[Bldg-sim] Cooling Tower gpm/HP to EIR
Jones, Christopher
Christopher.r.Jones at wsp.com
Wed Mar 21 12:16:59 PDT 2018
Thanks Nick,
Silly me, looking for TWR-EIR – still back in DOE2.1e.
Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy
[cid:image001.png at 01D3C127.A697FC20]
T +1 416-644-0252
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com
Please consider the environment before printing...
From: Nicholas Caton [mailto:Nicholas.Caton at schneider-electric.com]
Sent: Wednesday, March 21, 2018 2:37 PM
To: Javed Iqbal <javedvit at gmail.com>; Jones, Christopher <Christopher.r.Jones at wsp.com>
Cc: bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Cooling Tower gpm/HP to EIR
Here’s an eQUEST expression from my toolbox that doesn’t see so much use in my current line of work. This saves you the implicit step of looking up the motor HP table (10.8) for efficiencies to determine the motor kW draw. It’s an example I commonly point to when teaching expressions to point out you can go pretty far with nested if/then statements if that’s how your mind is operating in the moment, but the results aren’t always so pretty to look at. It’s a good segue into introducing the wonderful world of switch statements. Regardless, this is functional enough:
TOWERS - kW per cell
This will determine a tower's fan power input in accordance with ASHRAE 90.1 Appendix G. Requires a #PA "Baseline CW Design GPM" which should be populated with the CW loop's GPM, following an auto-sizing run (re: PV-A or PS-D).
$Autosize your baseline tower's FAN-KW/CELL!
#PA("Baseline CW Design GPM")/38.2 $Actual HP requirement
*0.745699872 $HP to kW
/if(#PA("Baseline CW Design GPM")/38.2 < 1)
then .825
else if(#PA("Baseline CW Design GPM")/38.2 < 3)
then .840
else if(#PA("Baseline CW Design GPM")/38.2 < 7.5)
then .875
else if(#PA("Baseline CW Design GPM")/38.2 < 15)
then .895
else if(#PA("Baseline CW Design GPM")/38.2 < 25)
then .910
else if(#PA("Baseline CW Design GPM")/38.2 < 40)
then .924
else if(#PA("Baseline CW Design GPM")/38.2 < 60)
then .930
else if(#PA("Baseline CW Design GPM")/38.2 < 100)
then .936
else if(#PA("Baseline CW Design GPM")/38.2 < 150)
then .941
else .950
endif endif endif endif endif endif endif endif
endif $Incremental HP efficiency lookup, per T10.8
Hope this helps!
~Nick
[cid:image002.png at 01D3C127.A697FC20]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image003.png at 01D3C127.A697FC20]
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Javed Iqbal via Bldg-sim
Sent: Wednesday, March 21, 2018 9:21 AM
To: Jones, Christopher <Christopher.r.Jones at wsp.com<mailto:Christopher.r.Jones at wsp.com>>
Cc: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Cooling Tower gpm/HP to EIR
Hi,
There was an old post back in 2012 on this topic. Here i am pasting the excerpt from the post:
'An axial fan cooling tower is required per G3.1.3.11. Required cooling tower efficiency is 38.2 gpm/hp per ASHRAE 90.1, Table 6.8.1G. Let eQUEST autosize the cooling tower, and use the design flowrate shown on the PV-A report to determine the fan HP. Then convert to kW and enter the value in FAN-KW/CELL. The cell is normally grayed out, so right-click the cell and enter the kW value by changing the user default.'
Moreover, I do follow the same in E+ too.
Hope this helps!
On Wed, Mar 21, 2018 at 7:26 PM, Jones, Christopher via Bldg-sim <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>> wrote:
My mind is dead this morning. I can’t recall how to convert the 90.1 cooling tower fan power requirement to TWR-EIR for DOE2.2. For example, given 40.2 gpm/HP and convert Btu/Btu. Seems like you have to assume a delta-T for the condenser water flow in order to convert the gpm flow to Btu?
Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy
[cid:image001.png at 01D3C127.A697FC20]
T +1 416-644-0252
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com<http://wsp.com>
Please consider the environment before printing...
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180321/3a033bf2/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25844 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180321/3a033bf2/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 255 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180321/3a033bf2/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 8477 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180321/3a033bf2/attachment-0002.png>
More information about the Bldg-sim
mailing list