[Bldg-sim] TABS/floor heating - EnergyPlus
    Michael J Witte via Bldg-sim 
    bldg-sim at lists.onebuilding.org
       
    Wed Jun 22 07:04:11 PDT 2016
    
    
  
I assume that TABS = thermally activated building systems?  The details 
of this model in EnergyPlus are explained in the Engineering Reference 
section "Low Temperature Radiant System Model", especially the 
subsection "Extension of Time Series Solutions to Include Heat Sources 
and Obtain Internal Temperatures".  There are technical papers 
referenced at the end of that section; the most pertinent are the ones 
by Strand and Pedersen.  Beyond that, the only thing that will have more 
detail is the source code itself.
Mike
On 6/21/2016 10:54 AM, Karol Bandurski via Bldg-sim wrote:
>
> Dear Experts
>
> We are looking for detailed description of modeling method for
>
> Floor heating and TABS
>
> in EnergyPlus.
>
> Could you give us some advice?
>
> (Engineering Reference is not enough)
>
> Regards,
>
> Karol
>
> ------------------------------------------------
>
> Karol Bandurski MSc.
>
> Institute of Environmental Engineering <http://www.ee.put.poznan.pl/>
>
> Poznan University of Technology
>
> www.put.poznan.pl/~karol.bandurski 
> <http://www.put.poznan.pl/%7Ekarol.bandurski>
>
> www.ee.put.poznan.pl <http://www.ee.put.poznan.pl>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20160622/3d0a1a5d/attachment-0001.html>
    
    
More information about the Bldg-sim
mailing list