[Bldg-sim] reflective ceramic paint
Bishop, Bill
bbishop at pathfinder-ea.com
Thu May 24 08:48:23 PDT 2018
Hi Leen,
We have discussed reflective paints a couple times in the forums - back in September 2017 here<http://energy-models.com/forum/discourse/general-discussion/experience-modeling-ceramic-insulation-coating> and in more detail in 2011 here<http://energy-models.com/forum/ceramic-insulating-paint-additives#comment-11419>.
I have not used the products. Research and anecdotes question the value of “ceramic insulation” paints. It is doubtful that they impact R-value in any meaningful way. You can try modeling it by varying the absorptance and/or emissivity of the wall, if the product you are considering provides those values.
The main thing to realize is at best, paints can affect radiative heat transfer, but do nothing for conduction, convection or infiltration.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[cid:image004.png at 01D3F355.4F862F00]134 South Fitzhugh Street
Rochester, NY 14608 Ask me why Carbon Fee & Dividend may be right for you.
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of leen peeters via Bldg-sim
Sent: Thursday, May 24, 2018 4:48 AM
To: BldgSim Mailing List <bldg-sim at onebuilding.org>; Egon Troch <egon at think-e.be>; thomas.vercammen at i-vec.be
Subject: [Bldg-sim] reflective ceramic paint
Hi,
is there anyone who ever applied this type of paint on the inside? One of the manufacturers claims it gives the effect of 7.5 cm of EPS insulation. Product is ThermaCote.
We have tried to simulate it with the reflective coating, but the impact disappears in the error margins...
Any experience and measured values would help us!
Thanks a lot!
Leen Peeters
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180524/261f5cf4/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180524/261f5cf4/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 4600 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180524/261f5cf4/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2257 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180524/261f5cf4/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 2000 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180524/261f5cf4/attachment-0001.png>
More information about the Bldg-sim
mailing list