Hi Alex,

Ok, I see. Thanks for sending this info. Yes it all points to modelling the
same heating system in baseline and proposed and efficiency improvements or
credits for infrared heaters can be taken into account.

Thank You



Syed Hussaini, PE, LEED GA

Energy Engineer II
------------------------------

*Partner **Energy*

680 Knox St., Suite 150 |Los Angeles, CA 90502
D: 310-622-8851 | C: 480-512-9739 | F: 310-862-2399

www.ptrenergy.com | shussaini at ptrenergy.com

P please consider the environment before printing this e-mail


On Tue, Aug 25, 2020 at 10:47 AM Chapin, Alex N <
Alex.Chapin at masonandhanger.com> wrote:

> Hi Syed,
>
>
>
> The baseline system types are only applicable to conditioned portions of
> the building (hence why exception a) to Section G3.1.1 uses the term
> conditioned floor area). Therefore, since you indicate that the Proposed
> design is semiheated for freeze protection only (you should double check
> the definition of semiheated space in the Section 3.2 definitions though),
> the Baseline System would be modeled as heating only of the same type as
> the proposed, but you can take credit for any efficiency improvements if
> applicable.
>
>
>
> Alex
>
>
>
> *Alex Chapin* EIT, BEMP, LEED AP BD+C, O+M
> Energy Engineer | Mason & Hanger
> A Day & Zimmermann Company
> *O *804.521.7072
> 4880 Sadler Road, Suite 300 | Glen Allen, VA 23060
> masonandhanger.com <http://www.masonandhanger.com/>
>
> An ISO 9001 Certified Company <https://www.masonandhanger.com/about/iso>
>
> *Building a More Secure World ®*
>
> CAUTION - THIS EMAIL MAY CONTAIN CONFIDENTIAL INFORMATION
>
> This electronic mail transmission and any accompanying documents may
> contain information belonging to the sender, which may be proprietary,
> confidential, and/or otherwise subject to restrictions on disclosure beyond
> the intended recipient. This information is intended only for the use of
> the individual or entity to whom this electronic mail transmission was sent
> as indicated above. If you are not the intended recipient, any disclosure,
> copying, distribution, or action taken in reliance on the contents of the
> information contained in this transmission is strictly prohibited. If you
> have received this transmission in error, please call 1-703-955-5702 and
> delete this transmission. Thank you.
>
>
>
>
>
>
>
>
> *From:* Syed Safiuddin Hussaini [mailto:safi.hussaini91 at gmail.com]
> *Sent:* Tuesday, August 25, 2020 12:50 PM
> *To:* Jim Dirkes <Jim at fsmgmt.co>
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] rintveld at ptrenergy.com
>
>
>
> Jim,
>
>
>
> Thank for sending this info. Actually ASHRAE 90.1-2007 code did not have
> this option for semi heated spaces which I was using for a 179d  project.
> This makes sense.
>
>
>
> Thank You
>
>
>
>
>
>
> Syed Hussaini, PE, LEED GA
>
> Energy Engineer II
> ------------------------------
>
> *Partner **Energy*
>
> 680 Knox St., Suite 150 |Los Angeles, CA 90502
> D: 310-622-8851 | C: 480-512-9739 | F: 310-862-2399
>
> www.ptrenergy.com
> <https://urldefense.com/v3/__http:/www.ptrenergy.com/__;!!EsbUyp2cb-_kIuQ!sbQ64k9hDKeMlYsLrGkWDdSWNOBl_9YEgwL8rOaYZ_93m5fJ_la7b-kjH5rWmboIEeIAdE8$>
> | shussaini at ptrenergy.com
>
> P please consider the environment before printing this e-mail
>
>
>
>
>
> On Tue, Aug 25, 2020 at 4:34 AM Jim Dirkes <Jim at fsmgmt.co> wrote:
>
> I think your Baseline HVAC system should be System #9 or #10
>
>
>
> >From 90.1-2013
>
>
>
> *James V Dirkes II, PE, BEMP, BCxP*
>
> Team Lead - Building Performance
>
> 616 450 8653
>
> Foresight Management
>
> *https://fsmgmt.co/
> <https://urldefense.com/v3/__https:/fsmgmt.co/__;!!EsbUyp2cb-_kIuQ!sbQ64k9hDKeMlYsLrGkWDdSWNOBl_9YEgwL8rOaYZ_93m5fJ_la7b-kjH5rWmboIrprv3H4$>*
>
> LinkedIn
> <https://urldefense.com/v3/__https:/www.linkedin.com/in/jim-dirkes-4134447/__;!!EsbUyp2cb-_kIuQ!sbQ64k9hDKeMlYsLrGkWDdSWNOBl_9YEgwL8rOaYZ_93m5fJ_la7b-kjH5rWmboImzDaaCs$>
>
>
>
> *Coffee Conversation:*
>
> Are we mistaking an increase of communication for an increase of
> communion? Is basic human loneliness driving us ever deeper into a culture
> of dislocated virtual relationships that temporarily relieve symptoms but
> worsen the disease?
> ------------------------------
>
> *From:* Bldg-sim <bldg-sim-bounces at lists.onebuilding.org> on behalf of
> Syed Safiuddin Hussaini via Bldg-sim <bldg-sim at lists.onebuilding.org>
> *Sent:* Monday, August 24, 2020 9:10 PM
> *To:* bldg-sim at lists.onebuilding.org <bldg-sim at lists.onebuilding.org>
> *Subject:* [Bldg-sim] rintveld at ptrenergy.com
>
>
>
> Hello All,
>
>
>
> I am doing an Appendix G model for a warehouse building that has a
> semi-heated space for freeze protection only by using infrared heaters. But
> it is a 35,000 SFT warehouse building and if I go by Table G3.1.1A the
> system type to be used will be System 5 Packaged VAV with Reheat in the
> Baseline 90.1 model and I would have infrared radiant heaters in the
> proposed model. Should I use the same system type in both Baseline and
> Proposed model i.e. infrared radiant heaters with same efficiencies and
> temperature setpoints or can the Baseline system be Packaged VAV with
> Reheat and infrared radaint heaters in the proposed model ?
>
> Thank You
>
> Syed Hussaini, PE, LEED GA
>
> Energy Engineer II
> ------------------------------
>
> *Partner **Energy*
>
> 680 Knox St., Suite 150 |Los Angeles, CA 90502
> D: 310-622-8851 | C: 480-512-9739 | F: 310-862-2399
>
> www.ptrenergy.com
> <https://urldefense.com/v3/__http:/www.ptrenergy.com/__;!!EsbUyp2cb-_kIuQ!sbQ64k9hDKeMlYsLrGkWDdSWNOBl_9YEgwL8rOaYZ_93m5fJ_la7b-kjH5rWmboIEeIAdE8$>
> | shussaini at ptrenergy.com
>
> P please consider the environment before printing this e-mail
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20200825/bd013a6f/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 51683 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20200825/bd013a6f/attachment-0004.png>