[Bldg-sim] measurement of SHGC in the field
Chris Yates
chris.malcolm.yates at gmail.com
Mon Nov 13 02:12:18 PST 2017
Correction > 400 nm misses uv-a as well.
On Mon, Nov 13, 2017 at 10:10 AM, Chris Yates <chris.malcolm.yates at gmail.com
> wrote:
> Hi Nathan
>
> Does the li-cor measure short enough wavelengths? I thought a lot of the
> uv was < 400nm. I guess that most "selective coatings" have quite a big
> crossover to the visible range in their reflectivity - hence the slight
> green or blue hues. So, I can imagine that missing some of the uv-b isn't
> too big a deal.
>
> Both responses are super interesting. Thank you very much!
>
> Chris
>
> On Fri, Nov 10, 2017 at 6:54 PM, D. Charlie Curcija <dccurcija at lbl.gov>
> wrote:
>
>> At LBNL, in collaboration with University Federal Santa Catarina (UFSC),
>> Brazil, we have designed partable window energy meter that measures SHGC in
>> the filed. The instrument is not yet commercialized, but two companies are
>> exploring commercialization (D&S and EPDT). In a mean time, UFSC can
>> manufacture unit for you. I can supply you with contact information if you
>> are interested. Also, attached link to US DOE newsletter about the
>> instrument: https://energy.gov/eere/articles/us-brazil-colla
>> boration-leads-innovative-device-reduces-energy-use-buildings.
>>
>> Charlie
>>
>> On Fri, Nov 10, 2017 at 10:07 AM, Nathan Brown via Bldg-sim <
>> bldg-sim at lists.onebuilding.org> wrote:
>>
>>> Hi Chris —
>>>
>>> That instrument won’t do it, because it is not sensitive to infrared.
>>> More than half of irradiance is in the near IR (aka solar infrared). You
>>> need a pyranometer (LiCor is our go-to
>>> <https://www.licor.com/env/products/light/pyranometer.html>, or an
>>> Eppley
>>> <http://www.eppleylab.com/instrument-list/standard-precision-pyranometer/> for
>>> critical measurements, although that is probably overkill for this). I
>>> would measure vertical irradiance just inside and just outside the glass
>>> under direct sunlight. Here in the Bay Area, there is a tool lending
>>> library that will loan a pyranometer. Perhaps you can find a similar source
>>> closer to you.
>>>
>>> Best,
>>> Nathan
>>>
>>> Nathan Brown, BEMP, LEED AP ~ Associate
>>> LOISOS + UBBELOHDE
>>> - - - - - - - - - - - - - - - - - - - - - - - - - - -
>>> 1917 Clement Avenue, Building 10A
>>> Alameda,CA 94501 USA
>>> - - - - - - - - - - - - - - - - - - - - - - - - - - -
>>> 510 521 3800 <(510)%20521-3800> VOICE
>>> 510 521 3820 <(510)%20521-3820> FAX
>>> - - - - - - - - - - - - - - - - - - - - - - - - - - -
>>> www.coolshadow.com
>>>
>>> On Nov 10, 2017, at 3:08 AM, Chris Yates via Bldg-sim <
>>> bldg-sim at lists.onebuilding.org> wrote:
>>>
>>> Dear all
>>>
>>> We are trying to get a reasonable estimate for SHGC in the field.
>>>
>>> Our project is a retrofit of a relatively recent build that has
>>> overheating problems. No records exist of the original glazing spec.
>>>
>>> The glazing has a slight green tint; i.e. the "look and feel" of a
>>> fairly modern spectrally selective product with g-value (sorry SHGC) of
>>> about 0.4. However, a team member has now produced some records indicating
>>> this is significantly higher (more like 0.6).
>>>
>>> Does anybody have any experience or know of any research relating to
>>> this?
>>>
>>> *I was thinking of something like this, taking measurements on the
>>> horizontal and vertical plane inside and out:
>>> https://www.uv-light.co.uk/meters/irradiance-and-exposure/
>>> <https://www.uv-light.co.uk/meters/irradiance-and-exposure/>*
>>>
>>> Our saint gobain rep tells me their spectrographic equipment is 50,000
>>> GBP - a bit out of our price range! (They've offered to test a sample for
>>> us!).
>>>
>>> Cheers
>>>
>>> Chris
>>> _______________________________________________
>>> Bldg-sim mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>>> To unsubscribe from this mailing list send a blank message to
>>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>>
>>>
>>> _______________________________________________
>>> Bldg-sim mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>>> To unsubscribe from this mailing list send a blank message to
>>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>>
>>
>>
>> --
>>
>>
>> *--------------------------------------------------------------------------*
>>
>> *D. Charlie Curcija**, Ph.D. ** Tel: (510) 495-2602
>> <(510)%20495-2602>*
>>
>> *Lawrence Berkeley National Laboratory Fax: (510) 486-4089
>> <(510)%20486-4089>*
>>
>> *Windows & Envelope Materials Group Cell:(510) 604-8668
>> <(510)%20604-8668>*
>>
>> *1 Cyclotron Rd., MS 90-3111 Email: dccurcija at lbl.gov
>> <dccurcija at lbl.gov>*
>>
>> *Berkeley, CA 94720
>> Web: http://windows.lbl.gov/ <http://btech.lbl.gov/>*
>>
>>
>> *--------------------------------------------------------------------------*
>>
>>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20171113/c6aeebc8/attachment-0002.html>
More information about the Bldg-sim
mailing list