[Bldg-sim] Proposed Case fan power modelling
Jim Dirkes via Bldg-sim
bldg-sim at lists.onebuilding.org
Tue Jul 18 04:27:09 PDT 2017
If the fan is using 4.73BHP, that's the value to consider for energy cost.
It is very common for a motor to have greater capacity than is actually
used.
On Tue, Jul 18, 2017 at 7:24 AM, Mayank Bhatnagar via Bldg-sim <
bldg-sim at lists.onebuilding.org> wrote:
> Hello Everyone,
>
>
> Ours is a Residential Project with PTAC units and DOAS in the Proposed
> design. The DOAS nameplate motor HP is 7.5 where as the fan absorbed power
> is 4.73 BHP. If we model 7.5 HP; we are falling short of the minimum LEED
> energy performance requirements. Modelling
> 4.73 BHP just gives us enough savings.
>
> Which one is the correct fan power to model?
>
> I have been through the archives and didn't find appropriate answer.
> Please help!
>
> Regards,
>
> Mayank.
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
James V Dirkes II, CEO / President
The Building Performance Team Inc.
1631 Acacia Dr, GR, MI 49504
(alphabet soup of efforts for excellence: PE, BEMP, BCxP, LEED AP)
Direct / Mobile: 616.450.8653
jim at buildingperformanceteam.com
Website <http://buildingperformanceteam.com>l LinkedIn
<https://www.linkedin.com/pub/jim-dirkes/7/444/413>
*Coffee conversation:*They love truth when it enlightens them, they
hate truth when it accuses them… They love truth when it reveals
itself, and hate it when it reveals them*.*
.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20170718/6d7fc891/attachment-0001.html>
More information about the Bldg-sim
mailing list