[Bldg-sim] Need a help with energy_plus Climate Data
Joe Huang
yjhuang at whiteboxtechnologies.com
Tue Mar 27 12:37:47 PDT 2018
The difficulty of converting measured weather data to an epw depends a lot on how complete
are your data. For a usable simulation weather file, you need these six key parameters -
temperature, humidity, wind speed and direction, global horizontal and direct normal solar
radiation. The solar radiation is generally the most problematic. There are various
models that calculate solar radiation from other climate parameters, esp. cloud cover, but
there are not many publicly-available programs that have them. Also, cloud cover requires
human observation or a dedicated laser and is almost never recorded at typical weather
monitoring stations. Lastly, you have to make sure that whatever program you use
interpolates in case there are missing observations in your data stream.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 3/26/2018 6:33 AM, Ibrahim NEYA via Bldg-sim wrote:
> Hello everybody,
>
> I have measured on-site climate data and stored them in an excel sheet.
> I want to use them in energy-plus for temperature prediction in the building.
> I don't know how to put them in an epw file in order to perform the simulation.
>
> I will be happy to know that you can help me.
> Thank you for your time
>
> Regards
>
> --
>
> NEYA Ibrahim
> Energy and Electrical Engineer
> Tél : 00226 61 85 77 07
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180327/9b613e19/attachment.html>
More information about the Bldg-sim
mailing list