Veronica,
I'm not sure if I understand your problem, but the exceptions for
non-predominant HVAC sytems are based on
"Peak thermal loads that *differ *by xx W/m2 or more from the average of
other spaces..."
Thus, if all zones are 30 W/m2, they should be modeled with the normal
Baseline HVAC. If, however, one or more zones is 15W/m2 or 50 W/m2, you
have justification for using Systems #3 or #4.
On Tue, Oct 13, 2015 at 11:37 AM, Veronica Ochoa <
veronica.ochoa at hurleypalmerflatt.com> wrote:
> Hi,
>
>
>
> I’m modelling a data center with 50 thermal zones for LEED EAp2/c1
> purposes. The baseline system determined based on area and building type is
> system 8. However when doing the load deviation average to determine
> suitability for System 4 (under exception B), all but 6 zones are greater
> than the 31 W/m2 of the averaged cooling load per system/floor. This means
> that I will have 6 zones (2.5% of total area) as system 8 and 44 zones as
> system 4. Do I need to follow the exception that says that each zone served
> by System 4 should be modelled as one zone per system?? I find this a bit
> too much… I was wondering if you can simplify this by grouping similar
> spacetypes by setpoints or floors and reduce the number of systems.
>
>
>
> Also, in the preliminary submission 100% of the zones were submitted as
> system 4, but this was noted by the USGBC reviewer as an error (as it was
> based on the average of the entire building not per system). As it has been
> now corrected and only 2.5% of the zones will be system 8, we are
> estimating the difference will be negligible. Would a narrative explaining
> this suffice? Has anyone been in this situation and how did you approach
> it?
>
>
>
> Many thanks in advance for your help,
>
> Veronica Ochoa
>
> Consultant
>
> *hurleypalmerflatt*
>
> *building* *sustainability*
>
> *d:*
>
> +44 20 7535 3750
>
> *t:*
>
> +44 20 7535 3100
>
> *e:*
>
> veronica.ochoa at hurleypalmerflatt.com
>
> <https://retrofit.architectsjournal.co.uk/shortlist-2015>
> [image: HPFWebsite] <http://www.hurleypalmerflatt.com> [image: LinkedIn]
> <https://uk.linkedin.com/company/hurleypalmerflatt> [image: Twitter]
> <https://twitter.com/hpf_group> [image: GooglePlus]
> <https://plus.google.com/105591062940781402373>
> <https://www.flickr.com/photos/127827710@N02/> [image: Facebook]
> <https://www.facebook.com/hurley.palmer.flatt?ref=hl> [image: YouTube]
> <http://www.youtube.com/user/hurleypalmerflatt>
>
> View company email disclaimer at: http://www.hurleypalmerflatt.com/
> <http://www.hurleypalmerflatt.com/disclaimer.html>disclaimer
> <http://www.hurleypalmerflatt.com/disclaimer.html>.html
> <http://www.hurleypalmerflatt.com/disclaimer.html>
>
> *P Please** consider the environment before printing this **email**.*
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653
jim at buildingperformanceteam.com
Website <http://buildingperformanceteamcom>l LinkedIn
<https://www.linkedin.com/pub/jim-dirkes/7/444/413>
“…happiness is the joy produced in us by truth. To be truly happy means
coming to know how things really are, experiencing …reality in its ultimate
root…
What matters more to one’s happiness than getting more freedom and power is
the end toward which we order whatever freedom and power we have. Unless we
order ourselves to the truth, more freedom and more power will bring only
more unhappiness, examples of which abound.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151013/c37ca4a3/attachment-0001.html>
More information about the Bldg-sim
mailing list