[Bldg-sim] Baseline HVAC system type question
Jim Dirkes via Bldg-sim
bldg-sim at lists.onebuilding.org
Thu Feb 16 12:18:11 PST 2017
Opps. I missed Anderson's response, which is more complete than mine :)
On Thu, Feb 16, 2017 at 3:17 PM, Jim Dirkes <jim at buildingperformanceteam.com
> wrote:
> The retail spaces are a section 3.1 "exception" and should be modeled as
> System 3 or 4
>
> On Thu, Feb 16, 2017 at 2:12 PM, Chris Jones via Bldg-sim <
> bldg-sim at lists.onebuilding.org> wrote:
>
>> Standard 90.1-2007. The building is a high rise residential with the
>> ground floor mainly retail. 90.1-2007 says to use the predominant condition
>> to select the baseline system. In this case residential is the predominant
>> condition therefore I am assuming the retail spaces would also have System
>> 1, PTAC? Heating is fossil fuel.
>>
>>
>>
>>
>>
>>
>>
>> [image: Title: RWDI - Description: RWDI logo]
>> <http://www.rwdi.com/assets/logos/RWDI-logo.gif>
>>
>> *Christopher Jones, **P.Eng. *| Senior Energy Analyst
>> *RWDI*
>> 901 King Street West, Suite 400, Toronto, ON M5V 3H5 Canada
>> Tel: (519) 823-1311 ext 2052 <(519)%20823-1311>
>> rwdi.com <http://www.rwdi.com/>
>>
>>
>>
>>
>>
>> *From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] *On
>> Behalf Of *Jim Dirkes via Bldg-sim
>> *Sent:* Wednesday, February 15, 2017 6:42 PM
>> *To:* bldg-sim at lists.onebuilding.org
>> *Subject:* [Bldg-sim] ASHRAE Building Performance Analysis conference
>> needs knowledgeable presenters
>>
>>
>>
>> What have you learned in the past few years that others will benefit from
>> hearing about? Sample topics of interest might be:
>>
>> - Making the business case for modeling
>> - Modeling challenging or unusual projects or systems
>> - Post-occupancy modeling tips, tricks and lessons learned
>> - Emerging trends
>>
>> This conference has been an amazing event to learn, share and network.
>> It's very much worth attending ... and of you present a topic part or all
>> of your registration fee is waived (I should know that detail, but forgot
>> and can't look it up right now.)
>>
>>
>>
>> Registration is available NOW. Presentations are being solicited NOW.
>> Find more information HERE
>> <https://www.ashrae.org/membership--conferences/conferences/ashrae-conferences/2017-ashrae-building-performance-analysis-conference>-
>> or feel free to call me and discuss a possible topic or other concern.
>>
>>
>>
>>
>>
>> --
>>
>> James V Dirkes II, PE, BEMP, LEED AP
>> CEO/President
>> The Building Performance Team Inc.
>> 1631 Acacia Dr, GR, Mi 49504
>>
>> Direct: 616.450.8653 <(616)%20450-8653>
>> jim at buildingperformanceteam.com
>>
>> Website <http://buildingperformanceteam.com>l LinkedIn
>> <https://www.linkedin.com/pub/jim-dirkes/7/444/413> | May 2016 ASHRAE
>> Journal article on energy modeling
>> <http://buildingperformanceteam.com/bpt-insights-blog/item/73-modeled-performance-isn-t-actual-performance>
>>
>> Choice. It is perhaps the most distinct and dignifying characteristic of
>> humans. Consciously and with understanding, we choose what is true,
>> honorable, right, pure, lovely … or otherwise. Like the rest of humanity,
>> my choices don’t always align with true, honorable, right, pure, and
>> lovely, but I know those are what I set my sights upon. I choose them.
>> ------------------------------
>> *RWDI - A Platinum Member of Canada's 50 Best Managed Companies*
>> This communication is intended for the sole use of the party to whom it
>> was addressed and may contain information that is privileged and/or
>> confidential. Any other distribution, copying or disclosure is strictly
>> prohibited. If you received this email in error, please notify us
>> immediately by replying to this email and delete the message without
>> retaining any hard or electronic copies of same. Outgoing emails are
>> scanned for viruses, but no warranty is made to their absence in this email
>> or attachments. If you require any information supplied by RWDI in a
>> different format to facilitate accessibility, contact the sender of the
>> email, email solutions at rwdi.com or call +1.519.823.1311
>> <(519)%20823-1311>.
>> ------------------------------
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
>
> --
>
> James V Dirkes II, PE, BEMP, LEED AP
> CEO/President
> The Building Performance Team Inc.
> 1631 Acacia Dr, GR, Mi 49504
>
> Direct: 616.450.8653 <(616)%20450-8653>
> jim at buildingperformanceteam.com
>
> Website <http://buildingperformanceteam.com>l LinkedIn
> <https://www.linkedin.com/pub/jim-dirkes/7/444/413> | May 2016 ASHRAE
> Journal article on energy modeling
> <http://buildingperformanceteam.com/bpt-insights-blog/item/73-modeled-performance-isn-t-actual-performance>
>
> Choice. It is perhaps the most distinct and dignifying characteristic of humans. Consciously and with understanding, we choose what is true, honorable, right, pure, lovely … or otherwise. Like the rest of humanity, my choices don’t always align with true, honorable, right, pure, and lovely, but I know those are what I set my sights upon. I choose them.
>
>
--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653
jim at buildingperformanceteam.com
Website <http://buildingperformanceteam.com>l LinkedIn
<https://www.linkedin.com/pub/jim-dirkes/7/444/413> | May 2016 ASHRAE
Journal article on energy modeling
<http://buildingperformanceteam.com/bpt-insights-blog/item/73-modeled-performance-isn-t-actual-performance>
Choice. It is perhaps the most distinct and dignifying characteristic
of humans. Consciously and with understanding, we choose what is true,
honorable, right, pure, lovely … or otherwise. Like the rest of
humanity, my choices don’t always align with true, honorable, right,
pure, and lovely, but I know those are what I set my sights upon. I
choose them.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20170216/ec33ca11/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 2227 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20170216/ec33ca11/attachment-0003.jpg>
More information about the Bldg-sim
mailing list