[Bldg-sim] LEED 2009 ice arena baseline case efficiencies
Aaron Smith
asmith at mreng.ca
Thu Oct 15 10:06:11 PDT 2015
Hi Chris,
Here it is. I don’t think ASHRAE 90.1 has any additional requirements but there are some rather vague requirements in the 2011 NECB and 1997 MNECB. These statements don’t belong in a code:
“Where an ice arena or a curling rink has
a heating requirement, the refrigeration system shall
incorporate means of recovering heat rejected by the
system to the extent that the heat recovered can be
used to satisfy some or all of the heating
requirements (see Appendix E).”
Appendix E:
“Heat recovered from refrigeration
equipment can be used for space heating, service
water heating or heating the soil beneath the ice
surface to prevent frost heave.”
Aaron
Aaron Smith, P.Eng
M&R Engineering Ltd.
From: Jones, Christopher [mailto:Christopher.r.Jones at wspgroup.com]
Sent: October-15-15 9:40 AM
To: 'Aaron Smith' <asmith at mreng.ca>
Subject: RE: [Bldg-sim] LEED 2009 ice arena baseline case efficiencies
Thanks Aaron,
Please send a copy when you have a moment.
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056
www.wspgroup.com <http://www.wspgroup.com/>
From: Aaron Smith [mailto:asmith at mreng.ca]
Sent: Wednesday, October 14, 2015 10:58 PM
To: Jones, Christopher; 'Mayer, Stephen'; bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] LEED 2009 ice arena baseline case efficiencies
Hi Chris,
I'd still use the Arena EE Wizard baseline described in the modeling guide. It is from 2008 and I'm not aware of anything more up to date so it's probably due for an update - the government probably just needs to create a new incentive program before they will spend the time doing it.
I can send you a copy if you need it.
Aaron Smith, P.Eng
M&R Engineering Ltd.
Sent from my BlackBerry 10 smartphone on the TELUS network.
From: Jones, Christopher
Sent: Friday, October 9, 2015 20:04
To: 'Mayer, Stephen'; bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] LEED 2009 ice arena baseline case efficiencies
Thank you Mayer. The article by Laurier Nichols is a good starting point.
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056
www.wspgroup.com <http://www.wspgroup.com/>
From: Mayer, Stephen [mailto:Stephen.Mayer at mwgroup.net]
Sent: Friday, October 09, 2015 4:12 PM
To: Jones, Christopher; bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org>
Subject: RE: [Bldg-sim] LEED 2009 ice arena baseline case efficiencies
Christopher,
ASHRAE had a whole cover story about an Ice Area a few months back (March 2012 and September 2015).
These may have useful information/contacts.
https://ashrae.org/resources--publications/periodicals/ashrae-journal/features/ice-rink-uses-co2-system
https://www.ashrae.org/File%20Library/docLib/eNewsletters/nichols-062009--feature.pdf
http://www.nxtbook.com/nxtbooks/ashrae/ashraejournal_201203/
http://www.nxtbook.com/nxtbooks/ashrae/ashraejournal_201509/
Hope this helps.
Best Regards,
Stephen Mayer, EIT, LEED AP BD+C
Mechanical Discipline
————————————————————————————————————
M+W U.S., Inc. – A Company of the M+W Group
380 Stonebreak Road Extension, P.O. Box 2318, Malta, NY 12020, USA
Phone +1 518-305-1614
mailto:stephen.mayer at mwgroup.net, www.mwgroup.net <http://www.mwgroup.net/>
————————————————————————————————————
P Please consider the environment before printing this email
This electronic message transmission contains information from the firm of M+W Group and is confidential or privileged. The information is intended to be for the sole use of the individual or entity named herein. If you are not the intended recipient, be aware that any disclosure, copying, distribution or use of the contents of this information is prohibited. If you have received this electronic transmission in error, please notify us by telephone (972-535-7300) immediately and please then delete this electronic transmission.
From: Jones, Christopher [mailto:Christopher.r.Jones at wspgroup.com]
Sent: Friday, October 09, 2015 12:11 PM
To: bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] LEED 2009 ice arena baseline case efficiencies
Hello,
I am wondering if there is a document that describes what the baseline case efficiencies should be for an arena ice plant for LEED 2009?
My suspicion is that there isn’t such a document and that one would have to apply an exceptional calculation listing the sources of information for establishing the baseline case efficiencies.
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056
www.wspgroup.com <http://www.wspgroup.com/>
_____
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com <mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
_____
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com <mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
_____
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com <mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/4f89d622/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/4f89d622/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: ArenaEEWizard.pdf
Type: application/pdf
Size: 964064 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/4f89d622/attachment-0003.pdf>
More information about the Bldg-sim
mailing list