[Bldg-sim] MODELLING THERMAL BRDIGES IN e-quest or DOE2
Jim Dirkes
jim at buildingperformanceteam.com
Thu Jan 28 13:22:02 PST 2016
There is also a landmark study by Morrison Hershfield in Canada which I
don't have access to at the moment that should provide guidance.
On Thu, Jan 28, 2016 at 4:11 PM, Marcus Sheffer <sheffer at sevengroup.com>
wrote:
> Follow the guidance in ASHRAE 90.1 Appendix A to determine the whole
> assembly values.
>
> Marcus Sheffer
> 7group
>
> -----Original Message-----
> From: Jones, Christopher [mailto:Christopher.r.Jones at wspgroup.com]
> Sent: Thursday, January 28, 2016 8:30 AM
> To: Luis Peréz-Lombard; bldg-sim at lists.onebuilding.org
> Subject: Re: [Bldg-sim] MODELLING THERMAL BRDIGES IN e-quest or DOE2
>
> Hello Sir,
> eQuest does not have the capability to directly model thermal bridges. The
> typical methodology is to calculate the effective U-value of the
> insulation/thermal bridge layer when building your layers for the
> construction. BC Hydro has published significant research on building
> envelope thermal bridging. See the lower portion of the webpage:
>
> https://www.bchydro.com/powersmart/business/programs/new-construction.html#thermal
>
>
>
>
> Christopher Jones, P.Eng.
> Senior Engineer
>
> WSP Canada Inc.
> 2300 Yonge Street, Suite 2300
> Toronto, ON M4P 1E4
> T +1 416-644-4226
> F +1 416-487-9766
> C +1 416-697-0056
>
> www.wspgroup.com
>
> -----Original Message-----
> From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf
> Of Luis Peréz-Lombard
> Sent: Thursday, January 28, 2016 4:08 AM
> To: bldg-sim at lists.onebuilding.org
> Subject: [Bldg-sim] MODELLING THERMAL BRDIGES IN e-quest or DOE2
>
> Dear building simulation colleagues,
> I would very much appreciate any insights or work around to simulate
> envelope thermal bridges in e-quest.
> Sincerely,
> LPL
> -------------------------------------------------------------
> Luis Pérez-Lombard
> Dr. Ingeniero Industrial
> Profesor Contratado Doctor
> Departamento de Ingeniería Energética
> Escuela Superior de Ingenieros
> Universidad de Sevilla
> Camino de los Descubrimientos s/n
> 41092 SEVILLA
> Tfno.: 95.448.72.56
> Fax: 95.446.31.53
> e-mail: lpl at us.es
> -------------------------------------------------------------
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> ________________________________
>
>
> You are receiving this communication because you are listed as a current
> WSP contact. Should you have any questions regarding WSP’s electronic
> communications policy, please consult our Anti-Spam Commitment
> www.wspgroup.com/casl. For any concern or if you believe you should not
> be receiving this message, please forward this message to us at
> caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that
> we can promptly address your request. This message is intended only for the
> use of the individual or entity to which it is addressed, and may contain
> information which is privileged, confidential, proprietary or exempt from
> disclosure under applicable law. If you are not the intended recipient or
> the person responsible for delivering the message to the intended
> recipient, you are strictly prohibited from disclosing, distributing,
> copying or in any way using this message. If you have received this
> communication in error, please notify the sender, and destroy and delete
> any copies you may have received.
>
> WSP provides professional land surveying services through the following
> entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited
> Partnership
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653
jim at buildingperformanceteam.com
Website <http://buildingperformanceteamcom>l LinkedIn
<https://www.linkedin.com/pub/jim-dirkes/7/444/413>
Fail faster!
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20160128/c6ef7bf2/attachment-0001.html>
More information about the Bldg-sim
mailing list