ASHRAE interpretation IC 90.1-2004-1 dated June 25, 2005 states that gross wall area is “the area of the wall measured from the exterior face from the top of the floor to the bottom of the roof”.
It goes on to say that buildings with conditioned below-grade space, the gross wall area includes below-grade space.
Cheryl M. Saldanha, P.E. (CA)
Senior Staff I - Building Technology
SIMPSON GUMPERTZ & HEGER
212.271.7000 main
212.271.6962 direct
917.856.7702 mobile
212.271.0111 fax
www.sgh.com
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rosenberg, Michael I
Sent: Thursday, October 15, 2015 1:34 PM
To: David Eldridge <DEldridge at grummanbutkus.com>; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 90.1 Window to Wall area definition
David is correct regarding prescriptive compliance with Section 4 in 90.1. However, 2010 Appendix G in table G3.1.5 clearly states that baseline WWR is limited to 40% of “gross above grade wall area”. This is an important distinction.
__________________________
Michael Rosenberg, CEM, LEED AP
Senior Research Scientist
ENERGY & ENVIRONMENT DIRECTORATE
Pacific Northwest National Laboratory
2032 Todd Street
Eugene, OR 97405
(509) 375-1995
michael.rosenberg at pnnl.gov<mailto:michael.rosenberg at pnl.gov>
www.pnnl.gov<http://www.pnl.gov/>
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of David Eldridge
Sent: Thursday, October 15, 2015 10:27 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] ASHRAE 90.1 Window to Wall area definition
Example 5-Q in the 90.1-2013 User’s Manual still uses both above-grade and below-grade walls as “exterior walls” for determining gross wall area.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher
Sent: Thursday, October 15, 2015 12:15 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] ASHRAE 90.1 Window to Wall area definition
I know this question has been asked before but I could not find a related thread.
90.1 states that the WWR is based on the gross wall area and the definition of gross wall area includes below ground walls as well as above ground walls.. Including the below grade walls can make a significant difference in the WWR for typical urban high rise buildings with a number of below grade parking floors.
Can someone confirm that the WWR calculation is based on above grade wall area plus below grade wall area?
[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056
www.wspgroup.com<http://www.wspgroup.com/>
________________________________
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/5540f86d/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/5540f86d/attachment-0003.png>
More information about the Bldg-sim
mailing list