[Bldg-sim] 90.1 Ap. G System selection: 5 stories + Underground - System 6 or 8?
Javed Iqbal
javedvit at gmail.com
Thu Jul 2 14:54:51 PDT 2015
In my opinion the *system type 8* would be applicable. As the *total
conditioned area *is not explicitly mentioned so i presume it is more than
150,000 sqft (above grade floor+basement floor areas).
Here are couple of reason which i could think of:
i) per G3.1.1, HVAC systems in the baseline building design shall be based
on usage, number of floors, conditioned floor area, and heating source as
specified in Table G3.1.1A and shall conform with the system descriptions
in Table G3.1.1B.
ii) per Table G3.1.1A, system 8 would be applicable if either of the
condition is met number of floors OR conditioned area OR both
iii) exception G3.1.1a would be applicable once you are decided with
the *predominant
system type* based on number of floors or conditioned area OR both per
section G3.1.1. I strongly feel that exceptions are applicable only when
the modeling scenario can not be addressed by the main sections which in
your case is G3.1.1.
Hope this helps!
On Wed, Jul 1, 2015 at 7:54 PM, Santiago Velez <santiagogvelez at gmail.com>
wrote:
> What is in your opinion the baseline for the following building:
>
> Floor area:12,000 sqm (130,000 sqft)
> Floors: 5 above grade, mostly conditioned. 5 underground parking, mostly
> unconditioned apart from some conditioned spaces in the first below grade
> floor.
>
> Predominant Use: Office (85% of sqft),
> Secondary use: bank in PB and below grade; Kitchen, below grade; control
> security room, below grade.
>
> I'm in between baseline 6 or 8. If conditioned spaces below grade fall
> under exceptions to G3.1.1 b. then can I consider for the baseline that the
> predominant building has 5 floors instead of 6?
>
> Thanks in advance.
>
> Santiago.
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150703/75fe30e1/attachment-0001.html>
More information about the Bldg-sim
mailing list