[Bldg-sim] Energy recovery with wheel and runaround loop coil?

Bishop, Bill bbishop at pathfinder-ea.com
Fri Dec 11 11:06:23 PST 2015


I'd appreciate comments on how to maximize the energy savings from using a runaround loop coil and energy recovery wheel in series.

I'm modeling a lab HVAC air handler that has an energy wheel and return/exhaust fan at the air handler but where 1/3 to ½ of the OA is exhausted elsewhere (a dedicated fume hood exhaust system). The designer is considering an option for additional heat recovery via a runaround loop with glycol coils at the fume hood exhaust and the air handler OA stream. This is in a heating-dominated climate (CZ 6A) and the SAT will be 55F.


-        Any thoughts on how to arrange the coils in the OA stream, which will also include a glycol preheat coil and a CHW coil? (Runaround coil -> wheel -> preheat coil -> CHW coil?)

-        How to control the system? (Activate and modulate the wheel first; activate the runaround loop when OAT drops below the point that wheel can maintain the mixed air temperature?)

-        I assume the pumping power for the runaround loop would be higher than the motor power for rotating the wheel.

Thanks!

William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[cid:image007.jpg at 01D1341D.1D641810]  [cid:image008.jpg at 01D1341D.1D641810]



134 South Fitzhugh Street                 Rochester, NY 14608

T: (585) 698-1956                        F: (585) 325-6005

bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>             www.pathfinder-ea.com<http://www.pathfinder-ea.com/>

[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151211/c30a56a8/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151211/c30a56a8/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151211/c30a56a8/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 3859 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151211/c30a56a8/attachment-0001.png>


More information about the Bldg-sim mailing list