[Bldg-sim] ASHRAE 90.1 Window to Wall area definition
Nathan Miller
nathanm at rushingco.com
Thu Oct 15 10:46:11 PDT 2015
But to further complicate things, my understanding is that if you have an enclosed-conditioned space within the parking garage (elevator lobby, maintenance room, etc), and walls of that space that border the unconditioned parking garage you WOULD count that as above-grade wall.
The most complicated scenario is a conditioned room tucked along the perimeter of the parking garage. In that case you WOULD COUNT the walls that separate the space from the unconditioned garage as part of the App G WWR calc, but you WOULD NOT COUNT the below grade walls that separate that space from dirt in the App G WWR calcs.
Nathan Miller, PE, LEED AP BD+C – Mechanical Engineer/Senior Energy Analyst
RUSHING | D 206-788-4577 | O 206-285-7100
www.rushingco.com<http://www.rushingco.com/>
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Thursday, October 15, 2015 1:40 PM
To: Shaun Martin <smartin at shaunmartinconsulting.com>; 'Jones, Christopher' <Christopher.r.Jones at wspgroup.com>; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 90.1 Window to Wall area definition
Expanding on Michael’s and Elizabeth’s comments…
Note that Appendix G. specifically refers to “above-grade wall area” for determining fenestration percentages (in 2007, 2010 and 2013 versions).
Also note that “parking garages with natural or mechanical ventilation are not considered enclosed spaces” per 90.1 definition of space. Therefore, any “walls”, whether above or below-ground, are not part of the building envelope, are therefore not technically walls per 90.1 and wouldn’t be included in WWR calculations.
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image001.jpg at 01D1074F.D45ADB30] [cid:image002.jpg at 01D1074F.D45ADB30]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Shaun Martin
Sent: Thursday, October 15, 2015 1:39 PM
To: 'Jones, Christopher' <Christopher.r.Jones at wspgroup.com<mailto:Christopher.r.Jones at wspgroup.com>>; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] ASHRAE 90.1 Window to Wall area definition
Page 213 of 90.1-2010 says “above-grade”
Shaun
Shaun Martin LEED-AP, BEMP
Principal
Shaun Martin Consulting
#90 – 425 Carrall Street
Vancouver, BC V6B 6E3
p. 604-789-1095
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher
Sent: Thursday, October 15, 2015 10:15 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] ASHRAE 90.1 Window to Wall area definition
I know this question has been asked before but I could not find a related thread.
90.1 states that the WWR is based on the gross wall area and the definition of gross wall area includes below ground walls as well as above ground walls.. Including the below grade walls can make a significant difference in the WWR for typical urban high rise buildings with a number of below grade parking floors.
Can someone confirm that the WWR calculation is based on above grade wall area plus below grade wall area?
[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056
www.wspgroup.com<http://www.wspgroup.com/>
________________________________
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/ffcb9715/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/ffcb9715/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/ffcb9715/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 3856 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/ffcb9715/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 6574 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/ffcb9715/attachment-0007.png>
More information about the Bldg-sim
mailing list