[Bldg-sim] How to determine Design day
    Joe Huang 
    yjhuang at whiteboxtechnologies.com
       
    Sun Oct 18 23:30:59 PDT 2015
    
    
  
Mayank,
The EnergyPlus Weather Converter does not calculate a DDY file, but just looks through a 
file of design day data from the ASHRAE 2013 Handbook of Fundamentals. If it finds a match 
in the Station WMO number, it will print the data from the HOF in the EnergyPlus IDF 
format as a DDY file;  if not, it will return a blank DDY file as in your situation.
The procedure used by ASHRAE to calculate design day conditions is explained in the ASHRAE 
Handbook of Fundamentals, but you will need a time series of at least 8 years, and 
preferably 12 years or more of  historical weather data.  Please note that when I generate 
typical-year weather files, such as the IWEC2 for ASHRAE or the 61 Indian weather files 
for ISHRAE, at the same time I also calculate the design day conditions following the 
ASHRAE procedure, and print out the DDY files.  If you tell me the location of your 
weather file, I can see what I have that's closest in my data base of DDY files.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 10/18/2015 9:20 PM, Mayank Bhatnagar wrote:
> Dear All,
>
> I am simulating for locations that are not in the energyplus weather database. I have 
> EPW files. For simulation in energyplus, I need to define design days. I was trying to 
> generate the DDY file with energyplus weather converter but the converted DDY file only 
> contains Site:Location.
>
> Please let me know whether there is any methodology to estimate design days.
>
> Thank you.
>
> Regards,
>
> Mayank Bhatnagar
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151018/40bc70db/attachment-0001.html>
    
    
More information about the Bldg-sim
mailing list