[Bldg-sim] 90.1-2010 ECB and PRM questions
Jones, Christopher via Bldg-sim
bldg-sim at lists.onebuilding.org
Fri Jul 14 08:38:26 PDT 2017
Thank you Jim,
I agree with your assessment. If you include shading from adjacent buildings in the proposed, then it should also be included in the baseline. I don’t believe anyone would agree with having shading in one but not the other.
Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy
[cid:image001.png at 01D2FC95.B3C31940]
T +1 416-644-0252
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com
Please consider the environment before printing...
From: Jim Dirkes [mailto:jim at buildingperformanceteam.com]
Sent: Friday, July 14, 2017 11:09 AM
To: Jones, Christopher <Christopher.r.Jones at wsp.com>
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] 90.1-2010 ECB and PRM questions
Dear Chris,
I think the "letter of the law" does not require that you model shading from an adjacent building for you Baseline.
The "spirit of the law" doesn't seem to require it, either. A Baseline building is intended to be a minimum performance standard against which your building is compared. For the Proposed building, the owner was not compelled to select a site with shading from an adjacent building - it could have been in the middle of a corn field with no shading. As a result, it seems that you need not include the shading in the Baseline.
It might, however, be beneficial or detrimental to include the shading in the Baseline, and it seems acceptable to do either within the standard's requirements. I'm imagining a situation where the shading blocks winter sun and is a net detriment to energy use. If I wanted a rigorous comparison, I'd make the Baseline model in the manner that gave the lowest Baseline energy use. If I wanted the most savings :), I'd include the adjacent building in the Baseline so as not to be penalized.
I agree that the Baseline model must include mandatory requirements for daylighting.
On Thu, Jul 13, 2017 at 8:07 AM, Jones, Christopher via Bldg-sim <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>> wrote:
Hello Sim Folks,
I have two questions regarding 90.1-2010 ECB and PRM. Our building code references ECB and LEED references App. G PRM.
Shading due to adjacent buildings – should this shading be modeled for:
ECB –
PRM –
90.1-2010 ECB doesn’t directly refer to shading by other buildings.
App. G as detailed in the PNNL PRM Manual states that external shading from other buildings or other objects can be modeled for 90.1-2010 PRM.
Therefore, I believe one can choose to model that shading or one can ignore it.
Daylighting controls – should daylighting controls be modeled for:
ECB –
PRM –
Re. Daylighting:
Reviewing Section 11.1.4 Compliance with Section 11 will be achieved if:
a. All requirements of Sections 5.4, 6.4, 7.4, 8.4, 9.4, and 10.4 are met;
Table 11.3.1, 6. Lighting, Baseline: Lighting controls shall be the minimum required.
These clauses lead me to believe that daylighting controls should be modeled in the baseline using the correct side-lighted and top-lighted area calculations.
App. G as detailed in the PNNL PRM Manual is clear – daylighting controls are to be modeled in the baseline.
Any and all thoughts appreciated.
Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy
[cid:image001.png at 01D2FC95.B3C31940]
T +1 416-644-0252<tel:(416)%20644-0252>
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com<http://wsp.com>
Please consider the environment before printing...
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of Sprout Info_Mail via Bldg-sim
Sent: Thursday, June 29, 2017 10:38 PM
To: Mayank Bhatnagar <mayank.23aug at gmail.com<mailto:mayank.23aug at gmail.com>>
Cc: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Building Energy Simulation: A Workbook Using DesignBuilder
Ohh wow Mayank.
This is really great. Thanks for sharing.
Does anybody have any more such resources.Please share.
Regards,
Namrata Dhamankar
On 29 Jun 2017 20:01, "Mayank Bhatnagar via Bldg-sim" <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>> wrote:
Hello everyone,
I have been searching for some books on basics of building physics, and energy simulation and found a very nice resource to understand the building physics along with energy simulation.
Hope this will help to new members in the field of energy modelling and simulation. The book is available at:
https://www.amazon.com/Building-Energy-Simulation-Workbook-DesignBuilderTM/dp/1498744516/ref=sr_1_1?ie=UTF8&qid=1498012115&sr=8-1&keywords=energy+simulation
https://www.crcpress.com/Building-Energy-Simulation-A-Workbook-Using-DesignBuilder/Garg-Mathur-Tetali-Bhatia/p/book/9781498744515
Regards,
Mayank Bhatnagar
Sr. Energy Analyst | Research Scholar
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
________________________________
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl<http://www.wspgroup.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wspgroup.com.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the addressee and may contain information which is privileged, confidential, proprietary, or exempt from disclosure under applicable law. If you are not the intended recipient, you are strictly prohibited from disclosing, distributing, copying, or in any way using this message. If you have received this communication in error, please notify the sender and delete any copies you may have received.
----------------------------------------------------------------------------------------------------------------------------------------
Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel www.wspgroup.com/lcap<http://www.wspgroup.com/casl>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wspgroup.com<mailto:conformitelcap at wspgroup.com> afin que nous puissions rapidement traiter votre demande. Ce message est destiné uniquement au destinataire et il peut contenir des informations privilégiées, confidentielles ou non divulgables en vertu de la loi. Si vous n’êtes pas le destinataire du présent message, il vous est strictement interdit de le divulguer, de le distribuer, de le copier ou de l’utiliser de quelque façon que ce soit. Si vous avez reçu la présente communication par erreur, veuillez en aviser l’expéditeur et supprimer le message.
______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
--
James V Dirkes II, CEO / President
The Building Performance Team Inc.
1631 Acacia Dr, GR, MI 49504
(alphabet soup of efforts for excellence: PE, BEMP, BCxP, LEED AP)
Direct / Mobile: 616.450.8653
jim at buildingperformanceteam.com<mailto:jim at buildingperformanceteam.com>
Website <http://buildingperformanceteam.com> l LinkedIn<https://www.linkedin.com/pub/jim-dirkes/7/444/413>
Coffee conversation:
They love truth when it enlightens them, they hate truth when it accuses them… They love truth when it reveals itself, and hate it when it reveals them.
.
________________________________
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl<http://www.wspgroup.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wspgroup.com.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the addressee and may contain information which is privileged, confidential, proprietary, or exempt from disclosure under applicable law. If you are not the intended recipient, you are strictly prohibited from disclosing, distributing, copying, or in any way using this message. If you have received this communication in error, please notify the sender and delete any copies you may have received.
----------------------------------------------------------------------------------------------------------------------------------------
Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel www.wspgroup.com/lcap<http://www.wspgroup.com/casl>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wspgroup.com<mailto:conformitelcap at wspgroup.com> afin que nous puissions rapidement traiter votre demande. Ce message est destiné uniquement au destinataire et il peut contenir des informations privilégiées, confidentielles ou non divulgables en vertu de la loi. Si vous n’êtes pas le destinataire du présent message, il vous est strictement interdit de le divulguer, de le distribuer, de le copier ou de l’utiliser de quelque façon que ce soit. Si vous avez reçu la présente communication par erreur, veuillez en aviser l’expéditeur et supprimer le message.
______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20170714/307a4489/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25844 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20170714/307a4489/attachment-0003.png>
More information about the Bldg-sim
mailing list