggest you ask the design engineer how the unit will be controlled. You can also look for a controls drawing or talk to a factory rep for that unit.
 
Regards,
 
~Bill
 
 
 
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
 
Senior Energy Engineer
 
 
 
T: (585) 698-1956                       F: (585) 325-6005
 
bbishop at pathfinder-ea.com        www.pathfinder-ea.com
 
134 South Fitzhugh Street
 
Rochester, NY 14608                     Ask me why Carbon Fee & Dividend may be right for you.
 
 
 
From: Bldg-sim <bldg-sim-bounces at lists.onebuilding.org>On Behalf Of Rathna Shree via Bldg-sim
Sent: Tuesday, September 22, 2020 7:39 AM
To: bldg <bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Constant air volume systems
 
 
 
Dear All,
 
 
 
In many of our projects, we have Air handling units with VFD and no VAV system. When simulated with minimum flow ratio as 1 and AHU with VFD, there is no difference in energy consumption. The impact of with and without VFD is negligible. Since there will be a small amount of variation in Airflow in zones due to VFD in AHU, can we reduce the minimum flow ratio from 1 to about 0.8 or 0.7?
 
 
 
Regards,
 
Rathnashree
   
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20200930/b9304495/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1554 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20200930/b9304495/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1903 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20200930/b9304495/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 8038 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20200930/b9304495/attachment-0005.jpg>


More information about the Bldg-sim mailing list