[Bldg-sim] ASHRAE 90.1-2013 App G Modeling- DHW System Efficiency
Nathan Miller
nathanm at rushingco.com
Tue Nov 20 10:48:59 PST 2018
All,
When modeling 90.1-2013 Appendix G Baseline buildings on projects with relatively large DHW plants (>1,000,000 BTUH), what do you believe would be an appropriate performance curve for the equipment? Specifically, if the baseline is required to have a 90% Et boiler/heater, that seems to fall in-between what I'd consider to be condensing or non-condensing boilers/heaters.
Under 90.1-2010 App G modeling we typically would use standard non-condensing curves for the 80% efficient baseline DHW heater, and if high-efficiency condensing units (92% or greater efficiency) were specified in the proposed, we would apply an appropriate curve for a condensing boiler, which obviously offers significant savings for low incoming water temps, such as with a DHW heater.
Obviously in 2013, much of that credit is gone because we compare to a 90% efficient baseline, but it seems like there might still be some reasonable performance-curve savings to be had if you compare condensing to non-condensing technology. We looked in the AHRI database, and there is very little equipment that is rated at 90% efficiency (basically just a few 50 gal single-family-scale tank heaters). For commercial equipment, there is essentially a performance gap between the "near-condensing" boilers (top out around 88% efficient) and the condensing boilers (start at about 92% efficient). So there isn't a "real-world" piece of equipment to look at to establish a performance curve.
What have you all been modeling for this scenario?
Example- Multifamily High Rise Project with > 1,000,000 BTUH of DHW boilers (gas fired).
Baseline details:
Equipment per G3.1.1-2, efficiency per 7.4.2:
[cid:image005.png at 01D480D7.C61A18B0]
Table G3.1.1-2 dictates baseline equipment type would be gas-storage-heaters:
[cid:image006.png at 01D480D7.C61A18B0]
7.4.2 sends you to table 7.8 for efficiency requirements:
[cid:image008.png at 01D480D7.C61A18B0]
Table 7.8 would nominally require 80% Et equipment, which would fairly obviously be a standard non-condensing heater, but footnote f of the table sends you to 7.5.3
[cid:image010.png at 01D480D7.C61A18B0]
[cid:image017.png at 01D480D7.C61A18B0]
7.5.3 requires 90% Et equipment:
[cid:image018.png at 01D480D7.C61A18B0]
Thanks,
Nathan Miller, PE, LEED AP BD+C - Mechanical Engineer/Senior Energy Analyst
RUSHING | O 206-285-7100 | C 207-650-3942
www.rushingco.com<http://www.rushingco.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20181120/5154adf0/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 273522 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20181120/5154adf0/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 270674 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20181120/5154adf0/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 115896 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20181120/5154adf0/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 135415 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20181120/5154adf0/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image017.png
Type: image/png
Size: 108587 bytes
Desc: image017.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20181120/5154adf0/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image018.png
Type: image/png
Size: 106760 bytes
Desc: image018.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20181120/5154adf0/attachment-0005.png>
More information about the Bldg-sim
mailing list