[Bldg-sim] measurement of SHGC in the field
D. Charlie Curcija
dccurcija at lbl.gov
Mon Nov 13 11:42:25 PST 2017
Please note that SHGC is not equal to solar transmittance. Even if you
would be able to make perfect Tsol measurement in the filed, that could be
way off in predicting SHGC. This is because, SHGC consists of two parts,
one is Tsol (directly transmitted solar radiation and the other is inward
flowing fraction of absorbed solar energy in the window. For the most part
inward flowing fraction is NOT small and it depends on the glazing and
framing configuration. In its extreme, single glazed tinted glass would
have SHGC more than twice than Tsol and often triple Tsol.
Charlie
On Mon, Nov 13, 2017 at 11:29 AM, Nathan Brown <nathan at coolshadow.com>
wrote:
> Hi Chris —
>
> A bit more reading shows that the LiCor Pyranometer is not designed for
> SHGC: the manual says the following:
>
> “The spectral response of the Li-200 does not include the entire solar
> spectrum, so it must be used in the same lighting conditions as those under
> which it was calibrated. Therefore, the LI-200 should only be used to
> measure unobstructed daylight. It should not be used under vegetation,
> artificial lights, in a greenhouse, or for reflected solar radiation”
>
> The solar radiation getting through the glass is obstructed, so the LiCor
> should not be used for measuring SHGC and I’d probably look elsewhere if
> the measurement is important enough to verify in the field.
>
> Best,
> Nathan
>
> Nathan Brown, BEMP, LEED AP ~ Associate
> LOISOS + UBBELOHDE
> - - - - - - - - - - - - - - - - - - - - - - - - - - -
> 1917 Clement Avenue, Building 10A
> Alameda,CA 94501 USA
> - - - - - - - - - - - - - - - - - - - - - - - - - - -
> 510 521 3800 <(510)%20521-3800> VOICE
> 510 521 3820 <(510)%20521-3820> FAX
> - - - - - - - - - - - - - - - - - - - - - - - - - - -
> www.coolshadow.com
>
> On Nov 13, 2017, at 11:06 AM, Nathan Brown <nathan at coolshadow.com> wrote:
>
> Hi Chris —
>
> The LiCor manual shows that the pyranometer is sensitive to wavelengths
> between 390 nm to 1100 nm. That means the LiCor misses most of the UV (and
> longer near IR). So the LiCOr is not perfect by any means, but it’s pretty
> good, given the coverage of the visible and shorter end of the near IR,
> which represent most of the energy in solar heat gain. So it’s a matter of
> how precise you need to be - LiCor gets you most of the way there, but you
> may need something more robust depending on the application. My instinct
> says that it’s good enough for telling the difference between 0.4 and 0.6
> SHGC.
>
> Best,
> Nathan
>
>
> [image:
> https://heatisland.lbl.gov/sites/all/files/Solar%20Energy%20Spectrum.jpg]
> (from https://heatisland.lbl.gov/sites/all/files/Solar%
> 20Energy%20Spectrum.jpg)
>
>
>
> Nathan Brown, BEMP, LEED AP ~ Associate
> LOISOS + UBBELOHDE
> - - - - - - - - - - - - - - - - - - - - - - - - - - -
> 1917 Clement Avenue, Building 10A
> Alameda,CA 94501 USA
> - - - - - - - - - - - - - - - - - - - - - - - - - - -
> 510 521 3800 <(510)%20521-3800> VOICE
> 510 521 3820 <(510)%20521-3820> FAX
> - - - - - - - - - - - - - - - - - - - - - - - - - - -
> www.coolshadow.com
>
> On Nov 13, 2017, at 2:10 AM, Chris Yates <chris.malcolm.yates at gmail.com>
> wrote:
>
> Hi Nathan
>
> Does the li-cor measure short enough wavelengths? I thought a lot of the
> uv was < 400nm. I guess that most "selective coatings" have quite a big
> crossover to the visible range in their reflectivity - hence the slight
> green or blue hues. So, I can imagine that missing some of the uv-b isn't
> too big a deal.
>
> Both responses are super interesting. Thank you very much!
>
> Chris
>
> On Fri, Nov 10, 2017 at 6:54 PM, D. Charlie Curcija <dccurcija at lbl.gov>
> wrote:
>
>> At LBNL, in collaboration with University Federal Santa Catarina (UFSC),
>> Brazil, we have designed partable window energy meter that measures SHGC in
>> the filed. The instrument is not yet commercialized, but two companies are
>> exploring commercialization (D&S and EPDT). In a mean time, UFSC can
>> manufacture unit for you. I can supply you with contact information if you
>> are interested. Also, attached link to US DOE newsletter about the
>> instrument: https://energy.gov/eere/articles/us-brazil-colla
>> boration-leads-innovative-device-reduces-energy-use-buildings.
>>
>> Charlie
>>
>> On Fri, Nov 10, 2017 at 10:07 AM, Nathan Brown via Bldg-sim <
>> bldg-sim at lists.onebuilding.org> wrote:
>>
>>> Hi Chris —
>>>
>>> That instrument won’t do it, because it is not sensitive to infrared.
>>> More than half of irradiance is in the near IR (aka solar infrared). You
>>> need a pyranometer (LiCor is our go-to
>>> <https://www.licor.com/env/products/light/pyranometer.html>, or an
>>> Eppley
>>> <http://www.eppleylab.com/instrument-list/standard-precision-pyranometer/> for
>>> critical measurements, although that is probably overkill for this). I
>>> would measure vertical irradiance just inside and just outside the glass
>>> under direct sunlight. Here in the Bay Area, there is a tool lending
>>> library that will loan a pyranometer. Perhaps you can find a similar source
>>> closer to you.
>>>
>>> Best,
>>> Nathan
>>>
>>> Nathan Brown, BEMP, LEED AP ~ Associate
>>> LOISOS + UBBELOHDE
>>> - - - - - - - - - - - - - - - - - - - - - - - - - - -
>>> 1917 Clement Avenue, Building 10A
>>> Alameda,CA 94501 USA
>>> - - - - - - - - - - - - - - - - - - - - - - - - - - -
>>> 510 521 3800 <(510)%20521-3800> VOICE
>>> 510 521 3820 <(510)%20521-3820> FAX
>>> - - - - - - - - - - - - - - - - - - - - - - - - - - -
>>> www.coolshadow.com
>>>
>>> On Nov 10, 2017, at 3:08 AM, Chris Yates via Bldg-sim <
>>> bldg-sim at lists.onebuilding.org> wrote:
>>>
>>> Dear all
>>>
>>> We are trying to get a reasonable estimate for SHGC in the field.
>>>
>>> Our project is a retrofit of a relatively recent build that has
>>> overheating problems. No records exist of the original glazing spec.
>>>
>>> The glazing has a slight green tint; i.e. the "look and feel" of a
>>> fairly modern spectrally selective product with g-value (sorry SHGC) of
>>> about 0.4. However, a team member has now produced some records indicating
>>> this is significantly higher (more like 0.6).
>>>
>>> Does anybody have any experience or know of any research relating to
>>> this?
>>>
>>> *I was thinking of something like this, taking measurements on the
>>> horizontal and vertical plane inside and out:
>>> https://www.uv-light.co.uk/meters/irradiance-and-exposure/
>>> <https://www.uv-light.co.uk/meters/irradiance-and-exposure/>*
>>>
>>> Our saint gobain rep tells me their spectrographic equipment is 50,000
>>> GBP - a bit out of our price range! (They've offered to test a sample for
>>> us!).
>>>
>>> Cheers
>>>
>>> Chris
>>> _______________________________________________
>>> Bldg-sim mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>>> To unsubscribe from this mailing list send a blank message to
>>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>>
>>>
>>> _______________________________________________
>>> Bldg-sim mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>>> To unsubscribe from this mailing list send a blank message to
>>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>>
>>
>>
>> --
>>
>>
>> *--------------------------------------------------------------------------*
>> *D. Charlie Curcija**, Ph.D. ** Tel: (510) 495-2602
>> <(510)%20495-2602>*
>> *Lawrence Berkeley National Laboratory Fax: (510) 486-4089
>> <(510)%20486-4089>*
>> *Windows & Envelope Materials Group Cell:(510) 604-8668
>> <(510)%20604-8668>*
>> *1 Cyclotron Rd
>> <https://maps.google.com/?q=1+Cyclotron+Rd&entry=gmail&source=g>., MS
>> 90-3111 Email: dccurcija at lbl.gov <dccurcija at lbl.gov>*
>> *Berkeley, CA 94720
>> Web: http://windows.lbl.gov/ <http://btech.lbl.gov/>*
>>
>> *--------------------------------------------------------------------------*
>>
>>
>>
>
>
>
--
*--------------------------------------------------------------------------*
*D. Charlie Curcija**, Ph.D. ** Tel: (510) 495-2602*
*Lawrence Berkeley National Laboratory Fax: (510) 486-4089*
*Windows & Envelope Materials Group Cell:(510) 604-8668*
*1 Cyclotron Rd., MS 90-3111 Email: dccurcija at lbl.gov
<dccurcija at lbl.gov>*
*Berkeley, CA 94720 Web: http://windows.lbl.gov/
<http://btech.lbl.gov/>*
*--------------------------------------------------------------------------*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20171113/1633df63/attachment-0002.html>
More information about the Bldg-sim
mailing list