[Bldg-sim] 90.1 Appendix G pumping power question
Jim Dirkes via Bldg-sim
bldg-sim at lists.onebuilding.org
Mon Aug 15 11:58:00 PDT 2016
Chris,
I'm glad you pointed that out, because I have not read the PNNL doc yet!
I suspect that since (9 + 13) = 22, the reference is for the chilled water
pumps only. The condenser water pump will always be 19 w / gpm.
On Mon, Aug 15, 2016 at 2:34 PM, Chris Jones via Bldg-sim <
bldg-sim at lists.onebuilding.org> wrote:
> This topic has come up a few times but I am still somewhat confused as to
> how to determine the overall baseline building pumping power for a
> primary/secondary chilled water system.
>
>
>
> Each chiller on the primary loop is to have its own chilled water and
> condenser water pump. The chilled water and condenser water loops have a
> pump each.
>
>
>
> My question is – what flow rate do you use when setting the W/gpm?
> Previously, I have been using the secondary chilled water loop flow for
> determining the 22 W/gpm – split over the primary and secondary loops.
> Similarly, I had been using the cooling tower loop flow for setting the
> overall 19 W/gpm for the condenser water system.
>
>
>
> Today I am reading the PNNL 25130.pdf manual. In 3.7.5, it states, “Each
> chiller has its own primary and condenser water pumps that operate when the
> chiller is active”. Then it states, “All primary pumps shall be 9 W/gpm and
> the secondary pump shall be 13 W/gpm, and the condenser water pump is
> assumed to be 19 W/gpm.”
>
>
>
> Where it states, “All primary pumps shall be 9 W/gpm”, does this mean all
> the pumps associated with the chillers – chilled and condenser water? Or
> just the primary chilled water pumps? If just the primary chilled water
> pumps and not the chiller condenser water pumps, then what pumping power
> should the chiller condenser water pump have?
>
>
>
>
>
>
>
>
>
> *Christopher Jones, P. Eng.*
>
> *Rowan Williams Davies & Irwin Inc.*
> *Consulting Engineers & Scientists*
> 901 King Street West, Suite 400, Toronto, Ontario, M5V 3H5
> *T:* (519) 823-1311 ext 2052
>
> *M:* (416) 697-0056
>
>
> ------------------------------
> RWDI - One of Canada's 50 Best Managed Companies - This communication is
> intended for the sole use of the party to whom it was addressed and may
> contain information that is privileged and/or confidential. Any other
> distribution, copying or disclosure is strictly prohibited. If you received
> this email in error, please notify us immediately by replying to this email
> and delete the message without retaining any hard or electronic copies of
> same. Outgoing emails are scanned for viruses, but no warranty is made to
> their absence in this email or attachments. If you require any information
> supplied by RWDI in a different format to facilitate accessibility, contact
> the sender of the email, email solutions at rwdi.com or call +1.519.823.1311.
>
> ------------------------------
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653
jim at buildingperformanceteam.com
Website <http://buildingperformanceteam.com>l LinkedIn
<https://www.linkedin.com/pub/jim-dirkes/7/444/413> | May 2016 ASHRAE
Journal article on energy modeling
<http://buildingperformanceteam.com/bpt-insights-blog/item/73-modeled-performance-isn-t-actual-performance>
When shouldering your personal pack of life's burdens, bring a pocket
full of grit and a
bucket full of joy.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20160815/2ea0de26/attachment-0001.html>
More information about the Bldg-sim
mailing list