[Bldg-sim] Exhaust Air Energy Recovery - 90.1-2010 6.5.6.1
Jones, Christopher
Christopher.r.Jones at wsp.com
Mon Oct 15 05:28:49 PDT 2018
Thank you David.
I agree with your assessment. The issue that leads me to consider heat recovery in the Baseline is that the proposed system has a run around loop so obviously the designer and the building code officials consider this general exhaust safe enough for run around heat recovery and hence it should apply to the baseline as well.
Christopher R Jones, P.Eng.
T+ 1 416-644-0252
[cid:image001.png at 01D46461.118BD8D0]
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of David Eldridge via Bldg-sim
Sent: Friday, October 12, 2018 5:44 PM
To: bldg-sim at onebuilding.org
Subject: Re: [Bldg-sim] Exhaust Air Energy Recovery - 90.1-2010 6.5.6.1
I'd look at these factors:
* Is the maintenance garage part of exception b for partially heated and not cooled spaces? Just wanted to make sure that one was also considered.
* Snorkel exhaust clearly toxic and perhaps corrosive, apply exception c.
* "General" exhaust - the air stream isn't itself at toxic levels as long as the room is maintained within the established bounds, but the contaminants are still toxic (although diluted) - I would say technically the exception c language doesn't say that the airstream is toxic, it says that the system is exhausting toxic fumes - which would still be true for CO and NOx. Mainly the point being: Would there be justification to exclude heat recovery systems that have a potential for cross-over like we do for laboratories?
If you contrast this to a laboratory, the idea is that modulation plus sensible heat recovery can remove the 50% effectiveness requirement, which allows use of a runaround coil to achieve heat recovery at a lower effectiveness but maintain higher air quality as well as potential corrosion of equipment where the options to make a runaround system may be more durable than a heat wheel.
Vehicle CO and NOx might be in the same category as the laboratory chemicals that cause us to avoid any potential for crossover, and which makes heat wheels and their high effectiveness inappropriate for the application. Obviously for a lab you get funneled to 6.5.7.2 which lets you use a less effective system that wouldn't apply to a vehicle facility - the vehicle facility would be exempted instead of passing to a lower requirement, although a runaround system could be considered if the owner still wanted to increase efficiency beyond code.
Similarly you may also encounter an argument for exception h if the two exhaust streams are similar magnitude airflows instead of a 75/25 split, but you could still put a partial heat recovery system on the project for improving over the code requirements.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Associate
Direct: (847) 316-9224 | Mobile: (773) 490-5038
Grumman/Butkus Associates | 820 Davis Street, Suite 300 | Evanston, IL 60201
Energy Efficiency Consultants and Sustainable Design Engineers
grummanbutkus.com<http://grummanbutkus.com/> | Blog<http://grummanbutkus.com/blog> | Facebook<https://www.facebook.com/pages/GrummanButkus-Associates/1385285015032526> | Twitter<https://twitter.com/grummanbutkus>
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher via Bldg-sim
Sent: Thursday, October 11, 2018 9:29 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Exhaust Air Energy Recovery - 90.1-2010 6.5.6.1
I have a vehicle maintenance garage. It has a typical two exhaust system configuration. The main MUA and associated exhaust fan control the level of CO, NOx, etc. in the space such that the level of contaminates never gets to toxic levels. The second exhaust system consists of snorkels that directly attach to the vehicle exhaust pipe. This system doesn't dilute the exhaust therefore Exception c., "Systems exhausting toxic, flammable, paint, or corrosive fumes or dust".
I am of the opinion that the general make-up air and exhaust system controls the system such that the exhaust is not at the point of being toxic and the exception doesn't apply?
Christopher R Jones, P.Eng.
T+ 1 416-644-0252
[cid:image003.png at 01D46461.118744F0]
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20181015/38105676/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 1860 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20181015/38105676/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 1860 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20181015/38105676/attachment-0005.png>
More information about the Bldg-sim
mailing list