[Bldg-sim] [EnergyPlus_Support] RE: [Equest-users] White Box Technologies brings simulation weather data to the satellite age
Aaron Powers
caaronpowers at gmail.com
Tue Jan 9 14:55:54 PST 2018
Joe,
Awesome work with the solar data! DOE2 uses IRAIN to set the outside
surface temperature of roofs to the ambient wetbulb when rain is present.
E+ increases the outside heat transfer coefficient to 1000 when rain is
present, but I can't quite tell if it is reading in a rain flag or if this
is always false. Probably only a small impact on energy consumption.
Aaron
On Tue, Jan 9, 2018 at 2:11 PM, Joe Huang via Bldg-sim <
bldg-sim at lists.onebuilding.org> wrote:
> The 9-digit Present Weather Code (PW) was used only in North America
> before the turn of the century an long since replaced by a METAR 2-digit PW
> code now used in weather reports around the world. So, if the epw format
> leaves space for this old coding, it's functionally dead space and probably
> filled with 999999999 in all files except the old TMY2s and CWECs. The
> Liquid Precipitation (LP) is very different because it gives the amount of
> precipitation and time over which it occurred, typically in multiples of 6
> up to 24 hours, not whether or not there is rain during that hour. This
> makes LP reports basically unusable in simulations, which is why I spent
> several weeks back in 2015 to convert the LP in the TMY3s to hourly
> records. So, if EnergyPlus is relying on the LP field to detect the
> presence of rain, make sure that the LP has undergone such a data
> transformation. And what about snow flag, which seems to be of greater
> interest ?
>
> In my opinion, if the rain and snow flags are useful, we should take them
> from the current 2-digit METAR PWC. I've already doing that starting with
> the IWEC2 weather files, where I added an extra field for PW to the end of
> the TMY3 format, although I never made a big fuss about the format
> change. PW appears on all the weather files that I produce in the *.FIN4
> format, but it's lost in the conversion to epw nor have I bothered to use
> them to set the ISNOW and IRAIN flags in the DOE-2 bin files. To do so is
> very easy, since in the METAR PWC all instances of rain have the same
> initial digit, as do all instances of snow.
>
> Joe
>
> Joe Huang
> White Box Technologies, Inc.
> 346 Rheem Blvd., Suite 205A
> Moraga CA 94556yjhuang at whiteboxtechnologies.comhttp://weather.whiteboxtechnologies.com for simulation-ready weather data
> (o) (925)388-0265 <(925)%20388-0265>
> (c) (510)928-2683 <(510)%20928-2683>
> "building energy simulations at your fingertips"
>
> On 1/9/2018 4:32 AM, Linda Lawrie wrote:
>
> Actually, EnergyPlus (and the epw format) uses coded flags in the 9 digit
> "Present Weather Codes" to determine and set Rain/Snow. Now that some
> stations include precipitation (albeit liquid) EnergyPlus sets the rain
> flag when there is adequate precipitation currently.
>
> I believe the updated TMY3 format went away from the 9 digit present
> weather codes, so EnergyPlus would rely on the "preciitation" field in the
> epw file.
>
> It would not be impossible to bring those back to the CWEC data; however,
> probably not as individual flags.
>
> Linda
>
> At 04:44 PM 1/8/2018, Joe Huang via Bldg-sim wrote:
>
> Content-Type: multipart/alternative;
> boundary="------------E16429D68ABA1BA04C74DF5C"
> Content-Language: en-US
>
> The rain and snow flags are still available in the raw weather station
> data, but haven't been included in the processed weather files since the
> 1990's because everyone in this hemisphere at least have adopted the
> TMY2/TMY3 formats, in content if not the literal file format, developed
> by NREL, which does not include these two flags. I was also under the
> impression that none of the simulation programs, such as DOE-2, do not use
> these two flags anyway.  If these flags are of use, it would make sense
> to include them, which would not require a change in the DOE-2 *.BINM
> format, but would require a change to the EnergyPlus *.epw format.
>
> Joe
>
> Joe Huang
> White Box Technologies, Inc.
> 346 Rheem Blvd., Suite 205A
> Moraga CA 94556
> yjhuang at whiteboxtechnologies.com
> http://weather.whiteboxtechnologies.com for simulation-ready weather
> data
> (o) (925)388-0265 <(925)%20388-0265>
> (c) (510)928-2683 <(510)%20928-2683>
> "building energy simulations at your fingertips"
>
> On 1/8/2018 12:15 PM, 'Jones, Christopher' christopher.r.jones at wsp.com
> [EnergyPlus_Support] wrote:
>
> Â
>
> I have a question – what happened to the rain and snow flags that were in
> the old CWEC file but are missing in the latest versions. Many snow melting
> systems have a snow/rain sensor in the slab used to trigger the system on.
>
> Â
>
>
> *Â *
> *Christopher R. Jones*, P.Eng.
>
> Technical Specialist
>
> Sustainability & Energy
>
> Â
>
> [image: []]
>
> T +1 416-644-0252 <(416)%20644-0252>
>
> Â
>
> 2300 Yonge Street, Suite 2300
>
> Toronto, ON M4P 1E4 Canada
>
> wsp.com <http://wsp.htm>
>
>
> *Â *
>
> *Â *
>
> *Please consider the environment before printing... *
> Â
>
> Â
>
> *From:* Equest-users [ mailto:equest-users-bounces at lists.onebuilding.org
> <equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Joe Huang
> via Equest-users
> *Sent:* Tuesday, January 02, 2018 10:15 PM
> *To:* Nicholas Caton <Nicholas.Caton at schneider-electric.com>
> <Nicholas.Caton at schneider-electric.com>; BLDG-SIM
> <bldg-sim at lists.onebuilding.org> <bldg-sim at lists.onebuilding.org>;
> EnergyPlus_Support <EnergyPlus_Support at yahoogroups.com>
> <EnergyPlus_Support at yahoogroups.com>; equest-users at onebuilding.org
> *Cc:* Jim Dirkes <jim at buildingperformanceteam.com>
> <jim at buildingperformanceteam.com>
> *Subject:* Re: [Equest-users] White Box Technologies brings simulation
> weather data to the satellite age
>
> Â
>
> Nick,
>
> This is an interesting topic that has evolved in an unexpected way. Now
> that NREL has mastered the technology of satellite-derived solar radiation,
> they have regarded weather station data as an impediment, since there's no
> way to get such measured data to match the 5-kilometer grid of the
> satellite-derived solar. Therefore, they have abandoned the weather
> station data (which was was used in all the TMYs to date) and gone instead
> to Reanalysis Data from NOAA's MERRA, which is running a climate
> forecasting model in retrospective mode. I don't have time now to discuss
> reanalysis, except to say that from what I've seen the results are
> decidedly "iffy". Almost two years ago, I managed to get a Work Statement
> through ASHRAEÂ for someone to take a good look at reanalysis data.
>
> So, what does this mean for your question?  NREL's National Solar
> Radiation Data Base (NSRDB) can now get you the hourly time series or a TMY
> for more than a million grid points over the US, all with satellite-derived
> solar radiation but MERRA results for the other climate parameters.Â
> I've told NREL several years ago that for the building simulation industry
> it would be much better to merge the satellite-derived solar with actual
> station data that give good accurate coverage of urban areas where
> buildings are located. NREL's response was that they'd be happy to do this,
> but someone has to pay them for the work.
>
> In response to your hypothesis below, I think you're being too disparaging
> of the previous modeling efforts while raising too high your expectations
> of satellite solar. It's not that the previous models failed to account
> for local climate conditions, but that they lacked good data to drive
> them. For example, all models included terms for cloud cover and
> clearness, or for the more detailed physical models arcane parameters like
> aerosol optical depth, preciptable moisture, etc., but how available are
> the input data and how reliable are they? The advantages of
> satellite-derived solar are that they provide a comprehensive and objective
> view of the cloud conditions, which combined with satellite measurements of
> the atmospheric conditions and improved modeling, results in accuracies
> that previous modeling efforts can not attain. As far as discerning
> localized effects of smog and dust in urban areas, that would still depend
> on whether there's sufficient monitoring at that spatial and time scale to
> detect the differences.  What I mean is that it's one thing to observe
> that in general urban locations have more smog and particulates than rural
> locations, but it's something else to quantify the resultant differences in
> solar radiation over time and distance.
>
> I'd like to take the opportunity here to step back and comment on the
> status of weather data for the building energy community, My interactions
> with NREL has brought the realization that we have been piggy-backing on
> the efforts of others outside our community for our weather data. I don't
> intend to pick on the NREL Solar Program, several of whom I consider
> friends and colleagues, but their target client is the solar power
> industry. Since solar power arrays can be installed anywhere, preferably
> in rural uninhabited locations, it makes sense to go to satellite-derived
> solar. It's also clear that to serve that industry, NREL would focus its
> efforts on getting the best solar values, while all the other climatic
> parameters, like temperature, humidity, wind speed, etc., are secondary,
> which may be why getting them from MERRA is a satisfactory choice. The
> focus on solar is also evident in the weighting used by NREL to develop the
> TMYs, with 50% weight placed on the 2 solar and 50% on the remaining 8
> non-solar parameters.
>
> For the building energy community, or priorities are somewhat different.
> Since 99% of buildings are located in urban locations, we should focus much
> more on climate in urban areas. Luckily, that's also where the great
> majority of existing weather are located, which is why I'm resistant to
> throwing out measured weather data and replacing them with synthetic data,
> no matter how much they've been "seeded" with real data. As for the
> weighting of climate parameters in selecting the typical months, why not
> use building energy simulations and weight them by the distribution of
> heating and cooling loads?
>
> Joe
>
> Joe Huang
>
>
> White Box Technologies,
> Inc.
>
>
> 346 Rheem Blvd., Suite
> 205A
>
>
> Moraga CA
> 94556
>
>
>
> yjhuang at whiteboxtechnologies.com
>
>
>
> http://weather.whiteboxtechnologies.com for simulation-ready weather
> data
>
>
> (o)(925)388-0265 <(925)%20388-0265>
>
>
> (c)(510)928-2683 <(510)%20928-2683>
>
>
> "building energy simulations at your
> fingertips"
>
>
> On 1/2/2018 9:30 AM, Nicholas Caton wrote:
>
> Hi Joe,
>
> Â
>
> From your perspective, are NREL or any other government/professional
> bodies making moves/indications to update/refresh the current TMY3 sets to
> utilize satellite-derived solar radiation? Seems like a no-brainer for
> our industry, but is there a counter-argument? It seems likely, but has
> there been rigorous comparisons of satellite-derived solar radiation
> against measured values and/or our “present-day†solar models used to
> derive solar radiation information for building energy simulation?
>
> Â
>
> Also, I’m trying to understand and correctly characterize the impact of
> this development in simple terms my brain can follow. Is it fair to say:
>
> Â
>
> The solar models used in developing weather files for building energy
> simulations to-date in our industry (including all/most industry-standard
> TMY weather sets), because they have been using solar radiation derived
> from (evolving) solar models, have not accounted for the likes of local
> climate cloud cover / smog / dust? Seattle (~47°N) has perhaps been
> seeing as much sunlight through the winter as Paris (~48°N)?
>
> Â
>
> Does satellite-derived solar radiation address some or all of these local
> climate issues (cloud cover, smog, dust) affecting direct/indirect solar
> radiation?
>
> Â
>
> Thanks sincerely for all your teaching Joe,
>
> Â
>
> ~Nick
>
> Â
>
> [image: []]
>
> Nick Caton, P.E., BEMP
>
> Â Senior Energy Engineer
> Â Regional Energy Engineering Manager
>
> Â Energy and Sustainability Services
> Â Schneider Electric
>
> DÂ Â 913.564.6361 <(913)%20564-6361>
> MÂ Â 785.410.3317 <(785)%20410-3317>
> FÂ Â 913.564.6380 <(913)%20564-6380>
> EÂ Â nicholas.caton at schneider-electric.com
>
> 15200 Santa Fe Trail Drive
> Suite 204
> Lenexa, KS 66219
> United States
>
> [image: []]
>
> Â
>
> Â
>
> From: Equest-users [ mailto:equest-users-bounces at lists.onebuilding.org
> <equest-users-bounces at lists.onebuilding.org>] On Behalf Of Joe Huang via
> Equest-users
> Sent: Thursday, December 14, 2017 8:13 PM
> To: BLDG-SIM <bldg-sim at lists.onebuilding.org>
> <bldg-sim at lists.onebuilding.org>; EnergyPlus_Support <EnergyPlus_Support@
> yahoogroups.com> <EnergyPlus_Support at yahoogroups.com>; equest-users at lists.
> onebuilding.org
> Subject: [Equest-users] White Box Technologies brings simulation weather
> data to the satellite age
>
> Â
>
> It is with joy and some trepidation to report that White Box Technologies
> (WBT) is updating all its historical weather files with satellite-derived
> solar radiation. Joy because this overcomes what has been the most
> significant question mark with weather files; trepidation because of the
> amount of work needed to carry out and maintain this effort. To show that
> this is more than marketing hype, I need to give a rather long explanation
> about this development.
>
> The bane of weather data over the past three decades has been the solar
> radiation (global horizontal and direct normal) which are not measured
> parameters, but derived using various solar and sky models. All the
> familiar "typical year" sets, i.e., TMY, WYEC, IWEC, etc., let alone the
> historical weather files, have modeled solar radiation. Although a lot of
> work has gone into such models (see M. Iqbal,"An Introduction to Solar
> Radiation", Academic Press, 1983), there remain an almost intractible
> problem of the lack of good measured solar to tune any of these models. For
> example, in the ASHRAE IWEC2 weather files, my team was able to find one or
> two years' measured data for less than 50 locations,
> from which were derived 28 sets of regression coefficients then used for
> all 3,012 IWEC2 locations.
>
> For the past decade and a half, researchers around the world have been
> working to derive solar radiation from weather satellite imagery, driven
> largely by the needs of the solar power industry for the siting of solar
> power plants and getting "bankable" solar estimates for their arrays. Our
> little building energy simulation sector can of course benefit by hanging
> on the coattails of the solar power industry, but the downside has been to
> be totally priced out, since the commercial cost for one year's solar data
> for one location (grid cell) typically runs around $1,000.
>
> A welcome development over the last five years is that various government
> offices or affiliated consortia are now beginning to also providing access
> to satellite-derived solar radiation at minimal or more acceptable costs
> under various conditions. Over the past three years, WBT has obtained
> access to such data and permission for its use in WBT weather files.
> WBT is now either replacing the solar radiation on its historical weather
> files, or using satellite-derived radiation to develop custom solar
> coefficients for each location to extend the satellite-derived solar to
> time periods outside the available time window. With the exception of polar
> locations above or below 60/66 degrees, island nations in the Pacific and
> Indian Ocean, and a few unfortunate "blind spots", the entire land mass is
> being covered with at least 10 years up to 18 years of hourly solar records.
>
> Starting in 2018, WBT historical weather files in the following areas will
> all have satellite-derived solar radiation for the following time periods:
> Europe, Africa, South America east of 66 West, i.e., Brazil and Uruguay
> (2004 to date), Australia (1999 to date), and East Asia (2007 to date,
> access pending). WBT historical weather files in the following areas will
> have satellite-derived solar radiation for the indicated time periods -
> North America and Central/South American down to 20 South (1998-2015),
> South Asia (2000-2014), with modeled solar radiation from 2016 on that has
> been individually tuned to the past satellite-derived solar.
>
> Another benefit to the satellite-derived solar is to increases the number
> of available weather stations, which in many places has been limited by the
> lack of cloud cover data needed to model the solar radiation. For reasons
> that are not immediately identifiable, several English-speaking
> Commonwealth countries has seen a marked drop in the number of available
> stations due to the decreases in the reporting of cloud cover (see plot,
> ZAF = South Africa). For example, the number of stations in the UK has
> dropped by almost 2/3s between 2001 and 2017 (174 to 64), but with
> satellite-derived solar, it will go back up to over 180, while in Australia
> and South Africa the comparable numbers are from 175 to well over 500, and
> from 37 to over 100, respectively.
> [image: []]
> If interested, customers who have purchased a historical weather files
> from WBT over the past five years can get an updated weather file at no
> cost. Lastly, although it will take at least a month to update all 10,000
> 2017 files, it's very quick to do for any specific location or even 50 or
> so locations. Therefore, if you have an urgent request please e-mail me and
> I will put that at the beginning of the queue for that day.
>
> --
>
>
> Joe
> Huang
>
>
> White Box Technologies,
> Inc.
>
>
> 346 Rheem Blvd., Suite
> 205A
>
>
> Moraga CA
> 94556
>
>
>
> yjhuang at whiteboxtechnologies.com
>
>
>
> http://weather.whiteboxtechnologies.com for simulation-ready weather
> data
>
>
> (o)(925)388-0265 <(925)%20388-0265>
>
>
> (c)(510)928-2683 <(510)%20928-2683>
>
>
> "building energy simulations at your
> fingertips"
>
>
> Â
>
> ------------------------------
>
>
> NOTICE: This communication and any attachments ("this message") may
> contain information which is privileged, confidential, proprietary or
> otherwise subject to restricted disclosure under applicable law. This
> message is for the sole use of the intended recipient(s). Any unauthorized
> use, disclosure, viewing, copying, alteration, dissemination or
> distribution of, or reliance on, this message is strictly prohibited. If
> you have received this message in error, or you are not an authorized or
> intended recipient, please notify the sender immediately by replying to
> this message, delete this message and all copies from your e-mail system
> and destroy any printed copies. You are receiving this communication
> because you are listed as a current WSP contact. Should you have any
> questions regarding WSP's electronic communications policy, please consult
> our Anti-Spam Commitment at www.wsp.com/casl. For any concern or if you
> believe you should not be receiving this message, please forward this
> message to caslcompliance at wsp.com so that we can promptly address your
> request. Note that not all messages sent by WSP qualify as commercial
> electronic messages.
>
> AVIS : Ce message, incluant tout fichier l'accompagnant (« le message
> »), peut contenir des renseignements ou de l'information privilégiés,
> confidentiels, propriétaires ou à divulgation restreinte en vertu de la
> loi. Ce message est destiné à l'usage exclusif du/des destinataire(s)
> voulu(s). Toute utilisation non permise, divulgation, lecture,
> reproduction, modification, diffusion ou distribution est interdite. Si
> vous avez reçu ce message par erreur, ou que vous n'êtes pas un
> destinataire autorisé ou voulu, veuillez en aviser l'expéditeur
> immédiatement et détruire le message et toute copie électronique ou
> imprimée. Vous recevez cette communication car vous faites partie des
> contacts de WSP. Si vous avez des questions concernant la politique de
> communications électroniques de WSP, veuillez consulter notre Engagement
> anti-pourriel au www.wsp.com/lcap. Pour toute question ou si vous croyez
> que vous ne devriez pas recevoir ce message, prière de le transférer au
> conformitelcap at wsp.com afin que nous puissions rapidement traiter votre
> demande. Notez que ce ne sont pas tous les messages transmis par WSP qui
> constituent des messages electroniques commerciaux.
>
>
>
> -LAEmHhHzdJzBlTWfa4Hgs7pbKl
> __._,_.___
> ------------------------------
> Posted by: "Jones, Christopher" <Christopher.r.Jones at wsp.com>
> <Christopher.r.Jones at wsp.com>
> ------------------------------
> Reply via web post
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/conversations/messages/37879;_ylc=X3oDMTJxajJicWVxBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzM3ODc5BHNlYwNmdHIEc2xrA3JwbHkEc3RpbWUDMTUxNTQ0MjU2MQ--?act=reply&messageNum=37879>
> • Reply to sender
> <Christopher.r.Jones at wsp.com?subject=RE%3A%20%5BEquest-users%5D%20White%20Box%20Technologies%20brings%20simulation%20weather%20data%20to%20the%20satellite%20age>•
> Reply to group
> <EnergyPlus_Support at yahoogroups.com?subject=RE%3A%20%5BEquest-users%5D%20White%20Box%20Technologies%20brings%20simulation%20weather%20data%20to%20the%20satellite%20age>•
> Start a New Topic
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/conversations/newtopic;_ylc=X3oDMTJlMWdkbGppBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA250cGMEc3RpbWUDMTUxNTQ0MjU2MQ-->
> • Messages in this topic
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/conversations/topics/37869;_ylc=X3oDMTM2bjlnNGs2BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzM3ODc5BHNlYwNmdHIEc2xrA3Z0cGMEc3RpbWUDMTUxNTQ0MjU2MQR0cGNJZAMzNzg2OQ-->
> (4)
> ------------------------------
> Check out the automatic photo album with 2 photo(s)
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/photos/photomatic/788930472;_ylc=X3oDMTE4M3R1OW82BF9TAzk3MzU5NzE0BGNmOQNQSE9UT01BVElDBHNlYwNtZWdhcGhvbmU->
> from this topic.
> [image: image003.png]
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/photos/photomatic/788930472;_ylc=X3oDMTE4M3R1OW82BF9TAzk3MzU5NzE0BGNmOQNQSE9UT01BVElDBHNlYwNtZWdhcGhvbmU->
> [image: image003.png]
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/photos/photomatic/788930472;_ylc=X3oDMTE4M3R1OW82BF9TAzk3MzU5NzE0BGNmOQNQSE9UT01BVElDBHNlYwNtZWdhcGhvbmU->
> ------------------------------
> [image: []]
> Have you tried the highest rated email app?
> With 4.5 stars in iTunes, the Yahoo Mail app is the highest rated email
> app on the market. What are you waiting for? Now you can access all your
> inboxes (Gmail, Outlook, AOL and more) in one place. Never delete an email
> again with 1000GB of free cloud storage.
> ------------------------------
> EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to
> energyplus-support at gard.com
>
> The EnergyPlus web site is found at:
> http://www.energyplus.net/
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a
> high speed connection. Limit attachments to small files.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> Visit Your Group
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlbmFlcm9tBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTUxNTQ0MjU2MQ-->
>
> - New Members
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmZjN2YmRvBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE1MTU0NDI1NjE->
> 1
>
> [image: Yahoo! Groups]
> <https://groups.yahoo.com/neo;_ylc=X3oDMTJkYzZoN2MxBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNTE1NDQyNTYx>
>
> • Privacy <https://info.yahoo.com/privacy/us/yahoo/groups/details.html> •
> Unsubscribe
> <EnergyPlus_Support-unsubscribe at yahoogroups.com?subject=Unsubscribe> • Terms
> of Use <https://info.yahoo.com/legal/us/yahoo/utos/terms/>
>
> .
>
> __,_._,___
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Sent from my DynaTAC 8000x
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180109/f3b76f6a/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 308766a.png
Type: image/png
Size: 25844 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180109/f3b76f6a/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 3087689.png
Type: image/png
Size: 255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180109/f3b76f6a/attachment-0009.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 30876a8.png
Type: image/png
Size: 12088 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180109/f3b76f6a/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 3087698.png
Type: image/png
Size: 8477 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180109/f3b76f6a/attachment-0011.png>
More information about the Bldg-sim
mailing list