[Bldg-sim] Baseline HVAC system type question
Chris Jones via Bldg-sim
bldg-sim at lists.onebuilding.org
Fri Feb 17 04:39:23 PST 2017
Thank you Anderson,
In this case, the retail is more than 20,000 ft2 so I need to select a different baseline system.
My follow-up question: the building is more than 5 floors (majority is residential) but the retail only occupies the ground floor. Would I select System 7, VAV reheat as the building is more than 5 floors.
Or would I select System 3 for the retail because the that space only occupies 1 floor?
[Title: RWDI - Description: RWDI logo]<http://www.rwdi.com/assets/logos/RWDI-logo.gif>
Christopher Jones, P.Eng. | Senior Energy Analyst
RWDI
901 King Street West, Suite 400, Toronto, ON M5V 3H5 Canada
Tel: (519) 823-1311 ext 2052
rwdi.com<http://www.rwdi.com/>
From: Anderson Letti [mailto:anderson.a.letti at gmail.com]
Sent: Thursday, February 16, 2017 2:23 PM
To: Chris Jones
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Baseline HVAC system type question
I believe that if the retail gross floor area is less than 1900 m2 you can use system 1, otherwise you can use exception a of section G3.1.1.
2017-02-16 17:12 GMT-02:00 Chris Jones via Bldg-sim <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>>:
Standard 90.1-2007. The building is a high rise residential with the ground floor mainly retail. 90.1-2007 says to use the predominant condition to select the baseline system. In this case residential is the predominant condition therefore I am assuming the retail spaces would also have System 1, PTAC? Heating is fossil fuel.
[Title: RWDI - Description: RWDI logo]<http://www.rwdi.com/assets/logos/RWDI-logo.gif>
Christopher Jones, P.Eng. | Senior Energy Analyst
RWDI
901 King Street West, Suite 400, Toronto, ON M5V 3H5 Canada
Tel: (519) 823-1311 ext 2052<tel:(519)%20823-1311>
rwdi.com<http://www.rwdi.com/>
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of Jim Dirkes via Bldg-sim
Sent: Wednesday, February 15, 2017 6:42 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] ASHRAE Building Performance Analysis conference needs knowledgeable presenters
What have you learned in the past few years that others will benefit from hearing about? Sample topics of interest might be:
* Making the business case for modeling
* Modeling challenging or unusual projects or systems
* Post-occupancy modeling tips, tricks and lessons learned
* Emerging trends
This conference has been an amazing event to learn, share and network. It's very much worth attending ... and of you present a topic part or all of your registration fee is waived (I should know that detail, but forgot and can't look it up right now.)
Registration is available NOW. Presentations are being solicited NOW. Find more information HERE <https://www.ashrae.org/membership--conferences/conferences/ashrae-conferences/2017-ashrae-building-performance-analysis-conference> - or feel free to call me and discuss a possible topic or other concern.
--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653<tel:(616)%20450-8653>
jim at buildingperformanceteam.com<mailto:jim at buildingperformanceteam.com>
Website <http://buildingperformanceteam.com> l LinkedIn<https://www.linkedin.com/pub/jim-dirkes/7/444/413> | May 2016 ASHRAE Journal article on energy modeling<http://buildingperformanceteam.com/bpt-insights-blog/item/73-modeled-performance-isn-t-actual-performance>
Choice. It is perhaps the most distinct and dignifying characteristic of humans. Consciously and with understanding, we choose what is true, honorable, right, pure, lovely … or otherwise. Like the rest of humanity, my choices don’t always align with true, honorable, right, pure, and lovely, but I know those are what I set my sights upon. I choose them.
________________________________
RWDI - A Platinum Member of Canada's 50 Best Managed Companies
This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com<mailto:solutions at rwdi.com> or call +1.519.823.1311<tel:(519)%20823-1311>.
________________________________
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Att.,
Eng. Anderson Letti
ASHRAE BEMP Certified - Building Energy Modeling Professional [https://docs.google.com/uc?export=download&id=0B7au6A8M6Tlyc0UwczE3aTRLX28&revid=0B7au6A8M6TlydWNTNkNMWkE2UExxdE40N1VVSEpkSjhhRklRPQ]
Rua 3700, 249. CEP 88330-203
Bal. Camboriú - SC - Brasil
Tell: +55 47 99632 3912<tel:+55%2047%2099632-3912>
Skype: anderson.letti
________________________________
RWDI - A Platinum Member of Canada's 50 Best Managed Companies
This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com or call +1.519.823.1311.
________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20170217/395995fa/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 2227 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20170217/395995fa/attachment-0003.jpg>
More information about the Bldg-sim
mailing list