[Bldg-sim] Simulating Heat Pump Chiller in eQuest Software
Bishop, Bill
bbishop at pathfinder-ea.com
Mon Oct 12 05:31:01 PDT 2020
Hi Ahmad,
Heat pump chillers in eQUEST can serve chilled water loops and 2-pipe loops. To serve hot water loads, you have to use a 2-pipe loop. I like to model heat pump chillers with a 2-pipe loop that is dedicated to heating loads by using a high outdoor snap temperature. Heat pump chillers are covered in the help documentation as water-to-water heat pumps. I suggest you join the equest-users list equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>.
[cid:image001.png at 01D6A071.FBF5D8F0]
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2][Logo Description automatically generated]
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image006.png at 01D6A071.FBF5D8F0] Ask me why Carbon Fee & Dividend may be right for you.
From: Bldg-sim <bldg-sim-bounces at lists.onebuilding.org> On Behalf Of Ahmad Fraij via Bldg-sim
Sent: Saturday, October 10, 2020 12:50 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Simulating Heat Pump Chiller in eQuest Software
Hello Everyone,
I am trying to simulate heat pump chiller in eQuest software but I could not. I know that I can select heat pump chiller in the detailed mode but how to connect it to the hot water loop and to the hot water coils?
Any help will be much appreciated.
Regards
Ahmad
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20201012/98ffe081/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 7845 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20201012/98ffe081/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20201012/98ffe081/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 21586 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20201012/98ffe081/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 1554 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20201012/98ffe081/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 2178 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20201012/98ffe081/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 3103 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20201012/98ffe081/attachment-0008.jpg>
More information about the Bldg-sim
mailing list