[Bldg-sim] MODELLING THERMAL BRDIGES IN e-quest or DOE2 (minor correction on dates).

Christian Cianfrone CCianfrone at morrisonhershfield.com
Fri Jan 29 20:38:46 PST 2016


Joe,

I think there is some misunderstanding.  The point of the research was to more accurately assess heat loss through assemblies that have heat flow paths in 3D as well as heat flow through complex details that are often ignored in typical North American practice of energy modeling for code compliance.  The research did not develop accompanying transfer functions for each 3D assembly and/or detail.

The research showed that common practice was to ignore substantial amounts of heat loss – this is where most of the inaccuracy in energy modeling is when dealing with the envelope.  Refining transfer functions, as you say, has been studied in other work – there was no need to recreate it in 1365-RP or the follow up BETB Guide.

I was also pointing out that for the climate zones for which energy modeling was done to support the 3D thermal modeling, it was shown that thermal mass has negligible energy impact, which further supports the notion that the U-value is of utmost important, and transfer functions can continue to be used as they always have been in energy models.

Hope that helps.

Christian

From: Joe Huang [mailto:yjhuang at whiteboxtechnologies.com]
Sent: Friday, January 29, 2016 6:25 PM
To: Christian Cianfrone <CCianfrone at morrisonhershfield.com>; Jones, Christopher <Christopher.r.Jones at wspgroup.com>; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] MODELLING THERMAL BRDIGES IN e-quest or DOE2 (minor correction on dates).

Christian,

Pardon me if my understanding is faulty, but skimming through the web pages on the Morrison-Hershfield web site, the analysis
seems to have been done under steady-state conditions, similar to using HEATING-7 or THERM, and is returning the effective U-value of the layer.   You wrote that "...transient analysis was done using EnergyPlus' Finite Difference method", but that's yet another method which is time-consuming and not practical for standard simulations.

It appears the tables from 1365-RP provide only the U-value, which means that the wall could only be modeled as a "quick" surface, and not as a delayed surface, or else one can create a monolithic layer with an average specific-heat and density.  This is not a big issue for steel-frame walls that have little thermal mass, but could give misleading results when modeling heavy concrete blocks or masonry walls.

The approach used in the 1986 LBNL work was somewhat different.  There, a 2-D finite-element program was used to model the wall section in 2-D (not 3-D) under dynamic conditions by putting triangular pulses of heat on each surface, and then tracking the thermal response of the surfaces over time (this is the standard way for calculating a response factor time series). Once that response factor has been derived,  it can be used in the DOE-2 simulations just like any other response factor, which is a very quick and efficient way to simulate conduction under dynamic conditions, with the only time burden that needed to set up and generate the 2-D response factors.

Several decades ago, Oak Ridge took another approach where they used another program to analyze the heat flows (response factors?) of the 2-D layer and replace it by a fictitious 3-layer 1-D wall having the same thermal characteristics and response, but I wasn't sure whether that made things any more understandable. However, what I liked about both the LBNL and ORNL approaches are that they were able to model 2-D heat flows in walls dynamically without slowing down the simulations.

Joe



Joe Huang

White Box Technologies, Inc.

346 Rheem Blvd., Suite 205A

Moraga CA 94556

yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>

http://weather.whiteboxtechnologies.com for simulation-ready weather data

(o) (925)388-0265

(c) (510)928-2683

"building energy simulations at your fingertips"


On 1/29/2016 1:51 PM, Christian Cianfrone wrote:
Chris, Joe,

Refer to ASHRAE 1365-RP for detailed methodology on the modeling.  The same methodology was used in the BETB Guide.  Sensitivity of transient analysis for the thermal modeling was addressed in 1365-RP.  In terms of thermal mass impacts on energy modeling, this is dealt with in Appendix C of the report.  Analysis was done using EnergyPlus’ Finite Difference method for conduction.

Chris – the point of derating the reference building in the BC Hydro incentive is to encourage design teams to understand the actual performance of their envelope (and buildings).  If you just force people to include all thermal bridging when the codes were clearly developed to ignore most of this thermal bridging, then nobody will ever account for the full effects of thermal bridging.

By not being realistic, designers end up adding (and paying) for more insulation with no real added value.  And the relative savings are not the same – The differences in energy at high R-values are not the same differences in energy at low R-values.

Paperwork is quite straightforward too.  It requires a few take-offs and looking up U-values/Psi Values, which an energy modeler is mostly already doing.  We’ll be releasing some how-to videos in the near future to help folks along.  I’ll post to this group when available.

Cheers,

Christian Cianfrone, M.A.Sc., P.Eng., LEED® AP BD+C
Principal, Building Energy Practice Lead
ccianfrone at morrisonhershfield.com<mailto:email at morrisonhershfield.com>

[Description: Description: Description: Description:                  Description: logo4email4]<http://www.morrisonhershfield.com/Pages/default.aspx>

Suite 310, 4321 Still Creek Drive  |  Burnaby, BC  V5C 6S7
Dir: 604 454 2006  |  Cell: 604 376 1315  |  Fax: 604 454 0403
morrisonhershfield.com/sustainability


From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher
Sent: Friday, January 29, 2016 10:15 AM
To: Joe Huang <yjhuang at whiteboxtechnologies.com><mailto:yjhuang at whiteboxtechnologies.com>; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] MODELLING THERMAL BRDIGES IN e-quest or DOE2 (minor correction on dates).

Joe,
I admit I haven’t read all the appendices. I use mainly appendix B which contains the steady-state U-values of dozens of constructions. Appendix C may provide some insights as to whether or not dynamic characteristics of the constructions were examined in their energy modeling.

From this work, BC Hydro has decided that all thermal bridging in buildings are to be accounted for when performing modeling for BC Hydro incentives. But BC Hydro also now includes blanket factors for de-rating the baseline case energy model to account for typical thermal bridging not accounted for in 90.1. It is a bit baffling to me as one has to go through a lot of work, fill in a bunch of forms to come up with almost no significant difference in relative results:

The same web page, just below “Resources” includes this Accounting for Thermal Bridging at Interface Details along with the spreadsheets:
https://www.bchydro.com/powersmart/business/programs/new-construction.html#thermal



[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones,P.Eng.
Senior Engineer

WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056

www.wspgroup.com<http://www.wspgroup.com/>

From: Joe Huang [mailto:yjhuang at whiteboxtechnologies.com]
Sent: Friday, January 29, 2016 11:46 AM
To: Jones, Christopher; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] MODELLING THERMAL BRDIGES IN e-quest or DOE2 (minor correction on dates).

Christopher,

I took a brief scroll through the link that you provided, and yes, there's a lot of information there. I haven't yet found a technical description of the methodology, but I did get to the tables with pretty colored pictures of wall sections and their computed U-values. I hope there's more information on the dynamic characteristics of these wall sections, i.e., thermal mass, diffusivity, etc., since those would be needed to model them correctly in a simulation program.

In terms of comparing the methodologies, as you've suggested, one place to start would be simply comparing the steady-state U-values derived for the same wall constructions. I've done some digging on my end and found an old 1997 User News newsletter with a brief description of the 2-D response factor work I did with Fred Winkelmann and Vladimir Bazjanac and a table listing the R-values for the 76 steel-frame wall sections modeled.  Since the whole newsletter is only 657K, I've attached it with this e-mail.  The newsletter is interesting in other ways, as well, including the announcement of the 5th IBPSA conference to be held in the Czech Republic :-) .

Joe



Joe Huang

White Box Technologies, Inc.

346 Rheem Blvd., Suite 205A

Moraga CA 94556

yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>

http://weather.whiteboxtechnologies.com for simulation-ready weather data

http://www.whiteboxtechnologies.com

(o) (925)388-0265

(c) (510)928-2683

"building energy simulations at your fingertips"
On 1/29/2016 5:18 AM, Jones, Christopher wrote:
Joe,
It would be very interesting to compare the methodologies in your paper with the results of the Morrison Herschfield research. BC Hydro published that detailed research.

https://www.bchydro.com/powersmart/business/programs/new-construction.html?WT.mc_id=rd_thermalguide#thermal

[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones,P.Eng.
Senior Engineer

WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056

www.wspgroup.com<http://www.wspgroup.com/>

From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Joe Huang
Sent: Friday, January 29, 2016 5:44 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] MODELLING THERMAL BRDIGES IN e-quest or DOE2 (minor correction on dates).

The work I did for the CEC was done in 1996 (as indicated in the report title), not 2000-2002, which was a follow-on effort to do 2-D foundation heat flows.

Joe



Joe Huang

White Box Technologies, Inc.

346 Rheem Blvd., Suite 205A

Moraga CA 94556

yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>

http://weather.whiteboxtechnologies.com for simulation-ready weather data

http://www.whiteboxtechnologies.com

(o) (925)388-0265

(c) (510)928-2683

"building energy simulations at your fingertips"
On 1/29/2016 2:41 AM, Joe Huang wrote:
I actually helped to develop a method to model thermal bridges in DOE-2 back in 1986 that has never been widely disseminated, although I still find it the most practical way to model 2-D heat flows in whole-building simulations.

This method uses a two-dimensional finite-element program (WALFERFN) that calculates one-dimensional equivalent response factors which are written directly into the DOE-2 layers library (BDLLIB.DAT), which can then be called by DOE-2 just like any other response factor in the library.

I've always used this technique in my residential modeling, with the added benefit of not needing to input duplicate sets of wall layers for the stud and non-stud portions, which measurably simplifies the  models and makes them easier to read.  The last time I did significant work on this subject was in 2000-2002, when I created for the California Energy Commission a library of over 100 wall layers with metal framing and thus considerable thermal bridging.  I compared the wall assembly U-values to that calculated by ORNL's Heating-7 program, and they were right on.  Unfortunately, a few years after the project was completed, the Commission decided to move to EnergyPlus as their reference program, and so this work was effectively abandoned.

For more information on this technique, i.e., creating 2-D response factors, please see this report:
http://www.whiteboxtechnologies.com/PAPERS/96_12_YJH_2Drespfacs_CEC_rpt.pdf

If there's anyone who's still running DOE-2 in batch, rather than just the eQUEST interface, this procedure should be quite understandable.  Just e-mail me and I'll be happy to give you a copy of the WALFERFN program and some sample input files.

Joe



Joe Huang

White Box Technologies, Inc.

346 Rheem Blvd., Suite 205A

Moraga CA 94556

yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>

http://weather.whiteboxtechnologies.com for simulation-ready weather data

http://www.whiteboxtechnologies.com

(o) (925)388-0265

(c) (510)928-2683

"building energy simulations at your fingertips"
On 1/28/2016 1:22 PM, Jim Dirkes wrote:
There is also a landmark study by Morrison Hershfield in Canada which I don't have access to at the moment that should provide guidance.

On Thu, Jan 28, 2016 at 4:11 PM, Marcus Sheffer <sheffer at sevengroup.com<mailto:sheffer at sevengroup.com>> wrote:
Follow the guidance in ASHRAE 90.1 Appendix A to determine the whole assembly values.

Marcus Sheffer
7group

-----Original Message-----
From: Jones, Christopher [mailto:Christopher.r.Jones at wspgroup.com<mailto:Christopher.r.Jones at wspgroup.com>]
Sent: Thursday, January 28, 2016 8:30 AM
To: Luis Peréz-Lombard; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] MODELLING THERMAL BRDIGES IN e-quest or DOE2

Hello Sir,
eQuest does not have the capability to directly model thermal bridges. The typical methodology is to calculate the effective U-value of the insulation/thermal bridge layer when building your layers for the construction.  BC Hydro has published significant research on building  envelope thermal bridging. See the lower portion of the webpage:
https://www.bchydro.com/powersmart/business/programs/new-construction.html#thermal




Christopher Jones, P.Eng.
Senior Engineer

WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226<tel:%2B1%20416-644-4226>
F +1 416-487-9766<tel:%2B1%20416-487-9766>
C +1 416-697-0056<tel:%2B1%20416-697-0056>

www.wspgroup.com<http://www.wspgroup.com>

-----Original Message-----
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of Luis Peréz-Lombard
Sent: Thursday, January 28, 2016 4:08 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] MODELLING THERMAL BRDIGES IN e-quest or DOE2

Dear building simulation colleagues,
I would very much appreciate any insights or work around to simulate envelope thermal bridges in e-quest.
Sincerely,
LPL
-------------------------------------------------------------
Luis Pérez-Lombard
Dr. Ingeniero Industrial
Profesor Contratado Doctor
Departamento de Ingeniería Energética
Escuela Superior de Ingenieros
Universidad de Sevilla
Camino de los Descubrimientos s/n
41092 SEVILLA
Tfno.:      95.448.72.56
Fax:         95.446.31.53
e-mail:    lpl at us.es<mailto:lpl at us.es>
-------------------------------------------------------------

_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
________________________________


You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl<http://www.wspgroup.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com><mailto:caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com>> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership

_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>


--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim at buildingperformanceteam.com<mailto:jim at buildingperformanceteam.com>

Website <http://buildingperformanceteamcom> l  LinkedIn<https://www.linkedin.com/pub/jim-dirkes/7/444/413>

Fail faster!





_______________________________________________

Bldg-sim mailing list

http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org

To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>


________________________________

You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership

________________________________

You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20160130/7d5a5602/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 7360 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20160130/7d5a5602/attachment-0009.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 7683 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20160130/7d5a5602/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 7668 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20160130/7d5a5602/attachment-0011.png>


More information about the Bldg-sim mailing list