[Bldg-sim] Vented cavity behind brick or precast panels and effective R-value
Leonard Sciarra
leonard_sciarra at gensler.com
Fri Mar 4 23:03:31 PST 2016
Christopher –
The ASHRAE SSPC 90.1 discussed this in preparation of addendum ac 4th public review to 90.1-2010. The handbook values for “air” are based on the somewhat subjective description of an air space where “air movement is minimized”. Minimized of course means different things to different people, and the description of the test procedure was a ‘sealed’ box with sheet metal and felt (the report we think was from like 1950). In general, the final discussions that resolved all the parties was (there were also modification to the allowances for assumptions of reflective barriers). There is a request for research proposal on this topic to better understand the effect of movement and effectiveness of radiant barriers.
However, in response to your request of the effectiveness of the air space in a cavity exposed to exterior conditions (wind, temperature, pressure differentials) it was pretty clear the handbook values would not apply as there is just too much air movement to create a stable mass of air. (note you could apply the air films listed for a semi-exterior space in A9.4.1)
The final text of ac 4th PRD: (the table did not change and you will note the current table in 90.1 does not exactly match the handbook as the committee simplified the table with only up, down, and side to side air spaces and made then all Delta T neutral)
A9.4.2 Airspaces. The R-value for airspaces shall be taken from Table A9.4A based on the effective emittance of the surfaces facing the airspace from Table A9.4B provided the following criteria are satisfied:
a) The airspace shall be an enclosed and unventilated cavity designed to minimize airflow into and out of the enclosed air space. Airflow shall be deemed minimized when the enclosed airspace is located on the interior of the continuous air barrier and bounded on all sides by building components.
b) Reflective insulation as defined in ASTM C1224, where used, shall be fitted closely around all non-heat producing components and taped or otherwise sealed to eliminate gaps or voids through which air, dust, or water vapor has the potential to pass.
c) Non-parallel spaces shall use the average distance to determine the thickness of the airspace.
d) Airspaces less than 0.5 in. (13 mm) depth thickness shall have no R-value.
e) The R-value for 3.5 in. (89 mm) airspaces shall be used for airspaces of that thickness or greater provided that that airspace does not exceed 12 in. (300 mm) between the surfaces at any point.
Leonard Sciarra, AIA, ASHRAE, LEED ap+
Senior Associate
+1 312.577.6580 Direct
+1 312.456.0123 Main
+1 847.345.5619 Mobile
Gensler
11 East Madison Street
Suite 300
Chicago, Illinois 60602
USA
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Keith Swartz
Sent: Friday, March 04, 2016 3:16 PM
To: Jones, Christopher <Christopher.r.Jones at wspgroup.com>; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Vented cavity behind brick or precast panels and effective R-value
Christopher,
The ASHRAE Handbook has a section about thermal resistance of air spaces. See the 2013 Fundamentals Handbook starting on p. 26.12. Is that what you are looking for?
Keith Swartz, PE | Senior Energy Engineer
Seventhwave
608.210.7123 seventhwave.org
From: Jones, Christopher [mailto:Christopher.r.Jones at wspgroup.com]
Sent: Friday, March 04, 2016 12:52 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Vented cavity behind brick or precast panels and effective R-value
Is anyone aware of any analyses of the effective insulation properties of brick or precast veneer with a vented air space? I assume the air in that cavity is moving slowly but it isn’t completely still therefore you can’t include all of the insulative properties of those two layers on the outside of a wall?
[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056
www.wspgroup.com<http://www.wspgroup.com/>
________________________________
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20160305/06fe903e/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20160305/06fe903e/attachment-0003.png>
More information about the Bldg-sim
mailing list