[Bldg-sim] Proposed model fan power question
Jim Dirkes
Jim at fsmgmt.co
Mon May 20 07:51:57 PDT 2019
Christopher,
It seems to me that the Proposed system fan power, and whether filter pressure drop is partially or fully included, is a design decision.
I always use that the flow and pressure values shown on the fan equipment schedules, assuming the design engineer has specified performance to include whatever is deemed appropriate.
James V Dirkes II, PE, BEMP, BCxP
Team Lead - Building Performance
616 450 8653
Foresight Management
https://fsmgmt.co/
Coffee Conversation:
… just as loving what is good is sanctity, or the health of the will
....so seeing what is there is sanity, or the health of the intellect.
There is the will: it’s work is to love and so to choose, to decide, to act.
There is the intellect: its work is to know, to understand, to see. To see what? To see what’s there.
________________________________
From: Jim Dirkes
Sent: Monday, May 20, 2019 10:34 AM
To: bldg-sim at lists.onebuilding.org; Jones, Christopher
Subject: Re: Proposed model fan power question
Christopher,
It seems to me that the Proposed system fan power, and whether filter pressure drop is partially or fully included, is a design decision.
I always use that the flow and pressure values shown on the fan equipment schedules, assuming the design engineer has specified performance to include whatever is deemed appropriate.
James V Dirkes II, PE, BEMP, BCxP
Team Lead - Building Performance
616 450 8653
Foresight Management
https://fsmgmt.co/
Coffee Conversation:
… just as loving what is good is sanctity, or the health of the will
....so seeing what is there is sanity, or the health of the intellect.
There is the will: it’s work is to love and so to choose, to decide, to act.
There is the intellect: its work is to know, to understand, to see. To see what? To see what’s there.
________________________________
From: Bldg-sim <bldg-sim-bounces at lists.onebuilding.org> on behalf of Jones, Christopher via Bldg-sim <bldg-sim at lists.onebuilding.org>
Sent: Friday, May 17, 2019 12:29 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Proposed model fan power question
When determining the proposed model fan power should we use clean filter pressure drops or partially loaded filter pressure drops? It isn’t entirely clear when looking at the Baseline pressure drop credits – two of the filter credits specify clean filter pressure drop and two ignore the topic. Table 6.5.3.1.1B 90.1-2010.
Christopher R. Jones, P.Eng.
Senior Building Performance Specialist
Sustainability & Energy
[cid:image001.png at 01D50CAC.1C820950]
T+ 1 416-644-0252
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com
Please consider the environment before printing...
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190520/846a92ac/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 1860 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190520/846a92ac/attachment-0002.png>
More information about the Bldg-sim
mailing list