[Bldg-sim] ASHRAE 90.1 Window to Wall area definition
Elizabeth Gillmor
elizabeth at energetics-eng.com
Thu Oct 15 11:36:19 PDT 2015
It would have to be heated enough to qualify per Table 3.1, which would be
pretty high:
[image: Inline image 1]
And then you would have to insulate it like a conditioned space (rather
than just a semi-heated space). But yes, then you could count it!
*Elizabeth Gillmor PE, BEMP, LC, LEED AP*
*e n e r g e t i c s **consulting engineers, llc*
energetics-eng.com
c 303.619.0091
On Thu, Oct 15, 2015 at 12:24 PM, Jones, Christopher <
Christopher.r.Jones at wspgroup.com> wrote:
> So up here in Zone 6 and 7 where the first level of parking below grade is
> often heated enough to make it a conditioned space, one would count those
> below grade walls in the WWR for the Energy Cost Budget method. That can
> make a somewhat significant difference in how much glazing the baseline
> case has in the above grade walls.
>
>
>
>
>
> [image: cid:image003.png at 01D09C46.E75BA0D0]
>
> *Christopher Jones,* P.Eng.
> Senior Engineer
>
>
>
> *WSP Canada Inc.*
>
> 2300 Yonge Street, Suite 2300
>
> Toronto, ON M4P 1E4
> T +1 416-644-4226
>
> F +1 416-487-9766
>
> C +1 416-697-0056
>
>
>
> www.wspgroup.com
>
>
>
> *From:* Elizabeth Gillmor [mailto:elizabeth at energetics-eng.com]
> *Sent:* Thursday, October 15, 2015 2:07 PM
> *To:* Shaun Martin
> *Cc:* Jones, Christopher; bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] ASHRAE 90.1 Window to Wall area definition
>
>
>
> That is a great point. Appendix G is different from the prescriptive
> requirements.
>
>
>
> The prescriptive requirements (and thus Energy Cost Budget method) allow
> you to count below-grade conditioned walls as per section 5.5.4.5 as part
> of your "gross wall area", while Appendix G specifically says above-grade
> walls only.
>
>
>
>
> *Elizabeth Gillmor **PE, BEMP, LC, LEED AP*
>
>
>
> *e n e r g e t i c s **consulting engineers, llc*
>
> energetics-eng.com
>
> c 303.619.0091
>
>
>
> On Thu, Oct 15, 2015 at 11:38 AM, Shaun Martin <
> smartin at shaunmartinconsulting.com> wrote:
>
> Page 213 of 90.1-2010 says “above-grade”
>
>
>
> Shaun
>
>
>
> Shaun Martin LEED-AP, BEMP
>
> Principal
>
> Shaun Martin Consulting
>
> #90 – 425 Carrall Street
>
> Vancouver, BC V6B 6E3
>
> p. 604-789-1095
>
>
>
>
>
>
>
> *From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] *On
> Behalf Of *Jones, Christopher
> *Sent:* Thursday, October 15, 2015 10:15 AM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] ASHRAE 90.1 Window to Wall area definition
>
>
>
> I know this question has been asked before but I could not find a related
> thread.
>
>
>
> 90.1 states that the WWR is based on the gross wall area and the
> definition of gross wall area includes below ground walls as well as above
> ground walls.. Including the below grade walls can make a significant
> difference in the WWR for typical urban high rise buildings with a number
> of below grade parking floors.
>
>
>
> Can someone confirm that the WWR calculation is based on above grade wall
> area plus below grade wall area?
>
>
>
>
>
> [image: cid:image003.png at 01D09C46.E75BA0D0]
>
> *Christopher Jones,* P.Eng.
> Senior Engineer
>
>
>
> *WSP Canada Inc.*
>
> 2300 Yonge Street, Suite 2300
>
> Toronto, ON M4P 1E4
> T +1 416-644-4226
>
> F +1 416-487-9766
>
> C +1 416-697-0056
>
>
>
> www.wspgroup.com
>
>
> ------------------------------
>
>
> You are receiving this communication because you are listed as a current
> WSP contact. Should you have any questions regarding WSP’s electronic
> communications policy, please consult our Anti-Spam Commitment
> www.wspgroup.com/casl. For any concern or if you believe you should not
> be receiving this message, please forward this message to us at
> caslcompliance at wspgroup.com so that we can promptly address your request.
> This message is intended only for the use of the individual or entity to
> which it is addressed, and may contain information which is privileged,
> confidential, proprietary or exempt from disclosure under applicable law.
> If you are not the intended recipient or the person responsible for
> delivering the message to the intended recipient, you are strictly
> prohibited from disclosing, distributing, copying or in any way using this
> message. If you have received this communication in error, please notify
> the sender, and destroy and delete any copies you may have received.
>
> WSP provides professional land surveying services through the following
> entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited
> Partnership
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> ------------------------------
>
> You are receiving this communication because you are listed as a current
> WSP contact. Should you have any questions regarding WSP’s electronic
> communications policy, please consult our Anti-Spam Commitment
> www.wspgroup.com/casl. For any concern or if you believe you should not
> be receiving this message, please forward this message to us at
> caslcompliance at wspgroup.com so that we can promptly address your request.
> This message is intended only for the use of the individual or entity to
> which it is addressed, and may contain information which is privileged,
> confidential, proprietary or exempt from disclosure under applicable law.
> If you are not the intended recipient or the person responsible for
> delivering the message to the intended recipient, you are strictly
> prohibited from disclosing, distributing, copying or in any way using this
> message. If you have received this communication in error, please notify
> the sender, and destroy and delete any copies you may have received.
>
> WSP provides professional land surveying services through the following
> entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited
> Partnership
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/3ad08aee/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 10218 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/3ad08aee/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/3ad08aee/attachment-0007.png>
More information about the Bldg-sim
mailing list