[Bldg-sim] 90.1-2013 vs 2015 IECC Performance Path Compliance

Jones, Christopher via Bldg-sim bldg-sim at lists.onebuilding.org
Mon May 2 11:34:13 PDT 2016


Elizabeth,
Don’t neglect Section 10 – it also includes mandatory provisions for whole building metering – all fuels. Measurements are to be taken every 60 minutes and reported hourly, daily, monthly, annually. The system shall be capable of storing the data for 36 months.



[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer

WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056

www.wspgroup.com<http://www.wspgroup.com/>

From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Elizabeth Gillmor via Bldg-sim
Sent: Monday, May 02, 2016 1:38 PM
To: Duggin, Cory
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] 90.1-2013 vs 2015 IECC Performance Path Compliance

I just did a little seminar on this very topic for our Rocky Mountain ASHRAE tech conference last week.  There are a few other key differences in 90.1:

- Mandatory occupancy and daylighting controls in parking garages
- Bi-level occ sensors required in stairwells
- Slightly more stringent cooling efficiency requirements (full load and part load, also slightly lower economizer thresholds). Differences in heat pumps as well I believe.
- More stringent envelope requirements (walls and windows). Also note limits to E/W glazing which may require that you rotate/average the baseline.

Other important items to note:

- A90.1 has MANDATORY electrical submetering requirements (separate monitoring for lighting, receptacles, and HVAC, plus some whole-building requirements) -- this is a biggie. Read section 8-Power thoroughly!
- You CAN take credit for renewable energy (up to 5%)
- A90.1 does not have the same commissioning requirements
- A90.1 allows extra lighting credit for room geometry adjustments and some extra lighting controls (see control factor table), whereas IECC does not


This is not a comprehensive list but those are the big ones that jump out.  Whichever method you choose, make sure you are using the space-by-space method for lighting (it will almost always come out better than whole-building).

Cheers,
Elizabeth


Elizabeth Gillmor  PE, BEMP, LC, LEED AP

e n e r g e t i c s  consulting engineers, llc
energetics-eng.com<http://energetics-eng.com> | 303.619.0091

On Mon, May 2, 2016 at 11:08 AM, Duggin, Cory via Bldg-sim <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>> wrote:
Does anyone have experience showing code compliance via the performance path in 90.1-2013 vs 2015 IECC?  I have a project that isn’t meeting the 15% threshold against the 2015 IECC standard reference design (per C401.2(3)).  I have always thought the 15% was to level the compliance paths, but the main difference I am finding between the 2015  IECC SRD and 90.1-2013 budget building is the mandatory plug load control requirement.  What am I missing to account for the 15% difference?

Thanks,

Cory Duggin, PE, LEED AP BD+C, BEMP
Principal/Energy Modeling Wizard
TLC Engineering for Architecture
6 Cadillac Drive, Suite 200
Brentwood, TN 37027-5080

direct:

615-346-1939<tel:615-346-1939>

website:

www.tlc-engineers.com<http://www.tlc-engineers.com/>




_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>

________________________________

You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20160502/e98dcea8/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20160502/e98dcea8/attachment-0003.png>


More information about the Bldg-sim mailing list