[Bldg-sim] Modelling groundwater cooling via concrete slab
Andy Tindale
Andy.Tindale at designbuilder.co.uk
Thu Jun 18 01:31:49 PDT 2015
Claire,
It sounds like you are using IES but you mention "other packages" as well so I thought I'd outline the ways that ground water cooling through hydronic slabs can be modelled in DesignBuilder EnergyPlus.
1. In DesignBuilder v4.5 there is an HVAC template which allows you to directly model this system with water from a ground borehole flowing through a HX component which cools water flowing through a second circuit into ceiling surfaces. You get the cooling injected into exactly the right part of the surface and slab thermal mass is included. You just have to load the template and set the position of the pipes in your ceiling slab construction. You can select a template with the number of boreholes or use water from a lake. For later more detailed design work you can refine the ground loop design using a third party tool such as GLD or GLHEPRO.
[cid:image003.jpg at 01D0A9A9.9A0E73F0]
Other simpler options include:
2. As suggested by others you can use a dummy chiller setting a fuel code to ignore the fuel consumption.
3. Use district cooling.
Options 2 and 3 would allow you to set a fixed 12degC for supply temperature. Option 1 would calculate the correct supply temperature based on the capacity of the ground water supply.
I hope it helps.
Andy
Andy Tindale
Managing Director I Tel: +44 (0)1453 755500 I andy.tindale at designbuilder.co.uk<mailto:andy.tindale at designbuilder.co.uk>
DesignBuilder Software Ltd, 1st Floor, Clarendon Court, 54-56 London Rd, Stroud, GL5 2AD
www.designbuilder.co.uk<http://www.designbuilder.co.uk/>
[cid:image006.jpg at 01D0A9A9.9A0E73F0]
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Claire Das Bhaumik
Sent: Wednesday, June 10, 2015 3:02 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Modelling groundwater cooling via concrete slab
I'm looking for the most suitable approach for modelling groundwater cooling in a thermal model. It's proposed to have pipes embedded in a concrete ceiling with groundwater flowing through them. The groundwater supply temp will be fixed at around 12degC.
I'm using IES software but I expect the possible approaches would be similar with most packages.
I could either use a simplified approach calculating the cooling capacity from the flow rate and temperature difference, or use a detailed systems modelling approach. I want something fairly quick but reasonably accurate (don't we all?!) as it's a preliminary study.
Thanks,
Dr Claire Das Bhaumik CEng FCIBSE
Partner - Inkling LLP
e: claire at inklingllp.com<mailto:claire at inklingllp.com>
t: 07950 282800
w: www.inklingllp.com<http://www.inklingllp.com/>
Follow us on Twitter: @DasInkling
Partnership No. OC367619
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150618/d2ec117a/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 48319 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150618/d2ec117a/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 2030 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150618/d2ec117a/attachment-0007.jpg>
More information about the Bldg-sim
mailing list