[Bldg-sim] Ground Source VRF with Energy Recovery
Duggin, Cory
Cory.Duggin at tlc-eng.com
Tue Sep 1 13:21:24 PDT 2015
Basically, IESVE is modifying the WLHP curves to the performance curves of the water-cooled VRV. The heat recovery would be shown through the common water loop in this case. When modeling air-cooled VRV/VRF in IESVE, you setup a CHW loop with a part load chiller curve for the condensing unit. Then engage condenser heat recovery to an air-air heat pump model for heat recovery VRV/VRF. It turns out pretty well.
http://www.daikinac.com/content/resources/software-tools/
Cory Duggin, PE, LEED AP BD+C
Associate/Energy Modeling Wizard, j.g.
[cid:image001.jpg at 01D0E4C9.DCF3D0B0]
TLC Engineering for Architecture
direct:
615-346-1939
From: Shane Wells [mailto:shane at hpengineeringinc.com]
Sent: Tuesday, September 01, 2015 2:59 PM
To: Duggin, Cory <Cory.Duggin at tlc-eng.com>; bldg-sim at lists.onebuilding.org
Subject: RE: Ground Source VRF with Energy Recovery
That was my thoughts for estimating this with trace - modifying the equipment curves. Do you know if IESVE is able to model the refrigerant loop heat recovery for simultaneous heating and cooling as well?
Thanks,
Shane Wells, EI
Mechanical Systems Designer
hp e n g i n e e r i n g , i n c .
479.899.6370 ext. 371
From: Duggin, Cory [mailto:Cory.Duggin at tlc-eng.com]
Sent: Tuesday, September 01, 2015 1:50 PM
To: Shane Wells <shane at hpengineeringinc.com<mailto:shane at hpengineeringinc.com>>; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: RE: Ground Source VRF with Energy Recovery
Daikin recently put out a document describing how to model water cooled VRV in IESVE with their performance curves. You could either assume a stable water temperature from the ground field or create a custom profile for the ground return temp.
Cory Duggin, PE, LEED AP BD+C
Associate/Energy Modeling Wizard, j.g.
[cid:image005.jpg at 01D0E4C9.A7306330]
TLC Engineering for Architecture
direct:
615-346-1939
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Shane Wells
Sent: Tuesday, September 01, 2015 7:16 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Ground Source VRF with Energy Recovery
I am a trace user and looking for a solution for modeling ground source VRF with energy recovery. The software says that it is currently one of Trace's limitations. Does anyone have suggestions for estimating this in Trace or another software?
Thanks,
Shane Wells, EI
Mechanical Systems Designer
hp e n g i n e e r i n g , i n c .
1800 S. Osage Springs Drive
Suite 110
Rogers, Arkansas 72758
479.899.6370 ext. 371
www.hpengineeringinc.com<http://www.hpengineeringinc.com/>
[cid:image006.jpg at 01D0E4C9.A7306330]
Thank you for voting us Best Engineering Firm in Northwest Arkansas!
We are honored to be your consulting engineering firm and are grateful for your continued support.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150901/a2123609/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 6387 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150901/a2123609/attachment-0009.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 9207 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150901/a2123609/attachment-0010.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 6387 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150901/a2123609/attachment-0011.jpg>
More information about the Bldg-sim
mailing list